Default Two Panels - Two Main Breakers?

I saw a detatched house with two main Service Panels side by side today - neither was a sub. Both fed off the meter. Is this common? Anything I need to be aware of when inspecting these or is it just two panels?
Attached Thumbnails
Two Panels - Two Main Breakers?-20140908_132037-jpg  
Reply With Quote
Need a home inspection in Texas? Check out InterNACHI's listing of Texas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/8/14, 7:09 PM
Michael Koester's Avatar
Michael Koester Michael Koester is offline
Certified Professional Inspector (CPI) ®
 
Join Date: May 2014
Location: Sarasota, FL
Posts: 678
Default Re: Two Panels - Two Main Breakers?

Sorry for the crappy pictures. I'll have a decent camera soon.
Reply With Quote
  #3  
Old 9/8/14, 7:14 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 3,199
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two Panels - Two Main Breakers?

Common for larger homes require more than a 200 amp service.
Reply With Quote
  #4  
Old 9/8/14, 7:17 PM
Michael Koester's Avatar
Michael Koester Michael Koester is offline
Certified Professional Inspector (CPI) ®
 
Join Date: May 2014
Location: Sarasota, FL
Posts: 678
Default Re: Two Panels - Two Main Breakers?

So do they usually just "double tap" off the meter as this case appeared to be? It was underground service and the meter was on the other side of the wall of where they were mounted. I know this is not a double tap that gets written up - just asking.
Reply With Quote
  #5  
Old 9/8/14, 7:21 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 3,199
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Two Panels - Two Main Breakers?

Typically you will have a double lugs at the meter listed for two conductors so it's not really a "double tap".
Reply With Quote
  #6  
Old 9/8/14, 7:25 PM
Michael Koester's Avatar
Michael Koester Michael Koester is offline
Certified Professional Inspector (CPI) ®
 
Join Date: May 2014
Location: Sarasota, FL
Posts: 678
Default Re: Two Panels - Two Main Breakers?

Okay, thanks Robert.
Reply With Quote
  #7  
Old 9/8/14, 8:23 PM
Michael A. Clark, CMI's Avatar
Michael A. Clark, CMI Michael A. Clark, CMI is offline
Certified Master Inspector
 
Join Date: Apr 2012
Location: Almost Heaven, WV
Posts: 6,948
Default Re: Two Panels - Two Main Breakers?

Like Robert said, it's not double tapped-it's double lugged at the meter base.

Be sure and check the meter to verify the service.

(2) 200 amp panels don't always mean 400 amp service.




Michael A Clark, Certified Master Inspector«
Inspection Connection
St Albans, West Virginia

"Always tell the truth,
do what you say you will,
and do it Righter than Right...Always"

Facebook

Google Plus

www.charleston-home-inspector.com
www.icwvhomes.com

mclark@icwvhomes.com
Reply With Quote
  #8  
Old 9/8/14, 8:44 PM
Michael Koester's Avatar
Michael Koester Michael Koester is offline
Certified Professional Inspector (CPI) ®
 
Join Date: May 2014
Location: Sarasota, FL
Posts: 678
Default Re: Two Panels - Two Main Breakers?

How would two 200A panels not equal 400A? Can the amperage coming in through the service entrance cables be less than 400A?
Reply With Quote
  #9  
Old 9/8/14, 9:03 PM
Christopher Currins, CMI Christopher Currins, CMI is offline
Certified Master Inspector ®
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 17,445
Default Re: Two Panels - Two Main Breakers?

If there is no disconnect at meter or before the panels, what you have is two 200 amp service panels.
Reply With Quote
  #10  
Old 9/8/14, 9:08 PM
Bradley K. Toye, CMI's Avatar
Bradley K. Toye, CMI Bradley K. Toye, CMI is online now
Certified Master Inspector
 
Join Date: Sep 2010
Location: Clearwater, FL
Posts: 5,279
Default Re: Two Panels - Two Main Breakers?

Quote:
Originally Posted by ccurrins View Post
If there is no disconnect at meter or before the panels, what you have is two 200 amp service panels.
Wouldn't that be a 400A service?



Brad K Toye
ITC/FLIR Level I Building Investigation Thermographer
FL Certified Building Contractor CBC034303
FL Certified Home Inspector HI 391
FL Certified Mold Assessor MRSA 589

727-403-5029
Lecsi2@gmail.com
www.LeadingEdgeInspectionServices.com
Reply With Quote
  #11  
Old 9/8/14, 9:38 PM
Kenneth A. Ramm Kenneth A. Ramm is offline
Certified Professional Inspector (CPI)
 
Join Date: Oct 2012
Location: New Glarus, WI
Posts: 3,783
Default Re: Two Panels - Two Main Breakers?

Yes its a 400amp service coming in to a 320 meter base or should be.



Kenneth (Kenny) Ramm
608-438-3986
RammHomeInspections@gmail.com
Wisconsin License 2516-106
InterNACHI #12101905
Level II Infraspection Institute Certified Infrared Thermographer #10786

"If you want to live a happy life, tie it to a goal, not to people or objects." Albert Einstein
Reply With Quote
  #12  
Old 9/8/14, 9:47 PM
Larry Kage, CMI's Avatar
Larry Kage, CMI Larry Kage, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: NW, MI
Posts: 17,325
Default Re: Two Panels - Two Main Breakers?

Quote:
Originally Posted by ccurrins View Post
If there is no disconnect at meter or before the panels, what you have is two 200 amp service panels.
I agree.

Quote:
Originally Posted by btoye View Post
Wouldn't that be a 400A service?
SEC could be sized differently.




Awards Committee Officer
SUBMIT YOUR AWARD NOMINATIONS HERE:
http://co.nachi.org/inachiawards/

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
____________________________________________

Larry Kage, CMI Lifetime Member
State Licensed Builder since 1973
InterNACHI Lifetime Member
~retired~

The above post represents my personal opinion.
Reply With Quote
  #13  
Old 9/8/14, 10:01 PM
Michael A. Clark, CMI's Avatar
Michael A. Clark, CMI Michael A. Clark, CMI is offline
Certified Master Inspector
 
Join Date: Apr 2012
Location: Almost Heaven, WV
Posts: 6,948
Default Re: Two Panels - Two Main Breakers?

Quote:
Originally Posted by btoye View Post
Wouldn't that be a 400A service?
It depends on the meter rating. It's probably 320 like Kenneth said.




Michael A Clark, Certified Master Inspector«
Inspection Connection
St Albans, West Virginia

"Always tell the truth,
do what you say you will,
and do it Righter than Right...Always"

Facebook

Google Plus

www.charleston-home-inspector.com
www.icwvhomes.com

mclark@icwvhomes.com
Reply With Quote
Need a home inspection in Texas? Check out InterNACHI's listing of Texas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 9/9/14, 6:21 AM
Michael Koester's Avatar
Michael Koester Michael Koester is offline
Certified Professional Inspector (CPI) ®
 
Join Date: May 2014
Location: Sarasota, FL
Posts: 678
Default Re: Two Panels - Two Main Breakers?

This base states 320A continuous & 400A maximum (burst).

http://www.homedepot.com/p/Milbank-3...-5T9/202504264
Reply With Quote
  #15  
Old 9/9/14, 8:11 AM
Kenneth A. Ramm Kenneth A. Ramm is offline
Certified Professional Inspector (CPI)
 
Join Date: Oct 2012
Location: New Glarus, WI
Posts: 3,783
Default Re: Two Panels - Two Main Breakers?

Quote:
Originally Posted by mkoester View Post
This base states 320A continuous & 400A maximum (burst).
http://www.homedepot.com/p/Milbank-3...-5T9/202504264
This is what should be there as per your question, 400amp noncontinuous 320amp continuous.
So for a 200amp service the meter base is 200amp noncontinuous 160amp continuous
This is how meters are rated.
So per your question 2-200amp panels do not make 400 amps, it's the service coming in that should be 400 amps as Larry mentioned and then split off with 4/0 aluminum or 2/0 copper to the panels from the meter base, then you have your 2/200amp panels with main breakers.



Kenneth (Kenny) Ramm
608-438-3986
RammHomeInspections@gmail.com
Wisconsin License 2516-106
InterNACHI #12101905
Level II Infraspection Institute Certified Infrared Thermographer #10786

"If you want to live a happy life, tie it to a goal, not to people or objects." Albert Einstein
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main panel and Sub panels wmisegades Electrical Inspections 6 11/8/11 2:30 PM
Zinsco Main and Sub panels dmcmullen Electrical Inspections 3 4/13/11 9:17 PM
Electric Panel dmozzillo Electrical Inspections 26 1/26/09 1:18 PM
SEC and panels also CEU course material dhostetter Electrical Inspections 3 10/3/08 5:49 PM
Shut off valves required? jcahill Plumbing Inspections 11 9/2/08 1:07 AM

All times are GMT -4. The time now is 11:41 AM.
no new posts