OK…Electricians…Go At It…explain article 250.130© and the options…
**VII. Methods of Equipment Grounding
250.130 Equipment Grounding Conductor Connections.
**Equipment grounding conductor connections at the source of
separately derived systems shall be made in accordance with
250.30(A)(1). Equipment grounding conductor connections at
service equipment shall be made as indicated in 250.130(A) or
(B). For replacement of non–grounding-type receptacles with
grounding-type receptacles and for branch-circuit extensions
only in existing installations that do not have an equipment
grounding conductor in the branch circuit, connections shall
be permitted as indicated in 250.130©.
**(A) For Grounded Systems. **The connection shall be
made by bonding the equipment grounding conductor to the
grounded service conductor and the grounding electrode
conductor.
**(B) For Ungrounded Systems. **The connection shall be
made by bonding the equipment grounding conductor to the
grounding electrode conductor.
© Nongrounding Receptacle Replacement or Branch
**Circuit Extensions. **
The equipment grounding conductor
of a grounding-type receptacle or a branch-circuit extension
shall be permitted to be connected to any of the following:
(1) Any accessible point on the grounding electrode system
as described in 250.50
(2) Any accessible point on the grounding electrode conductor
(3) The equipment grounding terminal bar within the enclosure
where the branch circuit for the receptacle or
branch circuit originates
(4) For grounded systems, the grounded service conductor
within the service equipment enclosure
(5) For ungrounded systems, the grounding terminal bar
within the service equipment enclosure
[size=3]FPN: See 406.3(D) for the use of a ground-fault circuitinterrupting
type of receptacle.
The idea of my lesson here was to go beyond the understanding that GFCI as the only option the client can have…don’t get me wrong…that is a great one…LOVE IT…but in the example we have an unfinished basement and plugs above…while it may cost more…if they truly want a EGC they have options…knowing them will not MAKE you quote them…it just helps you know their are options…now pulling it all out and rewiring the house is another option…however it will quite possibly be a more expensive option…dont know…virtual inspection…
But understanding that all the above can achieve and will also allow the use of a 3 prong plug…over an above to just the GFCI and Label option…know all the options because your client may really want to buy the house…and you want their best interests at heart…if their was an unfinished basement and open access to the floor above…or atleast some areas of the house…their are other options…and what they can’t get to…the GFCI is a good option as well…
The point of this…was to know their are other additonal options and how they are achieved…
Now I am sure the other fellow electricians are awaiting comments as well…