Overhead SEC cable weatherhead

Does anyone have an image showing a proper install, as far as the neutral wire? Is this how the neutral wire is supposed to be? There are/were only 2 “covered” holes for the hot legs. Wouldn’t this leave the wire susceptible to moisture intrusion as the exterior SEC cable sleeve is exposed? TIA.

You’re correct the neutral should fold over above the clamp to keep water from entering the cable. You can see the slot below the insulator.

Ahh. TY, sir.