Default Just some tidbits of info...History of AC (BX) and NM Cable

Here is some history about Type AC and NM Cable that you may find interesting. It is extracted from a 2012 Study on Damaging Type NM Cable from NFPA...Enjoy!

Armored Cable

Armored cable (AC) was first Listed in 1899 for the Sprague Electric Co. of New York, and was originally called “Greenfield Flexible Steel-Armored Conductors,” after one of its inventors, Harry Greenfield. There were originally two experimental versions of this product, one called “AX” and the other “BX,” with the “X” standing for “experimental."

The “BX” version became the one that eventually got produced, and hence Investigation of Damage and Degradation on Breakdown Voltage of NM Cables the name “BX” stuck, which also became the registered trade name of armored cable for General Electric, which later divested this business to Sprague Electric. Armored cable, or BX, first appeared in the 1903 NEC, but did not start becoming popular until around 1930, and is still a popular wiring method today. AC cable is described in Article 320 of the NEC. The armor of AC cable systems is tested for grounding and can provide a suitable equipment grounding path. AC cable made after 1959 requires an aluminum bonding strip under the armor to help improve the conductivity of this path.

Although originally produced with steel armor, in the late 1980’s lightweight
aluminum armored AC cable first became Listed in accordance to NEC requirements.

Nonmetallic Cable

Nonmetallic-sheathed cable, or NM for short, was first Listed and described in the NEC in 1926, but it was invented a few years earlier by Rome Wire Company in 1922 in Rome, NY, and marketed under the trade name “Romex®.” Romex® is now a registered trademark of Southwire Company of Carrollton, GA.

NOTE: It is officially Type NM Cable or Nonmetallic-Sheathed Cable versus using the tradenames...

Early NM cable had their individual conductor insulation wrapped in a cotton braid that was impregnated with either a varnish or tar-like substance for moisture protection. Around 1950, synthetic spun rayon was being permitted to replace the cotton thread in the jacket braid. Then in the early 1960’s, thermoplastic began replacing the braided jacket altogether, and by about 1970, most all NM cable had a compounded PVC outer jacket, even though a braid was still permitted until 1984. Also in 1984, NM-B cable was developed and required to have 90°C rated individual conductors, and a 75°C outer jacket.

Until the early 1960’s, most NM cable for residential use did not have a grounding conductor. However, changes in the 1962 Code that mandated equipment grounding for all branch circuits popularized the use of NM cable with ground. Earlier versions of NM cable with ground permitted the grounding conductor to be one or even two sizes smaller than the current carrying conductors. For example, a 16 AWG ground wire was permitted for 14 and 12 gauge copper NM, and 14 AWG ground for 10 gauge copper NM.

In 1969, new requirements no longer permitted an undersized grounding conductor for 14, 12 and 10 AWG NM cable.



Paul W. Abernathy, CMECP™
NFPA 70 (NEC®) Code Panel Member on #5 and #17
Founder of the Certified Master Electrical Code Professional® Program
CMECP™ Website - www.MyCMECP.com
Website - http://www.masterthenec.com
Twitter - https://twitter.com/MasterTheNEC
Facebook -https://www.facebook.com/masterthenec/
Spreaker PodCasts - https://www.spreaker.com/show/master-the-necs-tracks


Disclaimer - All my posts on this forum represent Electrical Code Academy, Inc.
Reply With Quote
Need a home inspection in Idaho? Check out InterNACHI's listing of Idaho certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/3/15, 5:31 PM
Paul Lesieur, CMI's Avatar
Paul Lesieur, CMI Paul Lesieur, CMI is online now
Certified Professional Inspector (CPI)
 
Join Date: Feb 2014
Location: North Oaks, Minnesota
Posts: 5,056
Default Re: Just some tidbits of info...History of AC (BX) and NM Cable

Interesting and at my advanced age I was aware of much of what you posted but not all. Up until recently I still refered to armored cable as Greenfield and was corrected more times than I can remember but Greenfield is like Kleenex, it is a branding name.

I started building in 1969 and was right there to see NM take over, slowly at first and then BAM, only saw armored on commercial.

Good to visit the past now and then.
Reply With Quote
  #3  
Old 2/3/15, 6:02 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
Certified Professional Inspector (CPI)
 
Join Date: Sep 2009
Location: Palm Bay FL
Posts: 4,650
Default Re: Just some tidbits of info...History of AC (BX) and NM Cable

good stuff. I found grounded conductor wiring in a 1959 home here last week.





Fogarty Inspection Services Group of Palm Bay FL
FL Licensed Home Inspector #8351
Infraspection Level 2 Thermographer #8788
FL Licensed Mold Assessor #MRSA2330
Certified Master Inspector

Home inspections, Commercial Inspections, Mold assessments, Thermal Imaging, Wind Mitigation and Insurance Inspections for Palm Bay, Melbourne, Cocoa, Titusville, Vero Beach and all the surrounding areas.

321-506-5125
fogartyinspectionservices@gmail.com

www.homeinspectorpalmbay.com
Reply With Quote
  #4  
Old 2/3/15, 6:30 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2007
Location: Minnesota & Northern Iowa
Posts: 30,879
Default Re: Just some tidbits of info...History of AC (BX) and NM Cable

Love these old tidbits. Thanks Paul!



Jeffrey R. Jonas
Owatonna, Minnesota



"I am not a teacher, but an awakener."
- Robert Frost, American poet (1874-1963).

"We Respect Our Clients Right to Privacy"

Reply With Quote
  #5  
Old 2/3/15, 6:59 PM
Frank Rotte Frank Rotte is offline
Community Guest
 
Join Date: Apr 2014
Location: Bonsall, CA, An island in the sea
Posts: 8,751
Default Re: Just some tidbits of info...History of AC (BX) and NM Cable

A walk through time.




Certified Inspection Services, LLC
5521 Mission Road #1422, Bonsall, CA 92003
Check out the HG User Group on FB
ITC Certified Level I Thermographer
Reply With Quote
  #6  
Old 2/3/15, 7:03 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
Certified Professional Inspector (CPI)
 
Join Date: Feb 2007
Location: Lorain Ohio
Posts: 7,358
Default Re: Just some tidbits of info...History of AC (BX) and NM Cable

thanks Paul....



Jim McKee
Lorain, Ohio
440 225 8688
www.classicinspector.com
Reply With Quote
  #7  
Old 2/3/15, 11:57 PM
Kenneth A. Ramm Kenneth A. Ramm is offline
Certified Professional Inspector (CPI)
 
Join Date: Oct 2012
Location: New Glarus, WI
Posts: 3,783
Default Re: Just some tidbits of info...History of AC (BX) and NM Cable

Very cool. Thanks for posting Paul.



Kenneth (Kenny) Ramm
608-438-3986
RammHomeInspections@gmail.com
Wisconsin License 2516-106
InterNACHI #12101905
Level II Infraspection Institute Certified Infrared Thermographer #10786

"If you want to live a happy life, tie it to a goal, not to people or objects." Albert Einstein
Reply With Quote
  #8  
Old 2/4/15, 7:14 AM
John Ritter John Ritter is offline
Community Guest
 
Join Date: May 2012
Posts: 1,354
Please Note: jritter is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Just some tidbits of info...History of AC (BX) and NM Cable

Always enjoy your postings Paul . Thanks for the info.
Reply With Quote
  #9  
Old 2/4/15, 7:40 AM
Mike Auger's Avatar
Mike Auger Mike Auger is offline
Certified Master Inspector ®
 
Join Date: Jun 2011
Location: Rhode Island
Posts: 4,371
Default Re: Just some tidbits of info...History of AC (BX) and NM Cable

thanks for sharing.



Mike Auger, CMI
RI Reg. # 32856
RI Radon Lic. # RMC-142 RMB-096
(401) 578-4878
A U.S.A.F. Veteran Owned Company
Reply With Quote
  #10  
Old 2/20/15, 5:32 PM
Joshua Obelenus Joshua Obelenus is offline
New User
 
Join Date: Nov 2013
Location: Columbus, OH
Posts: 11
Please Note: Joshua Obelenus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Just some tidbits of info...History of AC (BX) and NM Cable

I did not realize BX has been around that long. Thank you for sharing.
Reply With Quote
  #11  
Old 2/23/15, 7:41 PM
John Wickline John Wickline is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Apr 2006
Location: Hilton Head Island, SC
Posts: 104
Default Re: Just some tidbits of info...History of AC (BX) and NM Cable

Great info Paul. Thanks for sharing.

John M. Wickline
JW Home Inspections, Inc.
Hilton Head, SC
JWInspect.com
Reply With Quote
  #12  
Old 3/16/15, 1:24 PM
Steve Man Steve Man is offline
New User
 
Join Date: Mar 2015
Posts: 16
Please Note: Steve Man is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thumbs up Re: Just some tidbits of info...History of AC (BX) and NM Cable

Bravo Mr. Abernathy

We are always asking if it's 'to code' , or 'up to code'

But there are phenomenal differences of any install meeting code at the particular code cycle vs. the latest code.

I collect old code books for just this reason, but they do not portray any manufacturing history

I would be grateful for a link to pass onto my peers

~S~
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
U.S. Housing Market is the Most Awesome Opportunity in American History jburkeson1 Miscellaneous Discussion for Inspectors 2 9/9/12 8:31 PM
Strange history lesson cbottger Miscellaneous Discussion for Inspectors 1 3/18/08 3:52 PM

All times are GMT -4. The time now is 12:45 AM.
no new posts