Default Add on Chimney

I've never seen this before. Brick chimney serves main floor aftermarket gas insert (was wood burner) metal liner present. Steel chimney attached laterally to the masonry chimney for basement wood burning fireplace.
I know side by side clearance is 16" min on metal vents, but what about metal to masonry. I didn't measure but I believe steel vent has it's two feet over ridge.

My concern is what I can't see Re: the basement fire box/throat/off-set to the vent connection.

What say you?

Cheers

Mark
Attached Thumbnails
Add on Chimney-20131203_100349-jpg   Add on Chimney-20131203_123717-jpg  
Reply With Quote
Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/3/13, 5:07 PM
Chris Jacobi, HI01200061's Avatar
Chris Jacobi, HI01200061 Chris Jacobi, HI01200061 is online now
Certified Professional Inspector (CPI)
 
Join Date: Nov 2012
Location: Columbus, Indiana
Posts: 1,071
Send a message via Yahoo to cjacobi
Default Re: Add on Chimney

1. One flue for one wood burning fireplace. It's hard to tell from your pics, but I'm wondering if they share the flue at any point. If they do, that's a no-no.
2. Metal vent: It may be 2' higher than the ridge, but it's not 2' higher than the chimney chase.
3. Enough clearance through the soffit? Shouldn't there be a thimble/coller?



Chris Jacobi, CPI




Home Inspections - Termite Inspections - Radon Testing - Drinking Water Quality Testing - Thermagraphy

www.GreatHomeInspector.net
Chris@GreatHomeInspector.net


Facebook

Serving Indiana from Indianapolis to Greenwood, to Franklin to Columbus to Seymour.

Last edited by cjacobi; 12/3/13 at 10:39 PM.. Reason: typo
Reply With Quote
  #3  
Old 12/3/13, 6:08 PM
KEVIN WOOD, CMI KEVIN WOOD, CMI is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,820
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Add on Chimney

The National Standard of Canada, Installation Code for Solid Fuel Burning Appliances
and Equipment, CSA-B365-01 clause 5.2.9 states that:

Two or more appliances shall not be connected to the same chimney flue unless:

1) The appliances are located on the same story;
2) A negative pressure is maintained at the flue collar of each appliance;
3) Each appliance is provided with a means to control the rate of flow of air or flue
gases through the appliance combustion and heat exchanger chambers. Where
limitations on flue pressure (draft) are contained in the manufacturer’s instructions,
such means shall be capable of maintaining at the flue collar, the pressure
specified by the appliance manufacture; NOTE: For the purpose of this Clause,
draft controls include ash pit air control dampers, dampers or draft slides wherever
located, over fire and flue key pipe dampers, and check draft controls located on or
in the flue pipe.
4) The flue pipes of the appliances are connected to a manifold as close to the
chimney as practicable or directly to the chimney in the following order:
(i) If only solid fuel is used, the flue pipe from the smallest appliance shall be on
top (downstream);
(ii) If different fuels are used as permitted in Clause 5.2.7, the oil flue pipe shall be
on top (downstream); and the solid fuel flue pipe on the bottom (upstream); and
5) The chimney flue is capable of venting the flue gas by natural draft when all
appliances not interlocked to prevent simultaneous firing are firing at their
maximum rate at the same time.

When installing a wood-burning appliance to an existing chimney carefully inspect entire
chimney for the presence of old inlet holes, which may be improperly covered by metal
caps or other unacceptable means. Fill any openings with brick and mortar to ensure
no hazardous openings exist.

Judging from the size of the gas insert. It is possible for this to be completely separate. However I would not want to call that safe as you would need to anchor to the original chimney and that is not accepted. You also need proper brackets all the way up to the top anchored somewhere.

Last edited by kwood; 12/3/13 at 6:16 PM..
Reply With Quote
  #4  
Old 12/3/13, 6:42 PM
Mark Ellison, CMI's Avatar
Mark Ellison, CMI Mark Ellison, CMI is offline
Certified Master Inspector
 
Join Date: Apr 2007
Location: GTA, ON
Posts: 418
Default Re: Add on Chimney

The SS vent is definitely not sharing a flue. It's not easy to see the in the pic, but the SS vent connection is well below the main floor level, which prevents it from sharing the flue. I believe the termination up top is poor. I'm mainly concerned with the side connection to the main brick chase. The off set must be great, but I can't see anything. It's a manufactured fireplace in the basement. Fasteners are present Kevin
Attached Thumbnails
Add on Chimney-20131203_121825-jpg  
Reply With Quote
  #5  
Old 12/3/13, 7:11 PM
KEVIN WOOD, CMI KEVIN WOOD, CMI is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,820
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Add on Chimney

I do not see any brackets or straps unless they are attached at the wall and very well hidden from this picture.

Last edited by kwood; 12/3/13 at 7:32 PM..
Reply With Quote
  #6  
Old 12/3/13, 7:37 PM
Mark Ellison, CMI's Avatar
Mark Ellison, CMI Mark Ellison, CMI is offline
Certified Master Inspector
 
Join Date: Apr 2007
Location: GTA, ON
Posts: 418
Default Re: Add on Chimney

Quote:
Originally Posted by kwood View Post
I do not see any brackets or straps unless they are attached at the wall and very well hidden from this picture.
Not to worry Kevin, they are there. I just didn't post a pic showing them.
Reply With Quote
  #7  
Old 12/3/13, 10:20 PM
KEVIN WOOD, CMI KEVIN WOOD, CMI is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,820
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Add on Chimney

It is wrong anyways!
Reply With Quote
  #8  
Old 12/3/13, 11:55 PM
Juan C. Jimenez Juan C. Jimenez is offline
Certified Professional Inspector (CPI)
 
Join Date: Jan 2012
Location: central va
Posts: 7,690
Default Re: Add on Chimney

Quote:
Originally Posted by kwood View Post
It is wrong anyways!
What is wrong about it? Do you have a reference to something I can read?



Juan Jimenez
A House on a Rock Home Inspections LLC
God. Family. Home.
804-269-4321
Richmond Home Inspector
Richmond Chimney Sweep
Richmond Radon Testing



Last edited by jjimenez; 12/4/13 at 12:24 AM..
Reply With Quote
  #9  
Old 12/3/13, 11:56 PM
Juan C. Jimenez Juan C. Jimenez is offline
Certified Professional Inspector (CPI)
 
Join Date: Jan 2012
Location: central va
Posts: 7,690
Default Re: Add on Chimney

Here's a link I found

http://www.fornobravo.com/PDF/duratech.pdf



Juan Jimenez
A House on a Rock Home Inspections LLC
God. Family. Home.
804-269-4321
Richmond Home Inspector
Richmond Chimney Sweep
Richmond Radon Testing


Reply With Quote
  #10  
Old 12/4/13, 12:36 AM
Juan C. Jimenez Juan C. Jimenez is offline
Certified Professional Inspector (CPI)
 
Join Date: Jan 2012
Location: central va
Posts: 7,690
Default Re: Add on Chimney

Quote:
Originally Posted by cjacobi View Post
3. Enough clearance through the soffit?
It's fuzzy in the photo, but looks like there could be the 2" gap there.



Juan Jimenez
A House on a Rock Home Inspections LLC
God. Family. Home.
804-269-4321
Richmond Home Inspector
Richmond Chimney Sweep
Richmond Radon Testing


Reply With Quote
  #11  
Old 12/4/13, 1:51 AM
Mark Ellison, CMI's Avatar
Mark Ellison, CMI Mark Ellison, CMI is offline
Certified Master Inspector
 
Join Date: Apr 2007
Location: GTA, ON
Posts: 418
Default Re: Add on Chimney

That's a great document Juan, thanks.
What I'm unsure of is the lateral connection of the SS vent to the brick chase at the exterior of the chimney, at the basement level. The clearance at the vent termination as well as the fireplace clearances are all wrong.
Reply With Quote
  #12  
Old 12/4/13, 8:45 AM
Juan C. Jimenez Juan C. Jimenez is offline
Certified Professional Inspector (CPI)
 
Join Date: Jan 2012
Location: central va
Posts: 7,690
Default Re: Add on Chimney

Quote:
Originally Posted by mellison View Post
That's a great document Juan, thanks.
What I'm unsure of is the lateral connection of the SS vent to the brick chase at the exterior of the chimney, at the basement level. The clearance at the vent termination as well as the fireplace clearances are all wrong.
What's wron with the termination? Did you check to see if its a zero clearance fireplace?



Juan Jimenez
A House on a Rock Home Inspections LLC
God. Family. Home.
804-269-4321
Richmond Home Inspector
Richmond Chimney Sweep
Richmond Radon Testing


Reply With Quote
  #13  
Old 12/4/13, 12:40 PM
Mark Ellison, CMI's Avatar
Mark Ellison, CMI Mark Ellison, CMI is offline
Certified Master Inspector
 
Join Date: Apr 2007
Location: GTA, ON
Posts: 418
Default Re: Add on Chimney

Quote:
Originally Posted by jjimenez View Post
What's wron with the termination? Did you check to see if its a zero clearance fireplace?
The SS chimney should be at least 2 ft higher than the masonry chimney. It serves a wood burner Juan, not a gas insert. It's the masonry chimney that serves the aftermarket gas insert.
Reply With Quote
Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/4/13, 12:56 PM
Juan C. Jimenez Juan C. Jimenez is offline
Certified Professional Inspector (CPI)
 
Join Date: Jan 2012
Location: central va
Posts: 7,690
Default Re: Add on Chimney

Quote:
Originally Posted by mellison View Post
The SS chimney should be at least 2 ft higher than the masonry chimney.
Why?



Juan Jimenez
A House on a Rock Home Inspections LLC
God. Family. Home.
804-269-4321
Richmond Home Inspector
Richmond Chimney Sweep
Richmond Radon Testing


Reply With Quote
  #15  
Old 12/4/13, 5:21 PM
Mark Ellison, CMI's Avatar
Mark Ellison, CMI Mark Ellison, CMI is offline
Certified Master Inspector
 
Join Date: Apr 2007
Location: GTA, ON
Posts: 418
Default Re: Add on Chimney

Quote:
Originally Posted by jjimenez View Post
Why?
Must be 2 ft above anything within 10 ft.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
$5000 chimney tuck-pointing job??? fbartlo Structural Inspections 13 7/4/12 12:46 PM
What's Inside A Chimney mcyr Inspecting HVAC Systems 14 9/17/08 7:11 PM
Difficult Chimneys thance Inspecting HVAC Systems 2 1/29/08 9:16 PM
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior Inspections 6 10/13/07 9:10 AM
Fireplace Enclosure jpope Interior Inspections 19 10/25/06 6:08 PM

All times are GMT -4. The time now is 7:39 AM.
no new posts