Default Sub Panel: Neutrals and grounds on same bus bar Question

Is this narrative ok or what could I do to make it better?


"Neutrals and grounds on same bus bar. In a sub panel the neutrals and grounds should be on separate bars with the ground bar bonded to the panel and the neutral bar floating. Recommend further evaluation by a licensed electrician."




InterNACHI Lifetime Member.
www.1stproinspection.com
roy@1stproinspection.com
Serving Gainesville Florida and surrounding areas.
Florida Certified Contractor #CRC1328001
Florida Certified Home Inspector #HI7019
Deus solus me iudicare potest
#1st Pro Inspection
Reply With Quote
Need a home inspection in Arizona? Check out InterNACHI's listing of Arizona certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/1/16, 11:56 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 3,073
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

I would replace the word grounds with proper NEC term Equipment Grounding Conductors.
Reply With Quote
  #3  
Old 10/1/16, 12:09 PM
Roy Lewis, CMI's Avatar
Roy Lewis, CMI Roy Lewis, CMI is online now
Certified Master Inspector ®
 
Join Date: Nov 2012
Location: North Florida
Posts: 11,521
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Robert Thank you, but do you think the average homeowner would understand what Equipment Grounding Conductors are? Just askin'
I like to keep all my narratives very easy to understand by anyone..
However, I have changed it to Equipment Grounding Conductors.
Thanks again.




InterNACHI Lifetime Member.
www.1stproinspection.com
roy@1stproinspection.com
Serving Gainesville Florida and surrounding areas.
Florida Certified Contractor #CRC1328001
Florida Certified Home Inspector #HI7019
Deus solus me iudicare potest
#1st Pro Inspection

Last edited by rlewis5; 10/1/16 at 12:14 PM..
Reply With Quote
  #4  
Old 10/1/16, 12:24 PM
Linas Dapkus, CMI's Avatar
Linas Dapkus, CMI Linas Dapkus, CMI is online now
Certified Master Inspector ®
 
Join Date: Mar 2006
Location: Lockport, IL.
Posts: 12,602
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Quote:
Originally Posted by rlewis5 View Post
Robert Thank you, but do you think the average homeowner would understand what Equipment Grounding Conductors are? Just askin'
I like to keep all my narratives very easy to understand by anyone..
However, I have changed it to Equipment Grounding Conductors.
Thanks again.
If you use the above term and put "grounding wires" in parenthesis, homeowners and professionals would understand.
Just sayin'.



Linas Dapkus, CMI & LEO wannabe
Dapkus Home Inspections
Go away Rosie. You haven't had anything useful to say since you lost your mind when Trump won.
You are such a loser.


For God so loved the world that he gave his one and only Son, that whoever believes in him shall not perish but have eternal life.
TRUMP/PENCE 2020

"There is nothing more frightening than a man with a gun and nothing more helpless than a man without one..."
Reply With Quote
  #5  
Old 10/1/16, 12:26 PM
Roy Lewis, CMI's Avatar
Roy Lewis, CMI Roy Lewis, CMI is online now
Certified Master Inspector ®
 
Join Date: Nov 2012
Location: North Florida
Posts: 11,521
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Quote:
Originally Posted by ldapkus View Post
If you use the above term and put "grounding wires" in parenthesis, homeowners and professionals would understand.
Just sayin'.
Are you saying to replace grounds with "(grounding wires)"?

Neutrals and equipment grounding conductors (grounding wires) on same bus bar. In a sub panel the neutrals and equipment grounding conductors should be on separate bars with the ground bar bonded to the panel and the neutral bar floating. Recommend further evaluation by a licensed electrician.

Is that what you mean?

Thanks




InterNACHI Lifetime Member.
www.1stproinspection.com
roy@1stproinspection.com
Serving Gainesville Florida and surrounding areas.
Florida Certified Contractor #CRC1328001
Florida Certified Home Inspector #HI7019
Deus solus me iudicare potest
#1st Pro Inspection

Last edited by rlewis5; 10/1/16 at 12:30 PM..
Reply With Quote
  #6  
Old 10/1/16, 12:39 PM
Linas Dapkus, CMI's Avatar
Linas Dapkus, CMI Linas Dapkus, CMI is online now
Certified Master Inspector ®
 
Join Date: Mar 2006
Location: Lockport, IL.
Posts: 12,602
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Quote:
Originally Posted by rlewis5 View Post
Are you saying to replace grounds with "(grounding wires)"?

Neutrals and equipment grounding conductors (grounding wires) on same bus bar. In a sub panel the neutrals and equipment grounding conductors should be on separate bars with the ground bar bonded to the panel and the neutral bar floating. Recommend further evaluation by a licensed electrician.

Is that what you mean?

Thanks
No, replace them with ground black peppercorns. WTF??
Don't be a Wayne.



Linas Dapkus, CMI & LEO wannabe
Dapkus Home Inspections
Go away Rosie. You haven't had anything useful to say since you lost your mind when Trump won.
You are such a loser.


For God so loved the world that he gave his one and only Son, that whoever believes in him shall not perish but have eternal life.
TRUMP/PENCE 2020

"There is nothing more frightening than a man with a gun and nothing more helpless than a man without one..."
Reply With Quote
  #7  
Old 10/1/16, 12:53 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2007
Location: Minnesota & Northern Iowa
Posts: 29,630
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Quote:
Originally Posted by ldapkus View Post
If you use the above term and put "grounding wires" in parenthesis, homeowners and professionals would understand.
Just sayin'.
Agree, but use "...grounds (EGC's)..." instead of "...grounds (grounding wires)...".
JMHO



Jeffrey R. Jonas
Owatonna, Minnesota



"I am not a teacher, but an awakener."
- Robert Frost, American poet (1874-1963).

"We Respect Our Clients Right to Privacy"

Reply With Quote
  #8  
Old 10/1/16, 12:57 PM
Roy Lewis, CMI's Avatar
Roy Lewis, CMI Roy Lewis, CMI is online now
Certified Master Inspector ®
 
Join Date: Nov 2012
Location: North Florida
Posts: 11,521
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Quote:
Originally Posted by ldapkus View Post
No, replace them with ground black peppercorns. WTF??
Don't be a Wayne.
Thank you Linas for being you...
ground black peppercorns sounds good to me.




InterNACHI Lifetime Member.
www.1stproinspection.com
roy@1stproinspection.com
Serving Gainesville Florida and surrounding areas.
Florida Certified Contractor #CRC1328001
Florida Certified Home Inspector #HI7019
Deus solus me iudicare potest
#1st Pro Inspection
Reply With Quote
  #9  
Old 10/1/16, 1:00 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 3,073
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Quote:
Originally Posted by rlewis5 View Post
Robert Thank you, but do you think the average homeowner would understand what Equipment Grounding Conductors are? Just askin'
I like to keep all my narratives very easy to understand by anyone..
However, I have changed it to Equipment Grounding Conductors.
Thanks again.
I can understand your desire keep it simple but if they don't understand the difference between equipment grounding conductors and neutral conductors then they're going to need professional help anyway. Just my 2 cents but the word ground(s) is too broad and is often misused.
Reply With Quote
  #10  
Old 10/1/16, 1:08 PM
Roy Lewis, CMI's Avatar
Roy Lewis, CMI Roy Lewis, CMI is online now
Certified Master Inspector ®
 
Join Date: Nov 2012
Location: North Florida
Posts: 11,521
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Thanks...
Equipment Grounding Conductors it is!




InterNACHI Lifetime Member.
www.1stproinspection.com
roy@1stproinspection.com
Serving Gainesville Florida and surrounding areas.
Florida Certified Contractor #CRC1328001
Florida Certified Home Inspector #HI7019
Deus solus me iudicare potest
#1st Pro Inspection
Reply With Quote
  #11  
Old 10/1/16, 1:19 PM
Joshua L. Frederick Joshua L. Frederick is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 4,384
Send a message via AIM to jfrederick
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

No mention of why or what could happen if left as is? No mention of a safety issue? I think the average home buyer needs to know why.
I don't think the average home buyer needs to know the difference between grounds and egc's. An electrician is going to be the one doing the repairs, so word it in terms they understand with professional vocabulary.
Why does an electrician have to evaluate? Evaluate what? It's wrong and needs a fixin'




http://northwestohiohomeinspector.com

Defiance home inspector
Northwest Ohio home inspector
Reply With Quote
  #12  
Old 10/1/16, 1:31 PM
Roy Lewis, CMI's Avatar
Roy Lewis, CMI Roy Lewis, CMI is online now
Certified Master Inspector ®
 
Join Date: Nov 2012
Location: North Florida
Posts: 11,521
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

That is why I post the question..
Josh how would you phrase it?




InterNACHI Lifetime Member.
www.1stproinspection.com
roy@1stproinspection.com
Serving Gainesville Florida and surrounding areas.
Florida Certified Contractor #CRC1328001
Florida Certified Home Inspector #HI7019
Deus solus me iudicare potest
#1st Pro Inspection
Reply With Quote
  #13  
Old 10/1/16, 5:43 PM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
Certified Master Inspector
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 14,682
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Quote:
Originally Posted by rlewis5 View Post
Is this narrative ok or what could I do to make it better?


"Neutrals and grounds on same bus bar. In a sub panel the neutrals and grounds should be on separate bars with the ground bar bonded to the panel and the neutral bar floating. Recommend further evaluation by a licensed electrician."
This narrative doesn't accurately describe any particular condition (IMHO).

Here are several conditions that are usually associated with what you're trying to describe:

(1) Equipment grounding conductors are attached to the isolated neutral terminal.
(2) Neutrals have been attached to the equipment grounding terminal.
(3) The neutral terminal has been bonded to the enclosure.
(4) The equipment grounding conductors have not been bonded to the enclosure.

I use "equipment grounding conductors (EGC's)" in my reporting. Then, rather than "recommend further evaluation," I use "which should be corrected by a qualified electrician."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE «
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Need a home inspection in Arizona? Check out InterNACHI's listing of Arizona certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 10/1/16, 7:24 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 2,377
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

If the panel is in a detached building there is nothing wrong with that if fed by a 3 wire feeder under certain conditions. Do not just use that verbiage as a blanket unless it applies.
Reply With Quote
  #15  
Old 10/2/16, 9:46 AM
Michael A. Clark, CMI's Avatar
Michael A. Clark, CMI Michael A. Clark, CMI is online now
Certified Master Inspector
 
Join Date: Apr 2012
Location: Almost Heaven, WV
Posts: 6,767
Default Re: Sub Panel: Neutrals and grounds on same bus bar Question

Quote:
Originally Posted by jfrederick View Post
No mention of why or what could happen if left as is? No mention of a safety issue? I think the average home buyer needs to know why.
I don't think the average home buyer needs to know the difference between grounds and egc's. An electrician is going to be the one doing the repairs, so word it in terms they understand with professional vocabulary.
Why does an electrician have to evaluate? Evaluate what? It's wrong and needs a fixin'
I just add " dangerous conditions can occur"...

SAFETY: "Neutral wires and equipment grounds should not be bonded in a sub panel. Dangerous conditions can occur. They should be separated and isolated by a qualified electrical contractor for safety."




Michael A Clark, Certified Master Inspector«
Inspection Connection
St Albans, West Virginia

"Always tell the truth,
do what you say you will,
and do it Righter than Right...Always"

Facebook

Google Plus

www.charleston-home-inspector.com
www.icwvhomes.com

mclark@icwvhomes.com
Reply With Quote