Default Re: What would you say on your report?

Quote:
Originally Posted by kwood View Post
I am waiting for the ESA because I do not have the code in which you state has the Closet removed. This has not been displayed on the InspectionNews or here. I take great care to make sure I have what I stated in front of me. It has not changed and is still the same.
Raymond did state the code via a ESA blog but no one has produced the one we should be using on Home Inspection and even if they did I have already stated I protect clients only so the strictest code I can find is the way I present my reports whether that be CANADA, ONTARIO or US.
Obviously from the posts I here on the InterNachi site many do not!
You don't have a copy, but you know it has changed? What is wrong with the posting of the Articles from the codebook? Do you think the ESA has a secret book?
Reply With Quote
Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #107  
Old 7/16/12, 12:58 AM
Cameron Anderson's Avatar
Cameron Anderson Cameron Anderson is offline
Certified Professional Inspector (CPI)
 
Join Date: Nov 2011
Location: Peoria, IL
Posts: 6,989
Default Re: What would you say on your report?

ahhhhh! I can't keep up! I'm three pages back and the pages keep appearing!



Cameron Anderson
Integrity Home Inspection
Truth. In Real Estate.
Since 2004
Bachelor of Architecture, U of I, Urbana IL
Illinois Licensed Inspector

www.homeinspectionpeoria.com
Reply With Quote
  #108  
Old 7/16/12, 1:38 AM
Tyler Knelsen Tyler Knelsen is offline
Community Guest
 
Join Date: Jun 2008
Location: Alberta
Posts: 147
Default Re: What would you say on your report?

Kevin, the many comments in this thread from several very knowledgeable people have nothing to do with, as you stated, forcing opinions on or displaying a lack of respect for Canadians. There are many people here who are simply trying to point out the errors in your statements but you refuse to admit that you're wrong.

Jeffrey Pope is one of the most knowledgeable inspectors on this board and has helped many that have had electrical questions. However, you continually speak down to him and others as though you believe you are superior.

Stop trying to twist this thread into an attack on Canadians in an attempt to divert the focus off of you. You don't speak for me and I find your comments to be an embarrassment to this profession.



Welcome Home Inspections
Home Inspections, Commercial Inspections, and Infrared Inspections for Edmonton, Leduc, Sherwood Park, Wetaskiwin and Camrose.
Edmonton Home Inspector

Last edited by tknelsen; 7/16/12 at 12:36 PM..
Reply With Quote
  #109  
Old 7/16/12, 9:36 AM
KEVIN WOOD, CMI KEVIN WOOD, CMI is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,820
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What would you say on your report?

Tyler I do not now you but if you go to the CANADIAN ONLY section you will find the CODE Rule there.
Need further assistance go to OntarioAchi.ca and post info or e-mail me directly.
Reply With Quote
  #110  
Old 7/16/12, 9:57 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2007
Location: Minnesota & Northern Iowa
Posts: 30,889
Default Re: What would you say on your report?

I needed a chuckle to start my day, so I decided to go over to Kevvy's other association forum and see what's up...

I believe the link in this post of his explains everything very well...

Quote:
Originally Posted by kevin wood-ACHI Forum
Do you report outlets in Closets.
It has been pointed out that nothing is against putting one in a closet.
I always point out the DANGER does anyone else do this?

http://www.dslreports.com/forum/r2118596...-in-closet

Since I did not get a response I thaught I better put this in as it caused allot of confusion on another MB.
If anyone has the complete wording as per 26-702 can you post it?

CANADIAN ELECTRICAL CODE
Closets, Cupboards, Cabinets ect.

26-710 (i) prohibits plugs outlets in these enclosures exept for special cavities built for specific heating and non heating type appliances.

Like I said I don't like to mention CODE but safety only.

I am only doing this for XXXX because he has pointed out he does not have the CEC with him.
Note: His comment about no response (above) is in regards to NO-ONE having posted a reply to his posting on his own MB.
http://forums.ontarioachi.ca/Thread-Outlets-in-Closets



Jeffrey R. Jonas
Owatonna, Minnesota



"I am not a teacher, but an awakener."
- Robert Frost, American poet (1874-1963).

"We Respect Our Clients Right to Privacy"

Reply With Quote
  #111  
Old 7/16/12, 10:04 AM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 74,047
Default Re: What would you say on your report?

Quote:
Originally Posted by kwood View Post
Tyler I do not now you but if you go to the CANADIAN ONLY section you will find the CODE Rule there.
Need further assistance go to OntarioAchi.ca and post info or e-mail me directly.
You mean the one you still haven't told us whee it came from.

Go look at the real one I posted.



As a Professional Home Inspector, I support the privacy of my clients.

You own your private information. I won't sell or give away yours, others do


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
  #112  
Old 7/16/12, 10:26 AM
KEVIN WOOD, CMI KEVIN WOOD, CMI is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,820
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What would you say on your report?

Posted in the Canadian Only section!
Reply With Quote
  #113  
Old 7/16/12, 10:43 AM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 600
Default Re: What would you say on your report?

Come on now guys I know that you all can understand the dangers of a receptacle in a closet.

I installed a receptacle in a coat closet that was 48 by 24 inches. The lady of the house called me as she was having problems with this receptacle and needed it fixed. When I arrived at her home I found plug strips daisy chained with the following appliances plugged in; coffee pot, toaster, deep fryer, micro wave, and an iron.

After explaining to her the dangers of having an iron plugged in she relented and replaced the iron with a portable electric heater. Now everything is alright.

Boy talking about a big scare, I was sure that that iron was going to be the end of life as we know it. She understands that no cord can pass through the door as this might not let the door close and this would be really bad should the kids come home from school and start poking coat hangers into that plug.

Even though this was an American installation I referred her to the CEC and the dangers of having an iron plugged into a receptacle in a clothes closet. She was very adamant about this being a coat closet but she finally relented to the dangers. She ask if she installed some sort of fire suppression system could she keep the appliances plugged into that receptacle. I don’t think that the CEC will even allow this so I now ask the question should she have a barrel of water and a bucket in that closet will it still pose a danger.

On a side note, I would have posted this in one of those links outlined above but in order to do this I must join and this ain’t going to happen.



Mike Whitt
Contractor/Instructor
Reply With Quote
  #114  
Old 7/16/12, 11:35 AM
Harold Robinson Harold Robinson is offline
InterNACHI Member
 
Join Date: Jun 2012
Location: Miami, Fl
Posts: 105
Default Re: What would you say on your report?

Good read!! Very entertaining. By the way...There is also a double tap in this pic that no one has commented on. at least it looks like one.



Advantage Home Inspections, Inc
863-228-2801
Reply With Quote
  #115  
Old 7/16/12, 11:46 AM
Juan C. Jimenez Juan C. Jimenez is offline
Certified Professional Inspector (CPI)
 
Join Date: Jan 2012
Location: central va
Posts: 7,690
Default Re: What would you say on your report?

Quote:
Originally Posted by hrobinson View Post
Good read!! Very entertaining. By the way...There is also a double tap in this pic that no one has commented on. at least it looks like one.
I saw Two but I didn't feel the need to distract anyone from this train wreck



Juan Jimenez
A House on a Rock Home Inspections LLC
God. Family. Home.
804-269-4321
Richmond Home Inspector
Richmond Chimney Sweep
Richmond Radon Testing


Reply With Quote
  #116  
Old 7/16/12, 12:21 PM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
Certified Master Inspector ®
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 15,302
Default Re: What would you say on your report?

Quote:
Originally Posted by hrobinson View Post
Good read!! Very entertaining. By the way...There is also a double tap in this pic that no one has commented on. at least it looks like one.
Quote:
Originally Posted by jpope View Post
You are correct Juan... Other than a double-tapped breaker, I see no other apparent issues.
I saw only one Juan. Do you see another?

As far as I'm concerned, the train wreck is over. Time to pick up the pieces and move on



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE «

Jeff Pope
JPI Home Inspection Service
(661) 212-0738
Los Angeles, Santa Clarita & Antelope Valley CA
Reply With Quote
  #117  
Old 7/16/12, 12:22 PM
Harold Robinson Harold Robinson is offline
InterNACHI Member
 
Join Date: Jun 2012
Location: Miami, Fl
Posts: 105
Default Re: What would you say on your report?

True. Haha!! When Kevin first mentioned other problems I thought that was what he was refuring to. Maybe he missed that problem.


I geuss you did mention it Jeff My apologies.



Advantage Home Inspections, Inc
863-228-2801
Reply With Quote
  #118  
Old 7/16/12, 12:25 PM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
Certified Master Inspector ®
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 15,302
Default Re: What would you say on your report?

With all the nonsense in this thread (mine included) there are still a few things that can be learned from it. Everything from about page 3 on is for "entertainment purposes only."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE «

Jeff Pope
JPI Home Inspection Service
(661) 212-0738
Los Angeles, Santa Clarita & Antelope Valley CA
Reply With Quote
Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #119  
Old 10/19/18, 3:35 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
Certified Professional Inspector (CPI)
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 10,513
Default Re: What would you say on your report?

Came across this thread from many years ago and couldn't stop laughing. For the newbies that haven't seen this, consider it a lesson in humility and learning to admit you were wrong.....




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)

RETIRED


Pierce County -Thurston County - King County - Kitsap County
Reply With Quote
  #120  
Old 10/19/18, 9:25 PM
Christopher Currins, CMI Christopher Currins, CMI is offline
Certified Master Inspector ®
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 17,591
Default Re: What would you say on your report?

Quote:
Originally Posted by sstanczyk View Post
Came across this thread from many years ago and couldn't stop laughing. For the newbies that haven't seen this, consider it a lesson in humility and learning to admit you were wrong.....
So are you starting a campaign to bring KW back?

Good times.......
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Regarding providing a copy of the report to agents and the seller.... gromicko Legislation, Licensing, Ethics & Legal Issues for Inspectors 2 2/6/10 9:24 PM
**HOT** Texas Inspectors use of REI-7A-0 escanlan Legislation, Licensing, Ethics & Legal Issues for Inspectors 27 11/20/07 1:09 AM
New Report Upload Technology cdemsky Miscellaneous Discussion for Inspectors 49 5/1/07 11:19 AM

All times are GMT -4. The time now is 9:40 PM.
no new posts