Default Split bus double tap

I noted several issues with this split bus electrical panel but there is one issue I would like some help with.The 70 amp breaker for the lower breakers is double tapped. Simple question, Why? What would the thinking behind this be?
Attached Thumbnails
Split bus double tap-dscn0824-jpg   Split bus double tap-dscn0827-jpg  



David

InterNACHI Certified Home Inspector #08051301
NYS Licensed Home Inspector #16000038229
NYS DEC Certified Pest Technician # T4865884
518-505-8305
HouseAbout Home Inspections, LLC
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI
Connect on LinkedIn
Follow HouseAbout_LinkedIn
Follow me on Twitter
HouseAbout_Instagram
Google+
Reply With Quote
Need a home inspection in District Of Columbia? Check out InterNACHI's listing of District Of Columbia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/17/19, 1:01 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 2,690
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Split bus double tap

Simply out of breaker space and using the lighting main to power additional circuits.
Reply With Quote
  #3  
Old 2/17/19, 3:00 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 3,295
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Split bus double tap

Quote:
Originally Posted by dokeefe View Post
I noted several issues with this split bus electrical panel but there is one issue I would like some help with.The 70 amp breaker for the lower breakers is double tapped. Simple question, Why? What would the thinking behind this be?

Interesting find, do you have a cat # for that panel because the spit bus conductors appear to be factory.



Also there are many other violations besides the double tap including more than 6 throws of the hand for the main circuit breakers.
Reply With Quote
  #4  
Old 2/17/19, 4:31 PM
David OKeefe's Avatar
David OKeefe David OKeefe is offline
Certified Professional Inspector (CPI)
 
Join Date: May 2008
Location: Delmar, NY ★ New York's Capital Region
Posts: 1,936
Default Re: Split bus double tap

Quote:
Originally Posted by Jim Port View Post
Simply out of breaker space and using the lighting main to power additional circuits.
What additional circuits? All conductors on the double tap go to the bottom (lighting) bus.



David

InterNACHI Certified Home Inspector #08051301
NYS Licensed Home Inspector #16000038229
NYS DEC Certified Pest Technician # T4865884
518-505-8305
HouseAbout Home Inspections, LLC
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI
Connect on LinkedIn
Follow HouseAbout_LinkedIn
Follow me on Twitter
HouseAbout_Instagram
Google+
Reply With Quote
  #5  
Old 2/17/19, 4:34 PM
David OKeefe's Avatar
David OKeefe David OKeefe is offline
Certified Professional Inspector (CPI)
 
Join Date: May 2008
Location: Delmar, NY ★ New York's Capital Region
Posts: 1,936
Default Re: Split bus double tap

Quote:
Originally Posted by Robert Meier View Post
Interesting find, do you have a cat # for that panel because the spit bus conductors appear to be factory.



Also there are many other violations besides the double tap including more than 6 throws of the hand for the main circuit breakers.
I found no labeling for the panel. Yes, I noted the other defects, just didn't understand this double tap as all conductors run to the bottom of the lighting circuit.Could the double tap be powering the added breakers on the right?



David

InterNACHI Certified Home Inspector #08051301
NYS Licensed Home Inspector #16000038229
NYS DEC Certified Pest Technician # T4865884
518-505-8305
HouseAbout Home Inspections, LLC
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI
Connect on LinkedIn
Follow HouseAbout_LinkedIn
Follow me on Twitter
HouseAbout_Instagram
Google+
Reply With Quote
  #6  
Old 2/17/19, 4:38 PM
David OKeefe's Avatar
David OKeefe David OKeefe is offline
Certified Professional Inspector (CPI)
 
Join Date: May 2008
Location: Delmar, NY ★ New York's Capital Region
Posts: 1,936
Default Re: Split bus double tap

There are 6 added 20 amp breakers in the panel that are just for 6 outlets in the basement. Each breaker powers one outlet.
And another oddity is that there a 3 GFCI outlets and 3 non GFCI outlets. All basement outlets.
Attached Thumbnails
Split bus double tap-dscn0823-jpg  



David

InterNACHI Certified Home Inspector #08051301
NYS Licensed Home Inspector #16000038229
NYS DEC Certified Pest Technician # T4865884
518-505-8305
HouseAbout Home Inspections, LLC
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI
Connect on LinkedIn
Follow HouseAbout_LinkedIn
Follow me on Twitter
HouseAbout_Instagram
Google+
Reply With Quote
  #7  
Old 2/17/19, 5:25 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is online now
Certified Master Inspector ®
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 10,884
Default Re: Split bus double tap

Interesting find. I have no insights for you. Both pairs definitely feed the lighting circuits.

At least you have plenty of other things that warrant repair so it's not like it all hinges on that alone. Just add it to the laundry list of defects along with the mixed breaker types and shared neutral from the half-height breaker in slot 6 and all the other crap...



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
The Woodlands Home Inspections
Magnolia TX Home Inspections & Thermography


Houston, TX
_______________________
Awards Committee Member

SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #8  
Old 2/18/19, 10:05 AM
Don C. Hawley's Avatar
Don C. Hawley Don C. Hawley is offline
Certified Professional Inspector (CPI)
 
Join Date: Feb 2016
Location: Pocahontas, IL
Posts: 302
Default Re: Split bus double tap

Best guess and only a guess, it looks like two #10 wires were used because they didn't have #6 to feed the bottom.

Home Inspection Services, Termite, Radon & Sewer Scope
DonHawley575@gmail.com
Licensed Home Inspector
Licensed Radon Professional
Certified Sewer Inspector
IAC2 Certified Mold Inspector
Reply With Quote
  #9  
Old 2/18/19, 11:38 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 3,295
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Split bus double tap

Has anyone else ever seen factory parallel conductor run to the split-bus? Seems less cost effective to use four conductor instead of two when they're typically welded to the bus.
Reply With Quote
  #10  
Old 2/18/19, 11:42 AM
Bradley K. Toye, CMI's Avatar
Bradley K. Toye, CMI Bradley K. Toye, CMI is online now
Certified Master Inspector
 
Join Date: Sep 2010
Location: Clearwater, FL
Posts: 5,437
Default Re: Split bus double tap

Quote:
Originally Posted by Robert Meier View Post
Has anyone else ever seen factory parallel conductor run to the split-bus? Seems less cost effective to use four conductor instead of two when they're typically welded to the bus.
No, I haven't. Could this be a possible repair?



Brad K Toye
ITC/FLIR Level I Building Investigation Thermographer
FL Certified Building Contractor CBC034303
FL Certified Home Inspector HI 391
FL Certified Mold Assessor MRSA 589

727-403-5029
Lecsi2@gmail.com
Reply With Quote
  #11  
Old 2/18/19, 1:40 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 3,295
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Split bus double tap

Quote:
Originally Posted by btoye View Post
No, I haven't. Could this be a possible repair?

I don't know those conductors are typically spot welded to the bus. I'd be curious to see this panel with the CB's removed.
Reply With Quote
  #12  
Old 2/18/19, 6:46 PM
Michael PARKS Michael PARKS is offline
Community Guest
 
Join Date: Dec 2018
Location: OHIO
Posts: 21
Please Note: mparks2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Split bus double tap

Numerous conductors are improperly installed. Have Licensed Electrical Contractor repair affected circuits/conductors.
Reply With Quote
  #13  
Old 2/18/19, 10:00 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 2,690
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Split bus double tap

I have only seen single conductors welded to the bus, never paralleled.
Reply With Quote
Need a home inspection in District Of Columbia? Check out InterNACHI's listing of District Of Columbia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 2/19/19, 10:58 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 3,295
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Split bus double tap

Quote:
Originally Posted by Jim Port View Post
I have only seen single conductors welded to the bus, never paralleled.
Same here, that's why I find this panel to be so odd.
Reply With Quote
  #15  
Old 2/20/19, 2:25 PM
David OKeefe's Avatar
David OKeefe David OKeefe is offline
Certified Professional Inspector (CPI)
 
Join Date: May 2008
Location: Delmar, NY ★ New York's Capital Region
Posts: 1,936
Default Re: Split bus double tap

I'll try and update you later if I can.



David

InterNACHI Certified Home Inspector #08051301
NYS Licensed Home Inspector #16000038229
NYS DEC Certified Pest Technician # T4865884
518-505-8305
HouseAbout Home Inspections, LLC
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI
Connect on LinkedIn
Follow HouseAbout_LinkedIn
Follow me on Twitter
HouseAbout_Instagram
Google+
Reply With Quote
Reply