Old 2/15/10, 8:59 PM
Michael R. Pulka's Avatar
Michael R. Pulka Michael R. Pulka is offline
Default Two appliances connected into single vent
Take a look at the two pics, then:
The furnace is induced draft, the water heater natural. They are connected at the Wye. I know that IRC G2427.3.3 (4) allows these two appliances to join into a common vent connector. The water heater vent is located below the furnace vent (at the Wye). I checked the IRC and it says “where two or more vent connectors enter a common gas vent… the smaller connector shall enter at the highest level”… (IRC G2427.10.4). These seem to be the same diameter. I can't find anything in the IRC code that mandates the water heater vent must be installed above the furnace in this configuration.
So my question is: Which one should be at the top? Why? Where can I find a reference?
Two appliances connected into single vent-valentine_2010-013-jpg   Two appliances connected into single vent-valentine_2010-014-jpg
Need a home inspection in New Jersey? Check out InterNACHI's listing of New Jersey certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
Old 2/15/10, 9:06 PM
Bob Elliott's Avatar
Default Re: Two appliances connected into single vent
Yes
Smaller btu appliance gos on top.
That looks like a bad install.
Old 2/15/10, 9:59 PM
David P. Valley's Avatar
Certified Master Inspector
Originally Posted by belliott View Post
Yes
Not only that. When an additional vent is added on, the vent connector size must increase.
Recommend upgrade......
Old 2/15/10, 10:20 PM
Matthew K. Klein, P.E., MBA's Avatar
Matthew K. Klein, P.E., MBA Matthew K. Klein, P.E., MBA is offline
Did you operate the furnace and check for backdraft out of the water heater flue?
Old 2/15/10, 10:25 PM
Just guessing from the brick corbel , but is that in an attic area?
(not to mention the insulated supply vent)
How was the insulation and drain pan situation?
Old 2/16/10, 12:13 AM
Banned
Depends on the code.
The first knee-jerk reaction is to assume you must have a larger vent connector that also should require a larger flue. The Canadian oil burning code determines fluepipe/flue sizes needed by (1) the total BTU input into the flue, (2) chimney height, (3) minimum base temperature of flue gases, and (4) insulation value of chimney walls
For example: A flue venting 2 appliances with (1) a total BTU/hr input of 210,000, (2) a chimney height of 28', (3) minimum flue gas temperature of 320 deg F at fluepipe entry to chimney, and (4) a thermal resistance of less than 6 should have a mimimum inside flue diameter of 5" and a maximum of 7" or the equivalent if clay tile liner.
Just went through this exercise a few weeks ago when a young electrician was buying his first investment property of 4 apartments, each with its own forced air oil-fired furnace. The building only had 2 chimneys with each serving 2 furnaces.
The young fellow's father (a nervous Nelly) accompanied us for the whole inspection (which added a lot of time and aggravation!!). He kept repeating that he didn't think 2 furnaces could be vented into the same chimney/flue system. I was concerned with the total BTU input into each chimney flue as well as some other flue safety/oil line protection issues.
Actually talked to the head design engineer for the furnace manufacturer to confirm maximum oil nozzle sizes by design for these furnaces. There was no problem with 2 furnaces being vented by a 5" interior diameter stainless steel liner.
BTW, the call to the engineer earned me an invite to the manufacturer's design and test labs......an interesting place. They just put a high efficiency (about 95%) condensing oil furnace on the market; they have a wood pellet boiler in the last stages of testing and certification; they're building the first prototype of a 400,000 BTU commercial wood pellet boiler; they're are about to start selling a 3 ton outdoor pellet storage hopper with automatic feed auger into the boiler......no more bags of pellets!
Old 2/16/10, 2:25 PM
Brian/David thanks for the input. It did not even cross my mind... I guess I was so fixated on the possibility of back draft coming out the water heater vent.
I did check for back draft over the water heater, both with a mirror and CO analyzer. I had the furnace running, water heater off (and on) and the utility door closed behind me. I could not get it to back draft at all. To be honest I was surprised by this, I really thought it would.
As for drain pan install, it was good. -- yup it's in an attic space.
Old 2/16/10, 9:40 PM
Brian E. Kelly's Avatar
Exactly.
"So, what are your thoughts on the Flir One??"
Old 2/17/10, 7:18 AM
Banned
Originally Posted by bkelly2 View Post
Exactly.
From my earlier post:
"The first knee-jerk reaction is to assume you must have a larger vent connector that also should require a larger flue." ......if that thinking is continued forward!
Here's a hypothetical situation, Brian:
You have a 6" diameter chimney flue serving a heating appliance. The fluepipe is 6'' diameter. The homeowner wants to add a hot water heater (same fuel as the heating appliance) since their electric water heater costs are very high. The new water heater has a 5" breech size.
What do you do? Increase the vent connector size to 7" or 8" from the "Y" serving the 2 appliances to the flue and.......then have to reduce it down to 6" again where it enters the chimney?
If you know the BTU inputs of each appliance, the flue gas volume output is then known, taking into account the excess air needs of each unit. Then it can be determined if the chimney and vent connector are suitable for the two appliances.
The figures I gave above are from a CSA standard that forms part of our national building code.
Single wall vent connector mnicholet Inspecting HVAC Systems 3 3/31/09 10:26 PM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 6:22 PM
Another reason to recommend CO testers rnewman1 Interior Inspections 2 10/12/06 8:47 AM