  #1  
Old 11/9/09, 6:39 PM
Tim C. Howell Tim C. Howell is offline
Certified Professional Inspector (CPI)
 
Join Date: Jan 2009
Location: New Liberty, IA
Posts: 116
Default GFCI on 2 wire systems

Looking for some help on clarification. My understanding is a GFCI will prevent elec shock in a 2 wire system. I have seen them in bathrooms and kitchens. The part that trips me up is, a 2 wire system is still not grounded. That should be a safety concern, but not unsafe with a GFCI installed. (correct?)
Second part of question, in a home with 2 wire outlets why couldn't a person put GFCIs in all the locations? Like the living room for example. I was ask this question the other day. The occupants would be protected, correct?
Thanks folks.
Reply With Quote
Find an InterNACHI certified Georgia Home Inspector (and anywhere else in North America)
  #2  
Old 11/9/09, 7:17 PM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 74,991
Default Re: GFCI on 2 wire systems

He can.



As a Professional Home Inspector, I support the privacy of my clients.

You own your private information. I won't sell or give away yours, others do


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
  #3  
Old 11/9/09, 7:31 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is online now
Certified Master Inspector ®
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 10,752
Default Re: GFCI on 2 wire systems

I wouldn't say they prevent, but rather that they reduce the potential for someone to get shocked. People can always find ways to electrocute themselves.

Many older homes' electrical systems are not grounded, however, short of fully rewiring the house, GFCI can be an effective way of providing improved protection against shocks and maintain "code" compliance with three prong outlets (use the "no equipment ground" stickers).

As Mike said so succinctly, he can install them on most circuits for enhanced protection. Don't need to install on every outlet, just lead outlet on each circuit. Change the other outlets to three prog, install stickers and he's good to go.

Of course, I would advise him to use a qualified, licensed electrician to do the work vs. Bubba that handy guy.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
The Woodlands Home Inspections
Magnolia TX Home Inspections & Thermography


Houston, TX
_______________________
Awards Committee Member

SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #4  
Old 11/9/09, 7:34 PM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 74,991
Default Re: GFCI on 2 wire systems

Quote:
Originally Posted by cevans View Post
I wouldn't say they prevent, but rather that they reduce the potential for someone to get shocked. People can always find ways to electrocute themselves.
They prevent a fault current in excess of 5 mA from going through a person.

That is sufficient to prevent electrocution in most of the population.

Those at risk are ones that have a pathway via inter-venous lines or a compromise layer of skin.

GFCI outlets in non three wire systems need to be labeled appropriately.



As a Professional Home Inspector, I support the privacy of my clients.

You own your private information. I won't sell or give away yours, others do


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
  #5  
Old 11/9/09, 7:36 PM
Bob Elliott, 450.0002662's Avatar
Bob Elliott, 450.0002662 Bob Elliott, 450.0002662 is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2006
Location: Chicago
Posts: 37,739
Default Re: GFCI on 2 wire systems

Tim a grounded system is to protect the equipt and not you.

Not sure I would want a bunch of GFCI outlets with stickers everywhere that no one will pay attention to when they plug things in.

If this place has real conduit, a switch to grounded outlets is easy.
Reply With Quote
  #6  
Old 11/9/09, 7:37 PM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 74,991
Default Re: GFCI on 2 wire systems

Conduit in Iowa?

Come on Bob get real.



As a Professional Home Inspector, I support the privacy of my clients.

You own your private information. I won't sell or give away yours, others do


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
  #7  
Old 11/9/09, 7:39 PM
Bob Elliott, 450.0002662's Avatar
Bob Elliott, 450.0002662 Bob Elliott, 450.0002662 is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2006
Location: Chicago
Posts: 37,739
Default Re: GFCI on 2 wire systems

Quote:
Originally Posted by mlarson View Post
Conduit in Iowa?

Come on Bob get real.
Do you assume Mike? or have you been there.
I have not.

For all I know they are using Tesla coils to beam it all through space.
Reply With Quote
  #8  
Old 11/9/09, 7:41 PM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 74,991
Default Re: GFCI on 2 wire systems

Quote:
Originally Posted by belliott View Post
Do you assume Mike? or have you been there.
I have not.

For all I know they are using Tesla coils to beam it all through space.
Got relies their Bob.



As a Professional Home Inspector, I support the privacy of my clients.

You own your private information. I won't sell or give away yours, others do


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
  #9  
Old 11/9/09, 7:46 PM
Marcel Gratton, CMI's Avatar
Marcel Gratton, CMI Marcel Gratton, CMI is offline
Certified Master Inspector ®
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 4,424
Default Re: GFCI on 2 wire systems

Quote:
Originally Posted by mlarson View Post
They prevent a fault current in excess of 5 mA from going through a person.

That is sufficient to prevent electrocution in most of the population.

Those at risk are ones that have a pathway via inter-venous lines or a compromise layer of skin.

GFCI outlets in non three wire systems need to be labeled appropriately.
True, but GFCI's are not going to protect the 60" Plasma, microwave oven, computer, fridge,...



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #10  
Old 11/9/09, 8:16 PM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 74,991
Default Re: GFCI on 2 wire systems

Quote:
Originally Posted by mgratton View Post
True, but GFCI's are not going to protect the 60" Plasma, microwave oven, computer, fridge,...
Never said they were for equipment protection.

Follow the mfgs. instructions for appliances.



As a Professional Home Inspector, I support the privacy of my clients.

You own your private information. I won't sell or give away yours, others do


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
  #11  
Old 11/9/09, 8:49 PM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI on 2 wire systems

I'm sorry, but it really bugs me when people state that GFCI will reduce the risk of (or worse yet - prevent) electrical shocks.

GFCI PROTECTION DOES NOT REDUCE THE RISK OF ELECTRICAL SHOCKS!!!!!

They reduce the risk of death by electrocution, but have absolutly no affect on electrical shocks in general. A 5ma shock is still VERY painful (from what I have read).
Reply With Quote
  #12  
Old 11/9/09, 8:52 PM
Bob Elliott, 450.0002662's Avatar
Bob Elliott, 450.0002662 Bob Elliott, 450.0002662 is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2006
Location: Chicago
Posts: 37,739
Default Re: GFCI on 2 wire systems

Not really

Now 220 kinda bothers you.
110 just tickles.
Reply With Quote
  #13  
Old 11/9/09, 8:56 PM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI on 2 wire systems

Quote:
Originally Posted by belliott View Post
Not really

Now 220 kinda bothers you.
110 just tickles.
Have you ever tripped a GFCI with your body (across two fingers doesn't count)? I don't recommend trying it, but would be interested in hearing if anyone has.

From what I have heard, at least 220 will knock you off, unlike 110 which just makes your muscles hold tighter.
Reply With Quote
Find an InterNACHI certified Georgia Home Inspector (and anywhere else in North America)
  #14  
Old 11/9/09, 9:11 PM
Bob Elliott, 450.0002662's Avatar
Bob Elliott, 450.0002662 Bob Elliott, 450.0002662 is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2006
Location: Chicago
Posts: 37,739
Default Re: GFCI on 2 wire systems

I have been shocked many times ,so I do not count as I may have built an immunity.

In used to experiment from the time I was a kid.

None the less I would not depend on any devise to always do its job.(haven't we all inspected bad GFCI)?
Reply With Quote
  #15  
Old 11/9/09, 9:21 PM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 74,991
Default Re: GFCI on 2 wire systems

Resisting going there.



As a Professional Home Inspector, I support the privacy of my clients.

You own your private information. I won't sell or give away yours, others do


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Emergency Lighting (commercial) mcyr Electrical Inspections 26 6/20/14 11:00 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM