Came across this fused panel in a garage this AM. Is this considered double tapping, like a breaker? Multiple wires on same lug. There seems to be an excessive amount of wires connected to all the terminals.
In order for a terminal to be used with two conductors it must be listed for two conductors. From the photos I would say that those aren’t listed for more than one conductor.
Yes…I also recommend upgrading. At bare minimum have the electrician fix the double tap and evaluate the box.
Also, is the ground a bootleg ground?
No, the ground is Not a bootleg ground.
Thanks, I was confident that it was wired improperly.
I like Roberts response…go with that one…