Old 6/7/11, 12:25 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
Certified Master Inspector
Question Sure Test fails to trip AFCI breakers
New construction. None of the tested Square-D breakers would trip with a Sure-test. Got a strange read-out. What do you think?
Sure Test fails to trip AFCI breakers-060611-069-800x600-jpg
Theodore Roosevelt
Joe Funderburk, CBO, CMI
Angie's List Super Award Winner 2016, 2015, 2014, 2013, 2012, 2011, 2010.
Ph: 704-351-1776
www.aohomeinspection.com
Need a home inspection in New Hampshire? Check out InterNACHI's listing of New Hampshire certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
Old 6/7/11, 12:38 AM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
Default Re: Sure Test fails to trip AFCI breakers
You didn't wait long enough between tests. After a series of tests, it needs to cool down. Manual calls for 20 seconds between tests to dissipate heat.
Stephen Stanczyk
Pierce County -Thurston County - King County - Kitsap County
Old 6/7/11, 1:01 AM
Thanks Stephen.
None of the AFCI's tripped however. I've heard that the test button is the accepted test method, but when I can't get them to trip using the Sure-test, I write it up.
Theodore Roosevelt
Ph: 704-351-1776
Old 6/7/11, 4:59 AM
Roy D. Cooke, Sr's Avatar
Originally Posted by jfunderburk View Post
Thanks Stephen.
Did they trip with the test button?? .
That is the recommended way to test
Old 6/7/11, 6:17 AM
Brian E. Kelly's Avatar
Exactly Roy.
"So, what are your thoughts on the Flir One??"
Old 6/7/11, 7:54 AM
Wayne B. Wilson, TN 439's Avatar
Wayne B. Wilson, TN 439 Wayne B. Wilson, TN 439 is online now
Have you got a updated one/ we had problems with a couple of manufactures Siemens was one . Ideal had to update the unit
Wayne Wilson CMI
East TN Home Inspections LLC
865-256-1490
https://www.myhomeinspection.net/
Old 6/7/11, 8:11 AM
Robert Meier's Avatar
Thanks Stephen.
Does the test button trip the breaker? If so how can you write it up? Isn't the TEST button the prescribed testing method set forth by the manufacturer?
Old 6/7/11, 9:17 AM
What do you say when your tester won't trip a GFCI? I view AFCI's no differently. If I have an expensive device that is designed to trip the breaker and it does not, I write it up like so:
"An arc-fault circuit interrupters protecting the bedrooms and living areas do not trip when tested using a Sure-Test circuit analyzer, and should be evaluated by a licensed electrician. AFCI receptacles are life saving devices but may fail or be defective from the manufacturer. Any claim that the only reliable test is by using the breaker's integrated test button should be substantiated with written documentation from the manufacturer."
Theodore Roosevelt
Ph: 704-351-1776
Old 6/7/11, 10:14 AM
Unmoderated Guest
The only UL recognized test method is the built-in test buttons. You are not using a tester, it is more properly called an indicator.
To write up something when the proper procedure works would be a poor call IMO.
Old 6/7/11, 10:21 AM
Ideal's test recommendation:
http://www.idealindustries.com/media...d_circuits.pdf
Theodore Roosevelt
Ph: 704-351-1776
Old 6/7/11, 10:31 AM
Larry Kage, CMI Larry Kage, CMI is offline
Certified Master Inspector ®
From the link...They recommed using the integral test button.
Can the underlined/bolded always be verified by the home inspector?
1. At the panel, operate the test button on the AFCI breaker installed in the branch circuit.
a. If the AFCI breaker trips, reset the breaker to restore power.
b. If the AFCI breaker does not trip, verify proper installation of the breaker. If the installation is correct and the breaker still does not trip, replace the faulty breaker.
2. Then, check each outlet on the branch circuit for proper wiring configuration by using the LEDs on the 61-059 tester.
3. Go to the furthest outlet on the branch circuit from the panel and conduct an AFCI trip test with the tester.
a. If the breaker trips, then use the tester to check that each outlet on the branch circuit has been de-energized to confirm that the outlets are on the same AFCI branch circuit.
b. If the breaker doesn’t trip, then the branch circuit may have excessive line impedance (i.e. voltage drop) from undersized wiring, loose wire connections and/or faulty wiring devices. The SureTest® model 61-165 can be used to further identify the source of high impedance on the branch circuit.
Awards Committee Member
SUBMIT YOUR AWARD NOMINATIONS HERE:
http://co.nachi.org/inachiawards/
Larry Kage, CMI 2004-2017
State Licensed Builder since 1973
InterNACHI Lifetime Member
~retired~
The above post represents my personal opinion.
Old 6/7/11, 11:38 AM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
There are certain types of AFCI breakers that do not trip when the SureTest is used, although the AFCI function is operational.
As long as the circuit is opened when the internal test button on the breaker is used, the AFCI is considered functional.
The readings on your SureTest show "caution" (triangle with exclamation), "don't operate" (circle with line), "over heated" (thermometer) and "wait" (hour glass) - in other words STOP!
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Old 6/7/11, 9:13 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is online now
I thought the appropriate way was to test at the breaker itself??
Fogarty Inspection Services Group of Palm Bay FL
FL Licensed Home Inspector #8351
Infraspection Level 2 Thermographer #8788
FL Licensed Mold Assessor #MRSA2330
Home inspections, Commercial Inspections, Mold assessments, Thermal Imaging, Wind Mitigation and Insurance Inspections for Palm Bay, Melbourne, Cocoa, Titusville, Vero Beach and all the surrounding areas.
321-506-5125
fogartyinspectionservices@gmail.com
www.homeinspectorpalmbay.com
Old 6/7/11, 9:36 PM
Exactly.
Same if your Tester does not trip a GFCI and the Test Button does trip the Circuit, it is not a defect.
Old 6/7/11, 9:58 PM
Banned
Originally Posted by bkelly2 View Post
Exactly.
I carry 3 GFCI testers in my tool kit from the small $10 type to the original Suretest I bought in 1985. If none of my testers will trip a GFCI and the test button does, I call it as a defect!! Just being safe......... when 3 testers that are designed to "create a ground fault condition" do not cause a trip, I'm assuming the GFCI unit will not trip when a real one occurs!