Default Metal switch on a breaker

I am not familiar with this switch that I found today. The breaker is for the dishwasher and has a small metal toggle that appears to keep the breaker from tripping?
The panel box was installed in 2004 when the home was built.
Can someone help me understand this idea? Is it OK?
Thanks.
Attached Thumbnails
Metal switch on a breaker-untitled-jpg   Metal switch on a breaker-panel1-jpg  
Reply With Quote
Find an InterNACHI certified Florida Home Inspector (and anywhere else in North America)
  #2  
Old 11/4/09, 4:22 PM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 75,379
Default Re: Metal switch on a breaker

Quote:
Originally Posted by khackworth View Post
I am not familiar with this switch that I found today. The breaker is for the dishwasher and has a small metal toggle that appears to keep the breaker from tripping?
The panel box was installed in 2004 when the home was built.
Can someone help me understand this idea? Is it OK?
Thanks.
It appears to be a spring not a switch.

The trip mechanism of breakers is internal so I doubt it keeps it from tripping.

It may be some type of lock out device though I have not seen one like your pic.



As a Professional Home Inspector, I support the privacy of my clients.

You own your private information. I won't sell or give away yours, others do


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
  #3  
Old 11/4/09, 4:27 PM
Kenney Hackworth's Avatar
Kenney Hackworth Kenney Hackworth is offline
Certified Professional Inspector (CPI)
 
Join Date: Sep 2009
Location: Norfolk, VA
Posts: 7
Default Re: Metal switch on a breaker

Thanks for the speedy reply, this device pivots freely on the middle so that the "L" shaped arm could be turned to the opposite side, which would not keep the breaker switch from moving.
When I saw the metal arm it was engaged in a manner that would stop the breaker switch from moving to either the middle tripped position or the off position.
Reply With Quote
  #4  
Old 11/4/09, 5:43 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
Certified Master Inspector
 
Join Date: Oct 2004
Location: Michigan
Posts: 1,121
Send a message via Skype™ to gwells
Default Re: Metal switch on a breaker

Locks on breakers are more common in commercial panels than residential but there is nothing wrong with having it there. There may be a circuit (such as emergency lighting) that you don't want anyone to turn off but the breaker still does its job of protecting the circuit. Locks can also be used to prevent someone from turning on a breaker that you may not want to have turned on.

Quote:
Originally Posted by khackworth View Post
I am not familiar with this switch that I found today. The breaker is for the dishwasher and has a small metal toggle that appears to keep the breaker from tripping?
The panel box was installed in 2004 when the home was built.
Can someone help me understand this idea? Is it OK?
Thanks.



Forensic Electrical Consultant
EE, Licensed Master Electrician/Electrical Contractor



BestInspectors.Net
By Inspectors, For Inspectors

Inspection Report Software
& Business Coaching


Since 1992
Reply With Quote
  #5  
Old 11/4/09, 8:15 PM
Kenney Hackworth's Avatar
Kenney Hackworth Kenney Hackworth is offline
Certified Professional Inspector (CPI)
 
Join Date: Sep 2009
Location: Norfolk, VA
Posts: 7
Default Re: Metal switch on a breaker

Thanks for the help, I will note the lock on the report as an FYI for the buyer.
Reply With Quote
  #6  
Old 11/6/09, 7:41 PM
Robert Sole, CMI's Avatar
Robert Sole, CMI Robert Sole, CMI is offline
Certified Master Inspector
 
Join Date: Jun 2007
Location: Winter Park, Fl
Posts: 739
Default Re: Metal switch on a breaker

These are usually used on circuits such as to the dishwasher where the device is direct wired. It is so the person working on the device can shut the breaker off and flip the lock over to prevent it from accidentally being turned back on. Most of the ones now are designed so that a lock can be installed to protect it further.

Many areas are requiring these now.



Robert Sole, CMI



407-637-7288


Florida license numbers HI 169 and MRSA 92

Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

Check out my blog orlandohomeinspections.info/
REMinspections.com
OrlandoHomeInspector.net
OviedoHomeInspector.net
Reply With Quote
  #7  
Old 11/6/09, 7:45 PM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 75,379
Default Re: Metal switch on a breaker

Quote:
Originally Posted by rsole View Post
These are usually used on circuits such as to the dishwasher where the device is direct wired. It is so the person working on the device can shut the breaker off and flip the lock over to prevent it from accidentally being turned back on. Most of the ones now are designed so that a lock can be installed to protect it further.

Many areas are requiring these now.
That makes sense as I see the other on is a 2-pole breaker and is probably for the water heater.



As a Professional Home Inspector, I support the privacy of my clients.

You own your private information. I won't sell or give away yours, others do


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
  #8  
Old 11/11/09, 1:06 AM
Paul Dickerson Paul Dickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Metal switch on a breaker

Just to be clear, a circuit breaker WILL trip and cut power to a circuit even if the breaker handle is held or locked in the "on" position. If it trips in this manner, you have to switch it to the "off" position and back to "on" to reset it.
Reply With Quote
  #9  
Old 11/11/09, 1:23 AM
Mark E. Northrup's Avatar
Mark E. Northrup Mark E. Northrup is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Oregon
Posts: 480
Default Re: Metal switch on a breaker

Quote:
Originally Posted by rsole View Post
These are usually used on circuits such as to the dishwasher where the device is direct wired. It is so the person working on the device can shut the breaker off and flip the lock over to prevent it from accidentally being turned back on. Most of the ones now are designed so that a lock can be installed to protect it further.

Many areas are requiring these now.
These type of locks are in use here alot and Mr. Sole is correct they are used to keep someone from turning on the breaker and shocking the repairman.





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing, Ethics & Legal Issues for Inspectors 52 7/11/17 3:34 PM
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Operating a Switch or Breaker Handle jtedesco1 Electrical Inspections 7 12/21/07 1:49 PM
Double pole breaker, metal showing between sections lfoster Electrical Inspections 2 9/6/07 12:25 PM

All times are GMT -4. The time now is 9:47 PM.
no new posts