  #1  
Old 11/17/12, 1:24 AM
William T. Misegades William T. Misegades is offline
Certified Professional Inspector (CPI)
 
Join Date: Jun 2011
Location: Houston, TX
Posts: 2,745
Default overhead service drop height

Hey guys,
When did the overhead service drop height rule come into effect?
I noted the service drop conductors that were well under 10 feet above a walkway on a 50 year old home and the seller (who happens to be a lawyer) rebuked that and said this is ok because it is grand fathered in... I don't want to debate about inspecting according to today's standards or when my city specifically adopted this rule or even the safety issue at steak in this instance. I just want to know when it was first written in any of the code books. Any help would be much appreciated! Thanks



Where there is a Will there is a Way!

Will Misegades
TREC# 10465
RedFish Home Inspections

www.redfishinspections.com
Infraspection Institute Certified Infrared Thermographer Level I # 9631
"it's not just about how to turn on and tune the camera to make pretty colored spots!"
David A. Andersen, Woodlawn, TN
Reply With Quote
Need a home inspection in Kentucky? Check out InterNACHI's listing of Kentucky certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/17/12, 5:18 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2007
Location: Minnesota & Northern Iowa
Posts: 30,246
Default Re: overhead service drop height

Call your POCO as they decide what they want for their Service Drop in any given area. The code is just a nuisance/suggestion to them that they care nothing about.



Jeffrey R. Jonas
Owatonna, Minnesota



"I am not a teacher, but an awakener."
- Robert Frost, American poet (1874-1963).

"We Respect Our Clients Right to Privacy"

Reply With Quote
  #3  
Old 11/17/12, 9:05 AM
Gerald L. Coy Gerald L. Coy is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Nov 2012
Location: Webster, NY
Posts: 92
Default Re: overhead service drop height

If you think this is a safety issue report it as same. Don't get involved in a calling it a code violation you'll lose that argument. Remember building and electrical codes are the minimum acceptable requirements. If your standards are higher than the minimum acceptable years ago state it as such!
Reply With Quote
  #4  
Old 11/17/12, 9:20 AM
William T. Misegades William T. Misegades is offline
Certified Professional Inspector (CPI)
 
Join Date: Jun 2011
Location: Houston, TX
Posts: 2,745
Default Re: overhead service drop height

Guys, thanks for your input and really, I do appreciate it. Sometimes, all people want is formation. I inspect house to today's standards and write that in the report, so the seller knows about that. I did not ask this questions to get into a debate of how to inspect or how to report things, thus the reason why i posted the question the way I did. I would just like to know when the height for the service feeder was originally written up so that next time, I can simply give that info directly when questioned (on top of the fact that it is a safety hazard matter when the code was adopted).
Jeff, I'll give the POCO a call next week and post their answer.



Where there is a Will there is a Way!

Will Misegades
TREC# 10465
RedFish Home Inspections

www.redfishinspections.com
Infraspection Institute Certified Infrared Thermographer Level I # 9631
"it's not just about how to turn on and tune the camera to make pretty colored spots!"
David A. Andersen, Woodlawn, TN
Reply With Quote
  #5  
Old 11/17/12, 9:34 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2007
Location: Minnesota & Northern Iowa
Posts: 30,246
Default Re: overhead service drop height

Will, I understood exactly your question and reasoning behind asking it as written. You need to understand that you are about to get yourself in a heep of potential trouble with the Seller/Lawyer! DO NOT play into his game. Offering any CODE FACT (which is impossible to determine for grandfathering purposes in your situation) is a very bad idea, and will open up every comment you make to his interpretation and approval. Prepare your comments as you always do, and let HIM deal with the POCO and AHJ!



Jeffrey R. Jonas
Owatonna, Minnesota



"I am not a teacher, but an awakener."
- Robert Frost, American poet (1874-1963).

"We Respect Our Clients Right to Privacy"

Reply With Quote
  #6  
Old 11/18/12, 9:49 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
Certified Master Inspector ®
 
Join Date: Sep 2005
Location: McKinney, TX
Posts: 9,731
Send a message via Skype™ to pabernathy
Default overhead service drop height

Some wise advice from jjonas on this one. The height if "service drop" conductors is a NESC rule for the POCO and not the NEC as you have presented it. Note it, advise them to contact the POCO for clarity and move on.



Paul W. Abernathy, CMECP
Website - http://www.masterthenec.com
Twitter - https://twitter.com/MasterTheNEC
Facebook -https://www.facebook.com/masterthenec/
Spreaker PodCasts - https://www.spreaker.com/show/master-the-necs-tracks


Disclaimer - All my posts on this forum represent Electrical Code Academy, Inc.
Reply With Quote
  #7  
Old 11/18/12, 8:30 PM
William T. Misegades William T. Misegades is offline
Certified Professional Inspector (CPI)
 
Join Date: Jun 2011
Location: Houston, TX
Posts: 2,745
Default Re: overhead service drop height

Mike, thanks for that link. And your last comment was what I was also thinking.
Jeff I know you know and you know I value your answers and your answer on post#2 was good info.
Paul, thanks for your answer which confirmed Jeff's post#2.
So now I have a question. I presented 10' rule because that's what is in the IRC, NEC, not knowing the NESC would be any different.
Why would the NEC and IRC give a rule for vertical clearance above grade, if that same rule didn't apply to NESC which is the body that governs the service drop requirements?



Where there is a Will there is a Way!

Will Misegades
TREC# 10465
RedFish Home Inspections

www.redfishinspections.com
Infraspection Institute Certified Infrared Thermographer Level I # 9631
"it's not just about how to turn on and tune the camera to make pretty colored spots!"
David A. Andersen, Woodlawn, TN
Reply With Quote
  #8  
Old 11/18/12, 8:56 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 3,172
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: overhead service drop height

The utility company might have the same requirements as the ones outlined in the NEC but the NEC likely doesn't apply to the service drop. Basically it comes down to who you would look to for correction of the issue. From the 2011 NEC:

Quote:
90.2 Scope.
(B) Not Covered. This Code does not cover the following:
(1) Installations in ships, watercraft other than floating build-
ings, railway rolling stock, aircraft, or automotive vehicles
other than mobile homes and recreational vehicles
Informational Note: Although the scope of this Code in-
dicates that the Code does not cover installations in ships,
portions of this Code are incorporated by reference into
Title 46, Code of Federal Regulations, Parts 110–113.
(2) Installations underground in mines and self-propelled
mobile surface mining machinery and its attendant
electrical trailing cable
(3) Installations of railways for generation, transformation,
transmission, or distribution of power used exclusively
for operation of rolling stock or installations used ex-
clusively for signaling and communications purposes
(4) Installations of communications equipment under the
exclusive control of communications utilities located
outdoors or in building spaces used exclusively for
such installations
(5) Installations under the exclusive control of an electric
utility where such installations
a. Consist of service drops or service laterals, and as-
sociated metering
,
Reply With Quote
  #9  
Old 4/4/18, 11:41 PM
Bob, HI-4280  Bob, HI-4280 is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Oct 2017
Posts: 11
Default Re: overhead service drop height

Poco ?
Reply With Quote
  #10  
Old 4/5/18, 2:57 AM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
Certified Professional Inspector (CPI)
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 10,337
Default Re: overhead service drop height

The few times I have dealt with the POCO and mentioned "code", they either snickered or laughed out loud. One of the old lineman that was replacing my failed service drop kept laughing. When he finished, we talked and his comment was, "we supply the power under our rules". No building official around here tells us when, where or how to run our lines. Probably why my service drop is still attached to insulators on the roof surface.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Kitsap County
Reply With Quote
  #11  
Old 4/5/18, 4:46 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 3,172
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: overhead service drop height

Quote:
Originally Posted by bbob View Post
Poco ?
POwer COmpany, AKA POCO or electrical utility company.
Reply With Quote
  #12  
Old 4/5/18, 11:52 AM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Jun 2005
Location: Nashville, TN
Posts: 10,469
Default Re: overhead service drop height

Quit playing lawyer with a ****ing lawyer!

Report what you see. Let someone else work it out. It's not your job to make anyone do anything...

Put your Barney Fife badge away and be a home inspector, and quit acting like one.

Your client is the only 'authority' in a Home Inspection.
I wish someone would teach this ****.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40 (Retired)
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
HVAC Certification EPA Cert#2046620
BPI# 5015804
Reply With Quote
  #13  
Old 4/8/18, 10:40 PM
Don C. Hawley Don C. Hawley is online now
Certified Professional Inspector (CPI)
 
Join Date: Feb 2016
Location: Pocahontas, IL
Posts: 180
Default Re: overhead service drop height



Would you report this as to low?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Larger wires at service drop mtimpani Electrical Inspections 35 11/29/14 5:59 PM
Electricians Check List pabernathy Electrical Inspections 75 1/6/14 7:19 AM
Overhead service cable? crichiii Electrical Inspections 3 3/24/09 11:42 PM
Service Drop and SEC jpope Electrical Inspections 11 1/14/06 11:15 PM

All times are GMT -4. The time now is 11:48 AM.
no new posts