Default GE panel with all Cutler Hammer breakers?

Today a five year old well built home with two GE panels, GE main breaker(s). All of the breakers in each panel were Cutler Hammer. I know CH are capable with many different brands, not sure about GE. Of course the panel label said use only GE breakers. Any electricians care to share an opinion.

Last edited by ccurrins; 9/25/15 at 7:09 PM..
Reply With Quote
Need a home inspection in Montana? Check out InterNACHI's listing of Montana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/24/15, 10:59 PM
David Hays, CMI David Hays, CMI is offline
Certified Professional Inspector (CPI)
 
Join Date: Feb 2010
Location: Denver, CO
Posts: 3,051
Send a message via AIM to dhays Send a message via MSN to dhays
Default Re: GE panel with all Cutler Hammer breakers?

Quote:
Originally Posted by ccurrins View Post
Today a five year old well built home with two GE panels, GE main breaker(s). All of the breakers in each panel were Cutler Hammer. I know CH are capable with many different brands, not sure about GE. Of course the panel label said use only GE breakers. Any electricians care to share an opinion.
You answered your own question.



David Hays
All Points Property Inspections LLC
Denver, CO
720-217-7821
david@allpointinspect.com
www.allpointshomeinspections.org
www.denvercommercialinspections.com
Reply With Quote
  #3  
Old 9/24/15, 11:05 PM
Kenneth A. Ramm Kenneth A. Ramm is offline
Certified Professional Inspector (CPI)
 
Join Date: Oct 2012
Location: New Glarus, WI
Posts: 3,783
Default Re: GE panel with all Cutler Hammer breakers?

Quote:
Originally Posted by dhays View Post
You answered your own question.
Agree and this is good to have in your report.

GE panel with all Cutler Hammer breakers?-p9230130-jpg



Kenneth (Kenny) Ramm
608-438-3986
RammHomeInspections@gmail.com
Wisconsin License 2516-106
InterNACHI #12101905
Level II Infraspection Institute Certified Infrared Thermographer #10786

"If you want to live a happy life, tie it to a goal, not to people or objects." Albert Einstein
Reply With Quote
  #4  
Old 9/24/15, 11:16 PM
Larry Kage, CMI's Avatar
Larry Kage, CMI Larry Kage, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: NW, MI
Posts: 18,166
Default Re: GE panel with all Cutler Hammer breakers?

Quote:
Originally Posted by ccurrins View Post
Today a five year old well built home with two GE panels, GE main breaker(s). All of the breakers in each panel were Cutler Hammer. I know CH are capable with many different brands, not sure about GE. Of course the panel label said use only GE breakers. Any electricians care to share an opinion.
These may help, Christopher. I think they were from Paul:

ELEC-classified-breakers1 copy.pdf




Awards Committee Officer
SUBMIT YOUR AWARD NOMINATIONS HERE:
http://co.nachi.org/inachiawards/

The InterNACHI Awards Committee is the final authority of the issuance of any award the committee offers and any rules interpretation updates.
____________________________________________

Larry Kage, CMI Lifetime Member
State Licensed Builder since 1973
InterNACHI Lifetime Member
~retired~

The above post represents my personal opinion.

Last edited by lkage; 9/24/15 at 11:34 PM..
Reply With Quote
  #5  
Old 9/24/15, 11:30 PM
Christopher Currins, CMI Christopher Currins, CMI is offline
Certified Master Inspector ®
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 17,622
Default Re: GE panel with all Cutler Hammer breakers?

Thanks guys. This is why I ask. As David said I have my own answer with label. Then again the pdf Larry posted, which I've read many times, says certain CH breakers are UL classified and "approved" to use in GE panels.

I always call out mismatched breakers. In this case I was surprised to see ALL of the breakers of a different brand than panel manufacture.
Reply With Quote
  #6  
Old 9/25/15, 4:18 AM
Gordon R. Marchant, HI-298's Avatar
Gordon R. Marchant, HI-298 Gordon R. Marchant, HI-298 is offline
Certified Professional Inspector (CPI)
 
Join Date: Oct 2006
Location: Loxahatchee, Fl
Posts: 122
Default Re: GE panel with all Cutler Hammer breakers?

Looks like you left a word out of "use only GE breakers", it says "use only GE TYPE breakers"



Gordon Marchant, President, CMI
Florida Master Home Inspectors, Inc.
www.florida-mhi.com
Serving Southeast Florida
561-792-0271
State of Florida home inspector license #298
Reply With Quote
  #7  
Old 9/25/15, 8:24 AM
Andrew A. Griffin, CMI's Avatar
Andrew A. Griffin, CMI Andrew A. Griffin, CMI is offline
Certified Professional Inspector (CPI)
 
Join Date: Aug 2012
Location: Pittsburgh, PA.
Posts: 412
Default Re: GE panel with all Cutler Hammer breakers?

I always look for the big "ul listed" stamp that gets put on. I'm on my phone, but if you search cutler hammer ul listed breaker, there is a pdf download cut sheet. It is type CL breakers.




Andy Griffin
Griffin Inspection Services LLC
agriffin@griffinspection.com
412-407-2501
www.griffinspection.com
www.pittsburgh-home-inspections.com
Pittsburgh home inspections
Reply With Quote
  #8  
Old 10/1/15, 4:51 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
Certified Master Inspector ®
 
Join Date: Sep 2005
Location: McKinney, TX
Posts: 9,784
Send a message via Skype™ to pabernathy
Default Re: GE panel with all Cutler Hammer breakers?

Hello All -

Let's examine that actual statement.......

"Of course the panel label said use only GE breakers"

The use of a Classified Circuit Breaker in a panel that says use only GE Breakers would still be acceptable. https://en.wikipedia.org/wiki/Magnus...s_Warranty_Act

Fact is in new installations GE's statement would be correct....but in replacement situations the Magnuson Moss Act would be applicable. If the Classified Circuit Breakers have been evaluated for use in the SAID GE panel then it would be compliant in terms of code.

Now how about warranty....changes are GE would say they will not honor the warranty on the circuit breaker but in reality the warranty was probably over a long time ago so the new replacement circuit breaker more than likely has a better warranty on it anyway.

Point is......just because it says GE only......and Square D used to say that alot as well....the MM Act does apply to replacement applications...now your job is to determine if it is a replacement.....and if it is a classified circuit breaker then I would safely assume it is in my opinion.

If it is not a classified...some other brand that has not been evaluated for use in the GE panel then it would not be acceptable......see how Classified Circuit Breakers are DIFFERENT....they have been tested in the GE Panel.



Paul W. Abernathy, CMECP®
NFPA 70 (NEC®) Code Panel Member on #5 and #17
Founder of the Certified Master Electrical Code Professional® Program
CMECP® Website - www.MyCMECP.com
Website - http://www.masterthenec.com
Twitter - https://twitter.com/MasterTheNEC
Facebook -https://www.facebook.com/masterthenec/
Spreaker PodCasts - https://www.spreaker.com/show/master-the-necs-tracks


Disclaimer - All my posts on this forum represent Electrical Code Academy, Inc.
Reply With Quote
  #9  
Old 10/1/15, 11:10 PM
Christopher Currins, CMI Christopher Currins, CMI is offline
Certified Master Inspector ®
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 17,622
Default Re: GE panel with all Cutler Hammer breakers?

Quote:
Originally Posted by pabernathy View Post

Now how about warranty....changes are GE would say they will not honor the warranty on the circuit breaker but in reality the warranty was probably over a long time ago so the new replacement circuit breaker more than likely has a better warranty on it anyway.
House at OP was built in 2008. They were the original breakers. Which is why I thought it was odd. Two GE panels with All CH breakers.
Reply With Quote
  #10  
Old 10/2/15, 8:29 AM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
Certified Professional Inspector (CPI)
 
Join Date: Sep 2009
Location: Palm Bay FL
Posts: 4,650
Default Re: GE panel with all Cutler Hammer breakers?

What a fun challenge it would be to spend time determining if each and every breaker we find is indeed rated for that enclosure.
The possibility and options for breakers that fit and don't fit are endless.
In this case, looking up the specific breaker may determine compatibility since they are all the same, but me personally, I would consider having an electrician make that determination. Of course, they are not going to want to do the homework either.





Fogarty Inspection Services Group of Palm Bay FL
FL Licensed Home Inspector #8351
Infraspection Level 2 Thermographer #8788
FL Licensed Mold Assessor #MRSA2330
Certified Master Inspector

Home inspections, Commercial Inspections, Mold assessments, Thermal Imaging, Wind Mitigation and Insurance Inspections for Palm Bay, Melbourne, Cocoa, Titusville, Vero Beach and all the surrounding areas.

321-506-5125
fogartyinspectionservices@gmail.com

www.homeinspectorpalmbay.com
Reply With Quote
  #11  
Old 10/2/15, 10:02 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
Certified Master Inspector ®
 
Join Date: Sep 2005
Location: McKinney, TX
Posts: 9,784
Send a message via Skype™ to pabernathy
Default Re: GE panel with all Cutler Hammer breakers?

Quote:
Originally Posted by ccurrins View Post
House at OP was built in 2008. They were the original breakers. Which is why I thought it was odd. Two GE panels with All CH breakers.
Ahhh...that would be odd.

Must have been what they had on the truck...



Paul W. Abernathy, CMECP®
NFPA 70 (NEC®) Code Panel Member on #5 and #17
Founder of the Certified Master Electrical Code Professional® Program
CMECP® Website - www.MyCMECP.com
Website - http://www.masterthenec.com
Twitter - https://twitter.com/MasterTheNEC
Facebook -https://www.facebook.com/masterthenec/
Spreaker PodCasts - https://www.spreaker.com/show/master-the-necs-tracks


Disclaimer - All my posts on this forum represent Electrical Code Academy, Inc.
Reply With Quote
  #12  
Old 10/3/15, 10:12 AM
Michael A. Clark, CMI's Avatar
Michael A. Clark, CMI Michael A. Clark, CMI is offline
Certified Master Inspector
 
Join Date: Apr 2012
Location: Almost Heaven, WV
Posts: 6,952
Default Re: GE panel with all Cutler Hammer breakers?

Quote:
Originally Posted by ccurrins View Post
House at OP was built in 2008. They were the original breakers. Which is why I thought it was odd. Two GE panels with All CH breakers.
Best guess is the GE panel was cheapest, and the CH breakers were cheaper than GE breakers? What other reason could there be?




Michael A Clark, Certified Master Inspector®
Inspection Connection
St Albans, West Virginia

"Always tell the truth,
do what you say you will,
and do it Righter than Right...Always"

Facebook

Google Plus

www.charleston-home-inspector.com
www.icwvhomes.com

mclark@icwvhomes.com