Default Air Handler

Hi,

I woke up this morning to my second floor Air Handler not running. The Heat Pump outside is running, yet the Air Handler won't turn on. Any ideas as to what this could be or recommendations on what to do or where to start? I checked the breaker at the unit and it doesn't seem to be visibly damaged in any way.


Thanks,

Steve
Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/22/10, 6:07 PM
Stephen P. Shockley's Avatar
Stephen P. Shockley Stephen P. Shockley is offline
InterNACHI Member
 
Join Date: May 2009
Location: Salisbury, Maryland
Posts: 259
Default Re: Air Handler

Just an update on my previous post. When I came home this evening I tried turning the fan to the "On" position and then went up to check out the Air Handler. I could hear a humming sound when I got up there. When I pull the breaker of course it stops. So it seems as though the fan motor is seized up. Other than this I don't know what else to do but call a repair person. If anyone has any experience with this I would certainly appreciate their inputs.


Regards,

Steve
Reply With Quote
  #3  
Old 1/22/10, 6:12 PM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 70,853
Default Re: Air Handler

See if the fan moves freely when you have the breaker off.

It may be the start capacitor on the fan motor.

It sounds like a repair tech is in your future.



As a Professional Home Inspector, I support the privacy of my clients.

You own your private information. I won't sell or give away yours, others do


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
  #4  
Old 1/22/10, 6:24 PM
Stephen P. Shockley's Avatar
Stephen P. Shockley Stephen P. Shockley is offline
InterNACHI Member
 
Join Date: May 2009
Location: Salisbury, Maryland
Posts: 259
Default Re: Air Handler

Thanks for the response Michael. I just went back up there and open the unit back up and check the fan. It does spin freely. Therefore, by your response this sound like a burn't capacitor. Any idea how much effort there is to swapping out a burnt capacitor or is this a simple plug and replace part. This may sound like a dumb question, but what do these capacitors actually look like. I did see two round yellow plastic capped devices behind a panel to the fan, but wasn't sure if this was it. I could post a pic if that helps.


Thanks,

Steve
Reply With Quote
  #5  
Old 1/22/10, 6:29 PM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 70,853
Default Re: Air Handler

Quote:
Originally Posted by sshockley View Post
Thanks for the response Michael. I just went back up there and open the unit back up and check the fan. It does spin freely. Therefore, by your response this sound like a burn't capacitor. Any idea how much effort there is to swapping out a burnt capacitor or is this a simple plug and replace part. This may sound like a dumb question, but what do these capacitors actually look like. I did see two round yellow plastic capped devices behind a panel to the fan, but wasn't sure if this was it. I could post a pic if that helps.


Thanks,

Steve
Size, shape and location vary,

http://images.google.com/images?hl=e...-8&sa=N&tab=wi



As a Professional Home Inspector, I support the privacy of my clients.

You own your private information. I won't sell or give away yours, others do


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
  #6  
Old 1/22/10, 6:39 PM
Stephen P. Shockley's Avatar
Stephen P. Shockley Stephen P. Shockley is offline
InterNACHI Member
 
Join Date: May 2009
Location: Salisbury, Maryland
Posts: 259
Default Re: Air Handler

I'll post a pic in the next hour. Thanks, Steve
Reply With Quote
  #7  
Old 1/22/10, 7:02 PM
Stephen P. Shockley's Avatar
Stephen P. Shockley Stephen P. Shockley is offline
InterNACHI Member
 
Join Date: May 2009
Location: Salisbury, Maryland
Posts: 259
Default Re: Air Handler

Here is the pic that I took. You'll see two yellow components that I was referring to, although not sure if that's what they are. Are the caps typically soldered in place or do they usually have a plug type connection?



Regards,

Steve
Attached Thumbnails
Air Handler-img_1806-jpg  
Reply With Quote
  #8  
Old 1/22/10, 7:10 PM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 70,853
Default Re: Air Handler

The only yellow I see is the two wire nuts and the yellow paint on the temp sensors.

I suggest you find someone knowledgeable with HVAC and circuit diagrams.

The motor for the fan is not in the pic.

If it is the motor humming it probably has to do with the start circuit.

The capacitor provides a push(so to speak) to get the motor spinning.



As a Professional Home Inspector, I support the privacy of my clients.

You own your private information. I won't sell or give away yours, others do


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
  #9  
Old 1/22/10, 7:12 PM
Stephen P. Shockley's Avatar
Stephen P. Shockley Stephen P. Shockley is offline
InterNACHI Member
 
Join Date: May 2009
Location: Salisbury, Maryland
Posts: 259
Default Re: Air Handler

Ok, after looking at the pics in the shortcut you sent, I think I've located the capacitors. Looks like they are mounted right on the side of the fan housing. I can't tell if they are soldered in place or not though.


Regards,

Steve
Attached Thumbnails
Air Handler-img_1807-jpg  
Reply With Quote
  #10  
Old 1/22/10, 7:15 PM
Stephen P. Shockley's Avatar
Stephen P. Shockley Stephen P. Shockley is offline
InterNACHI Member
 
Join Date: May 2009
Location: Salisbury, Maryland
Posts: 259
Default Re: Air Handler

One more thing. My mistake in my original description. The sound is more of a light buzzing sound rather than a humming sound....


Regards,

Steve
Reply With Quote
  #11  
Old 1/22/10, 7:26 PM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 70,853
Default Re: Air Handler

Yes that is a start cap but unless you can determine the buzz is from the motor I doubt if that is the problem.



As a Professional Home Inspector, I support the privacy of my clients.

You own your private information. I won't sell or give away yours, others do


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
  #12  
Old 1/23/10, 3:17 PM
Stephen P. Shockley's Avatar
Stephen P. Shockley Stephen P. Shockley is offline
InterNACHI Member
 
Join Date: May 2009
Location: Salisbury, Maryland
Posts: 259
Default Re: Air Handler

Michael,

Update on the Air Handler...

I went and purchased a multi-meter. I first wanted to verify that I was getting the full 240 volts to the unit and that tested fine. Then, I went ahead and dis-charged that capacitor with a screw driver so I could check its capacitance. It was rated at 5 uF and only measured about 0.9 uF. Also, when I went to order a replacement for the unit, the distrbutor looked my AHU model # up and said that the wrong size capacitor was being used. He said it should be a 7.5 uF. That will be here on Wednesday, so I'm hoping this is all that's wrong with the unit. Thanks again for your help Michael.


Regards,

Steve
Reply With Quote
  #13  
Old 1/23/10, 6:00 PM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Jun 2005
Location: Nashville, TN
Posts: 10,275
Default Re: Air Handler

Quote:
That will be here on Wednesday,
Had to order it!

That makes me scared!!!

You don't have to order a cap! They are everywhere!
Hell, go pull one of the junk pile at your local land fill!



"working together to get-IR-done" Chris Walsh
Bracebridge, Ontario:


David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/23/10, 6:11 PM
Stephen P. Shockley's Avatar
Stephen P. Shockley Stephen P. Shockley is offline
InterNACHI Member
 
Join Date: May 2009
Location: Salisbury, Maryland
Posts: 259
Default Re: Air Handler

David,

Honestly, I didn't have to order it, but I work a full time as a Lean Mfg Engineer on Boeing Business Jets during the day. So with a 35 mile commute leaving at 7 AM and getting home at 7 PM, there are no stores open around here that I can go to unless I take off of work to pick this up. In this economy, I don't want to do anything that will jepordize my full time job. Also, these distributors won't even sell to me unless I'm a liscensed HVAC repairmen. Hence, my rational for ordering... Plus it is supposed to be a little warmer here over the next few days, so I figured I would wait for it to come in.


Regards,

Steve
Reply With Quote
  #15  
Old 1/26/10, 12:15 AM
Stephen P. Shockley's Avatar
Stephen P. Shockley Stephen P. Shockley is offline
InterNACHI Member
 
Join Date: May 2009
Location: Salisbury, Maryland
Posts: 259
Default Re: Air Handler

Michael,

Just wanted to let you know that you were correct that it was the capacitor that was the problem. I ended up finding one on my lunch break for $3.29. Put it in tonight and everything was working fine. Just hope it stays that way.

Thanks again for your help.


Regards,

Steve
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Ducane Heat pump and air handler dates?? tallen Inspecting HVAC Systems 19 12/30/09 4:11 AM
Armstrong air handler age? amccormick Inspecting HVAC Systems 2 6/2/09 8:01 PM
Air handler question lking Inspecting HVAC Systems 5 8/25/08 11:11 PM
Goodman Air Handler runs 24/7/365? Michael McDonald Inspecting HVAC Systems 14 3/27/08 3:42 PM

All times are GMT -4. The time now is 1:02 AM.
no new posts