  #46  
Old 8/11/17, 7:24 AM
Justin Ake Justin Ake is offline
Certified Professional Inspector (CPI)
 
Join Date: Aug 2010
Posts: 69
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Roy,

I think I'd try to use both the professional terminology and the layman's term in parenthesis like you did. Our main goal is to educate our client and if they can't understand what we're saying then we haven't helped them out at all. Plus it helps prevent those follow up clarification calls when the client is trying to describe the deficiencies to their realtor or whoever. I agree the term "ground" can be misused, so throwing EGC in there covers all the bases and makes it simple for the electrician when the client calls one.

Jim,

You mentioned that it may sometimes be ok for the neutral bar to be bonded at the sub. Can you explain a little more please? Here's a pic of a sub I did yesterday (in the same building as main panel) and I called it out b/c the neutral was bonded. Was I correct?
Attached Thumbnails
sub-panel-neutrals-and-grounds-same-bus-bar-question-dsc_0039.jpg   sub-panel-neutrals-and-grounds-same-bus-bar-question-dsc_0040.jpg   sub-panel-neutrals-and-grounds-same-bus-bar-question-dsc_0041.jpg  
Reply With Quote
Need a home inspection in Arizona? Check out InterNACHI's listing of Arizona certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #47  
Old 8/11/17, 12:41 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 2,258
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Older editions of the code allowed 3 wire feeders to detached structures. The panel needed to be bonded like a service panel.

If the panel is in or on the same building as the service it needs a 4 wire feeder and the neutral is not bonded. You were correct .
Reply With Quote
  #48  
Old 8/11/17, 1:26 PM
Justin Ake Justin Ake is offline
Certified Professional Inspector (CPI)
 
Join Date: Aug 2010
Posts: 69
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Ok, so that brings up another question. Sorry, but I don't understand why a 3 wire feeder would require bonding at a sub. Once it's bonded, wouldn't that still provide a parallel path for neutral current, regardless of how many wires are used for the hook up?
Reply With Quote
  #49  
Old 8/11/17, 3:30 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 2,988
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Quote:
Originally Posted by jake1 View Post
Ok, so that brings up another question. Sorry, but I don't understand why a 3 wire feeder would require bonding at a sub. Once it's bonded, wouldn't that still provide a parallel path for neutral current, regardless of how many wires are used for the hook up?
Because it's only a 3-wire feeder. You would have two hot legs and a neutral and that's it. The equipment grounding would be provided by bonding the neutral. This was permitted prior to the 2008 NEC for remote structures.
Reply With Quote
  #50  
Old 8/11/17, 4:09 PM
Roy Lewis, CMI's Avatar
Roy Lewis, CMI Roy Lewis, CMI is online now
Certified Master Inspector ®
 
Join Date: Nov 2012
Location: North Florida
Posts: 10,815
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Quote:
Originally Posted by Robert Meier View Post
Because it's only a 3-wire feeder. You would have two hot legs and a neutral and that's it. The equipment grounding would be provided by bonding the neutral. This was permitted prior to the 2008 NEC for remote structures.
Thank you Robert we appreciate you being a member of this board.
Me personally ground rods are cheap. I stick them everywhere .
I don't believe there would ever be a problem with overdoing ground rods. At least down here in Florida . less than two feet down its moist year round.




InterNACHI Lifetime Member.
www.1stproinspection.com
roy@1stproinspection.com
Serving Gainesville Florida and surrounding areas.
Florida Certified Contractor #CRC1328001
Florida Certified Home Inspector #HI7019
Deus solus me iudicare potest
#1st Pro Inspection

Last edited by rlewis5; 8/11/17 at 4:13 PM..
Reply With Quote
  #51  
Old 8/11/17, 5:10 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 2,258
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

One thing to remember is that ground rods do nothing to trip a breaker.
Reply With Quote
  #52  
Old 8/11/17, 5:20 PM
Roy Lewis, CMI's Avatar
Roy Lewis, CMI Roy Lewis, CMI is online now
Certified Master Inspector ®
 
Join Date: Nov 2012
Location: North Florida
Posts: 10,815
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Jim is the other one. Both give great advice when it comes to electrical.




InterNACHI Lifetime Member.
www.1stproinspection.com
roy@1stproinspection.com
Serving Gainesville Florida and surrounding areas.
Florida Certified Contractor #CRC1328001
Florida Certified Home Inspector #HI7019
Deus solus me iudicare potest
#1st Pro Inspection
Reply With Quote
  #53  
Old 8/11/17, 5:23 PM
Roy Lewis, CMI's Avatar
Roy Lewis, CMI Roy Lewis, CMI is online now
Certified Master Inspector ®
 
Join Date: Nov 2012
Location: North Florida
Posts: 10,815
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Quote:
Originally Posted by Jim Port View Post
One thing to remember is that ground rods do nothing to trip a breaker.
Yes but they do keep transient voltage at bay.
Here in Florida is probably the most lightning prone place in the US. Ground rods are a good thing




InterNACHI Lifetime Member.
www.1stproinspection.com
roy@1stproinspection.com
Serving Gainesville Florida and surrounding areas.
Florida Certified Contractor #CRC1328001
Florida Certified Home Inspector #HI7019
Deus solus me iudicare potest
#1st Pro Inspection
Reply With Quote
  #54  
Old 8/16/17, 12:51 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is online now
Certified Master Inspector
 
Join Date: Oct 2004
Location: Michigan
Posts: 1,080
Send a message via Skype™ to gwells
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Quote:
Originally Posted by rlewis5 View Post
Yes it does.
Then there is a serious problem with the system. Residential systems are always solidly grounded. Floating grounds are very rare. In more than 42 years in the electrical trade, having done many hundreds of installations and hundreds of forensic electrical investigations I have never encountered a floating ground in a residential system unless it was damaged.

Look at the utility pole where the transformer is mounted, the meter socket, and the service panels and you will clearly see the system is solidly grounded.



Forensic Electrical Consultant
EE, Licensed Master Electrician/Electrical Contractor



BestInspectors.Net
By Inspectors, For Inspectors

Inspection Report Software
& Business Coaching


Since 1992
Reply With Quote
  #55  
Old 8/16/17, 12:57 PM
Roy Lewis, CMI's Avatar
Roy Lewis, CMI Roy Lewis, CMI is online now
Certified Master Inspector ®
 
Join Date: Nov 2012
Location: North Florida
Posts: 10,815
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

I was referring to floating neutrals in a sub panel. Not the grounding conductors.




InterNACHI Lifetime Member.
www.1stproinspection.com
roy@1stproinspection.com
Serving Gainesville Florida and surrounding areas.
Florida Certified Contractor #CRC1328001
Florida Certified Home Inspector #HI7019
Deus solus me iudicare potest
#1st Pro Inspection
Reply With Quote
  #56  
Old 8/16/17, 2:30 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is online now
Certified Master Inspector
 
Join Date: Oct 2004
Location: Michigan
Posts: 1,080
Send a message via Skype™ to gwells
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Quote:
Originally Posted by rlewis5 View Post
I was referring to floating neutrals in a sub panel. Not the grounding conductors.
Neutrals do not float. They are called the grounded conductor because they are solidly grounded. It is only relatively recently that referring to them as neutral conductors has become acceptable. They are truly only neutral in a perfectly balanced 240V circuit. Residential systems are split-phase. In order to have 120V, the grounded conductor is connected to the center of the source transformer's secondary winding. The center tap is always grounded. Hence, the name Grounded Conductor.

Modern residential systems are usually grounded at no fewer than three locations. It is not impossible but it is extremely rare for a system to lose its connection to ground. A system with a floating neutral would require major screw-ups by both the electrician who wired the house and the lineman who installed the source transformer.

When I investigate a fire or electrocution, I am digging deep into the electrical system. I am not doing a casual inspection as I would in a home inspection. I have seen fires caused by loss of the neutral it even in those cases, the neutral was grounded.

My memory is not perfect but I am sure that if I ever encountered a floating neutral in a house, I'd remember it.



Forensic Electrical Consultant
EE, Licensed Master Electrician/Electrical Contractor



BestInspectors.Net
By Inspectors, For Inspectors

Inspection Report Software
& Business Coaching


Since 1992
Reply With Quote
  #57  
Old 8/16/17, 2:35 PM
Roy Lewis, CMI's Avatar
Roy Lewis, CMI Roy Lewis, CMI is online now
Certified Master Inspector ®
 
Join Date: Nov 2012
Location: North Florida
Posts: 10,815
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

So at a subpanel. If I took my ohms meter. And went from the neutral bar to the housing. I should see no deflection. Correct?




InterNACHI Lifetime Member.
www.1stproinspection.com
roy@1stproinspection.com
Serving Gainesville Florida and surrounding areas.
Florida Certified Contractor #CRC1328001
Florida Certified Home Inspector #HI7019
Deus solus me iudicare potest
#1st Pro Inspection
Reply With Quote
  #58  
Old 8/16/17, 3:09 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is online now
Certified Master Inspector
 
Join Date: Oct 2004
Location: Michigan
Posts: 1,080
Send a message via Skype™ to gwells
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Quote:
Originally Posted by rlewis5 View Post
So at a subpanel. If I took my ohms meter. And went from the neutral bar to the housing. I should see no deflection. Correct?
The measurement with an Ohmmeter should be at zero or very close to zero (depending on the accuracy of the meter) if it is grounded. Measuring with an Ohmmeter, a megger, or a hi-pot would also show as open (though using a hi-pot would not be a good idea) if it were floating. If you had a floating neutral, it would be very high, close to infinity. In other words, it would show as an open. If you were to encounter a very high resistance at any given point, you would need to look to see where the connection was lost. Merely losing the connection at one point in the system does not by itself constitute a floating neutral.

It is also possible to lose one or more connections and read low but higher than expected resistance or a resistance of thousands of Ohms. You could, for example read a couple of hundred ohms. One possibility is that you would be reading through connected loads. If you are troubleshooting or trying to determine the cause of a fire, you would need to remove all loads from all circuits.

I've seen houses burn so intensely that the entire house was in the basement. In one such case, I arrived on the scene before the rest of the people I was working with arrived. Within five minutes, I was able to see that the neutral was still solidly grounded. The reason was that it was a pole mounted transformer. The fuse had blown on the transformer as a result of the fire (which was arson) but the transformer was completely intact. There again, that is not to say that the neutral didn't lose its connection to ground somewhere in the house. I was, however, able to determine that they system was solidly grounded as it was supposed to be.

The chances of a home inspector encountering a floating neutral are almost infinitesimally small. If even if you were to find what you suspect may be a floating neutral, the next question is, do you have the skills to make that determination? The typical journeyman or master electrician does not. The typical electrical engineer does not. Properly diagnosing and identifying many electrical deficiencies and defects requires very specialized training and lots of experience. I've been training electricians, electrical technicians, and electrical engineers for decades so I have a pretty good idea of what their training consists of.



Forensic Electrical Consultant
EE, Licensed Master Electrician/Electrical Contractor



BestInspectors.Net
By Inspectors, For Inspectors

Inspection Report Software
& Business Coaching


Since 1992

Last edited by gwells; 8/16/17 at 3:18 PM..
Reply With Quote
Need a home inspection in Arizona? Check out InterNACHI's listing of Arizona certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #59  
Old 8/16/17, 4:02 PM
Roy Lewis, CMI's Avatar
Roy Lewis, CMI Roy Lewis, CMI is online now
Certified Master Inspector ®
 
Join Date: Nov 2012
Location: North Florida
Posts: 10,815
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Without all the technical babble. So we shouldn't use floating we should use isolated at the sub panel correct?




InterNACHI Lifetime Member.
www.1stproinspection.com
roy@1stproinspection.com
Serving Gainesville Florida and surrounding areas.
Florida Certified Contractor #CRC1328001
Florida Certified Home Inspector #HI7019
Deus solus me iudicare potest
#1st Pro Inspection
Reply With Quote
  #60  
Old 8/16/17, 4:12 PM
Roy Lewis, CMI's Avatar
Roy Lewis, CMI Roy Lewis, CMI is online now
Certified Master Inspector ®
 
Join Date: Nov 2012
Location: North Florida
Posts: 10,815
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Mr. Wells I tried to call you from your website phone number. All I got was robotic voicemail. Have a great day




InterNACHI Lifetime Member.
www.1stproinspection.com
roy@1stproinspection.com
Serving Gainesville Florida and surrounding areas.
Florida Certified Contractor #CRC1328001
Florida Certified Home Inspector #HI7019
Deus solus me iudicare potest
#1st Pro Inspection
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


All times are GMT -4. The time now is 1:27 PM.
no new posts