Tie bar

No tie bar visible in service panel. Center bar in second photo appears to be all plastic serving as a standoff. Is this a problem? Ground bus is grounded to conduit ring.

DSCF5378 (Small).JPG

DSCF5374 (Small).JPG

And what makes you think that is the service panel?

Haha, good question :roll:… Slow down, step back, focus, deep breath…

GE panels have the tie bar at the end which can be removed when using as a non-service panel like in the photo below. Your panel should have a bonding screw install in the EGC’s bus.

https://lh3.googleusercontent.com/fmX0HSrk68JIZuEcYjUqIXi5zTONjesXOocfCHdR0rOhNNMUEA9cbDtJQxZOp7yDEna1F49-E0ks3dwimnNaQXX7NE7s8KJ1Y0K0EBM9oENFFVWTX23DgzctogmKw5djaWWwsC3wJdaFem74vx_q7FEGCbllSFwVvpB4vBOT-bcfQgDSStvG7O_78UGpsYxusVp1r_pcssWX3diLDaot3-Ygbivb8DClBqMlWrfrFob18Bqgf35VF8J_DF61QcQAgtt8i-05ZdXkC81UvQYRdlhOIJOkYeOUQcfPx3GMSD9M0tF0Zu28BusDdCrRTXOeVcAFTyr9AqVpQqSHAhsQS3M7dFl1GAUjKYAGkGiL7f14SfBiWVcOmTEVJ2Q-_WlHXwrnQvrNB3Du25mAwhzaP_As2UA1sf1nqgg1XQFt1Um7z-YOTwnwawjk48GbMnefPP4ZYdJULY891RhVMl6s9S0D6XiVKwrE1StODFxBz5LPCj8BOi9N8WJMu8hXX2-h_ZyZOuhOaw9enInxmQBoJqjJbfyJ1HlY5mPiuZ_EwceBjY4mmJeM3A3shU4YlninViMz=w1035-h1380-no

The fact that the neutrals are segregated from the grounding conductors should be a clue this is not a service panel. The 4 wire feed is another clue.

If this is the only panel in the home then there may be a single main breaker outside by the meter. That will be the service panel and the neutral and ground will be bonded there.

No main breaker
4 wire
Neutral and ground seperate
No bonding screw

All clues to this situation.

That white wire on the bottom right also should be phase taped.

Shouldn’t there be a bonding screw in the bus being used to terminate the EGC’s?