Default Electrical contractor could not understand why tandems were not allowed

I get a call from a 20 plus year electrician wanting me to explain why tandem (or has he insisted calling them, twins) breakers were not allowed in this panel. And how I know this.

I tried to explain to him over and over that the diagram on the panel door illustrated that tandems were not allowed; and also 20 spaces/circuits was the maximum, and the installed tandems exceeded this. He kept asking how I could determine this. I told him it was on the diagram inside the panel door. He was not able to comprehend this. He said in older homes when panels are overloaded and there is no more room it is common practice to install twins.

He then said well there are a few other things to repair, such as 40 amp breaker with #10 conductor for the AC. I tried again explaining that it is often allowed to under size the conductor for the AC. It depends on the AC data plate. He never heard o that.
Attached Thumbnails
Electrical contractor could not understand why tandems were not allowed-20180809-18-jpg   Electrical contractor could not understand why tandems were not allowed-20180809-19-jpg  
Reply With Quote
Need a home inspection in Pennsylvania? Check out InterNACHI's listing of Pennsylvania certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/21/18, 8:40 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
Certified Master Inspector
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 10,877
Send a message via Yahoo to jfunderburk
Default Re: Electrical contractor could not understand why tandems were not allowed

I agree with Mr. Sparky. Based on what you provided, I see nothing that prohibits the use of tandems or slim-line breakers. My own panel has some. As long as it is of the same manufacturer, I think it is OK. Keep in mind that you aren't doing load calculations. (BTW, the Square-D breaker is prohibited in that panel I'm pretty sure.)



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Award Winner 2017, 2016, 2015, 2014, 2013, 2012, 2011, 2010.
Ph: 704-351-1776
www.aohomeinspection.com

Reply With Quote
  #3  
Old 8/21/18, 8:48 PM
Bradley K. Toye, CMI's Avatar
Bradley K. Toye, CMI Bradley K. Toye, CMI is online now
Certified Master Inspector
 
Join Date: Sep 2010
Location: Clearwater, FL
Posts: 5,384
Default Re: Electrical contractor could not understand why tandems were not allowed

Quote:
Originally Posted by jfunderburk View Post
I agree with Mr. Sparky. Based on what you provided, I see nothing that prohibits the use of tandems or slim-line breakers. My own panel has some. As long as it is of the same manufacturer, I think it is OK. Keep in mind that you aren't doing load calculations. (BTW, the Square-D breaker is prohibited in that panel I'm pretty sure.)
Well, that's two that don't know how to read a panel diagram.



Brad K Toye
ITC/FLIR Level I Building Investigation Thermographer
FL Certified Building Contractor CBC034303
FL Certified Home Inspector HI 391
FL Certified Mold Assessor MRSA 589

727-403-5029
Lecsi2@gmail.com
www.LeadingEdgeInspectionServices.com
Reply With Quote
  #4  
Old 8/21/18, 8:49 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 31,051
Default Re: Electrical contractor could not understand why tandems were not allowed

Chris, send him this link to educate him.
How to know when tandem circuit breakers can be used (aka - cheater breakers) - StarTribune.com





CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers and any rules updates.
Reply With Quote
  #5  
Old 8/21/18, 9:20 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
Certified Professional Inspector (CPI)
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 10,590
Default Re: Electrical contractor could not understand why tandems were not allowed

Quote:
Originally Posted by ccurrins View Post
I get a call from a 20 plus year electrician
C'mon Chris. Watch the spelling. It should be 20 year "Lektrishun".....




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
InterNACHI Lifetime Member

RETIRED

Reply With Quote
  #6  
Old 8/21/18, 11:26 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 2,666
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical contractor could not understand why tandems were not allowed

Quote:
Originally Posted by jfunderburk View Post
I agree with Mr. Sparky. Based on what you provided, I see nothing that prohibits the use of tandems or slim-line breakers. My own panel has some. As long as it is of the same manufacturer, I think it is OK. Keep in mind that you aren't doing load calculations. (BTW, the Square-D breaker is prohibited in that panel I'm pretty sure.)
The wiring diagram clearly shows only a single breaker is allowed. Tandems are only allowed in certain panels according to their listings. The wiring diagram will show.if allowed. Also the model number will typically be something like 200m3040.
Reply With Quote
  #7  
Old 8/21/18, 11:56 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
Certified Master Inspector
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 10,877
Send a message via Yahoo to jfunderburk
Default Re: Electrical contractor could not understand why tandems were not allowed

Interesting article. Learned something new.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Award Winner 2017, 2016, 2015, 2014, 2013, 2012, 2011, 2010.
Ph: 704-351-1776
www.aohomeinspection.com

Reply With Quote
  #8  
Old 8/21/18, 11:57 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
Certified Master Inspector
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 10,877
Send a message via Yahoo to jfunderburk
Default Re: Electrical contractor could not understand why tandems were not allowed

What do you do when there is no panel label???



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Award Winner 2017, 2016, 2015, 2014, 2013, 2012, 2011, 2010.
Ph: 704-351-1776
www.aohomeinspection.com

Reply With Quote
  #9  
Old 8/22/18, 8:37 AM
Joshua L. Frederick Joshua L. Frederick is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 4,846
Send a message via AIM to jfrederick
Default Re: Electrical contractor could not understand why tandems were not allowed

Quote:
Originally Posted by jfunderburk View Post
What do you do when there is no panel label???
Pretty simple...panel label missing and couldn't verify panel manufacturer requirements. It's possible defects exist that could not be confirmed due to this. Have an electrician... blah, blah, blah.




http://northwestohiohomeinspector.com

Defiance home inspector
Northwest Ohio home inspector
Reply With Quote
  #10  
Old 8/22/18, 10:28 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
Certified Master Inspector ®
 
Join Date: Sep 2005
Location: McKinney, TX
Posts: 9,708
Send a message via Skype™ to pabernathy
Default Re: Electrical contractor could not understand why tandems were not allowed

Not all Electrical Contractors are created equal and being in the business for "20 years" doesn't mean he did everything correctly for those "20 years" as well. The learning process is never ending and when I teach someone who refuses to listen then I smile, agree to disagree and move on.

Was not the case 10 years ago but I have mellowed in my old age and do not have time to stress those who do not care to learn or listen and I am always willing and ready to learn new things.



Paul W. Abernathy, CMECP®
NFPA 70 (NEC®) Code Panel Member on #5 and #17
Founder of the Certified Master Electrical Code Professional® Program
CMECP® Website - www.MyCMECP.com
Website - http://www.masterthenec.com
Twitter - https://twitter.com/MasterTheNEC
Facebook -https://www.facebook.com/masterthenec/
Spreaker PodCasts - https://www.spreaker.com/show/master-the-necs-tracks


Disclaimer - All my posts on this forum represent Electrical Code Academy, Inc.
Reply With Quote
  #11  
Old 8/26/18, 9:53 AM
Mark Raumikaitis Mark Raumikaitis is offline
Certified Master Inspector
 
Join Date: Jan 2011
Location: Candia, NH
Posts: 864
Default Re: Electrical contractor could not understand why tandems were not allowed

Paul, well said





Mark Raumikaitis, CMI, NH Lic #133
HomeCheck Professional Home Inspections LLC
Derry, NH
603-432-3211
Inspecting New Hampshire and Southern Maine
http://homecheckhomeinspections.com/

"Always think long term, do not be influenced by short term thinking or rewards."
Reply With Quote
  #12  
Old 8/26/18, 8:24 PM
Bryan Beneke Bryan Beneke is offline
Certified Professional Inspector (CPI)
 
Join Date: Apr 2014
Posts: 35
Default Re: Electrical contractor could not understand why tandems were not allowed

Can There be tandem circuits on this panel board?
Reply With Quote
  #13  
Old 8/26/18, 8:36 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
Certified Professional Inspector (CPI)
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 10,590
Default Re: Electrical contractor could not understand why tandems were not allowed

Quote:
Originally Posted by bbeneke View Post
Can There be tandem circuits on this panel board?
There is a picture of the label. What does that tell you?




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
InterNACHI Lifetime Member

RETIRED

Reply With Quote
Need a home inspection in Pennsylvania? Check out InterNACHI's listing of Pennsylvania certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 8/26/18, 9:33 PM
Bryan Beneke Bryan Beneke is offline
Certified Professional Inspector (CPI)
 
Join Date: Apr 2014
Posts: 35
Default Re: Electrical contractor could not understand why tandems were not allowed

Not absolutely sure. I'm thinking no, but that's why I posted it. I was hoping someone would confirm my thoughts instead of mess with them.
Reply With Quote
  #15  
Old 8/26/18, 10:20 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
Certified Professional Inspector (CPI)
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 10,590
Default Re: Electrical contractor could not understand why tandems were not allowed

Quote:
Originally Posted by bbeneke View Post
Not absolutely sure. I'm thinking no, but that's why I posted it. I was hoping someone would confirm my thoughts instead of mess with them.
Nobody is messing with you. The information you seek is right on the label. Maybe this will help. Note the circuits at the bottom.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
InterNACHI Lifetime Member