Default Basement Heat

I need an opinion on my basement heating. I have a 1200 sq. ft. basement. 2/3 is finished. I have 3 heat vents. I can't get the basement to stay warm. My home is 65 years old, the finished area is paneling installed on 1x2 inch boards conected to cocncrete block walls, no insulation in the walls. There is no return vent in the basement. My question is do you think it would help if I put a return vent in to get rid of some of the cold air? I may take the paneling down and insulate the walls at some point in the future. Curious for your opinions. Thanks, Stan
Reply With Quote
Need a home inspection in Vermont? Check out InterNACHI's listing of Vermont certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/31/10, 2:27 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
Certified Professional Inspector (CPI)
 
Join Date: Aug 2006
Location: Chicago
Posts: 37,459
Default Re: Basement Heat

You pretty much answered your own question.

The thermostat will cut off the warm air before it has effect on the coldest room , if that room has no return I am sure.

You could add the return ,but remember that your bill will go way up with the furnace running longer.

Insulation is defiantly needed.

Easy way would be to install a baseboard heater.

You could add a small hydronic system boiler or a electric baseboard.
Reply With Quote
  #3  
Old 1/31/10, 2:36 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2007
Location: Minnesota & Northern Iowa
Posts: 29,494
Default Re: Basement Heat

Do you plan on occupying the basement regulary? If not, Bob is correct, baseboard heaters are the way to go. Off when not needed.



Jeffrey R. Jonas
Owatonna, Minnesota



"I am not a teacher, but an awakener."
- Robert Frost, American poet (1874-1963).

"We Respect Our Clients Right to Privacy"

Reply With Quote
  #4  
Old 1/31/10, 3:51 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 29,318
Default Re: Basement Heat

How much of the foundation wall is above ground?

And where is the furnance, not in the basement.?



CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #5  
Old 1/31/10, 6:56 PM
Stan Croenne Stan Croenne is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Springfield, IL
Posts: 72
Please Note: scroenne is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Basement Heat

My boys have been using the basement for years. X-box and computer central. My wife and I use it all the time to work out. I've thought about baseboard heat. I would have to add a sub-panel. The furnace is in the unfinished section of the basement. New high efficiency type. The basement is totally underground. I'm wondering if installing a return down close to the floor would help get rid of some of the cold air at the floor level. I'm sure another cause is the thermostat is on the main level of our home and does not read the basement temperature. I'm trying to warm it up with what is there (existing furnace) before I install baseboard heat or insulate the walls etc.
Reply With Quote
  #6  
Old 1/31/10, 6:59 PM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Jun 2005
Location: Nashville, TN
Posts: 10,275
Default Re: Basement Heat

Quote:
There is no return vent in the basement.
I will say this again...

HAVC forced air systems "SUCK" not "BLOW!

If you don't remove the air from the space and treat it in a properly sized HVAC unit and put it back in the correct proportion, it will not work!

You also can not condition two floors with the same system without a zone system installed.

You do not have the same heating and cooling loads in the basement as you do in upper levels.



"working together to get-IR-done" Chris Walsh
Bracebridge, Ontario:


David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #7  
Old 1/31/10, 7:15 PM
Stan Croenne Stan Croenne is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Springfield, IL
Posts: 72
Please Note: scroenne is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Basement Heat

Dave, I understand all of that. My furnace is properly sized. I know that basements are figured different than above ground floors. I know zone heating would also do the trick. I'm looking for friendly conversation on the matter. It's Sunday and I'm kicking the thought around. You could of said, a return air vent would be your next logical step. That would of been fine with me. Thanks for your comments guys. Stan
Reply With Quote
  #8  
Old 1/31/10, 7:37 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 29,318
Default Re: Basement Heat

Stan, check out this link; http://ths.gardenweb.com/forums/load...214126879.html

Almost sounds like a similar situation.
I would contact a HVAC contractor local and ask for some advice and options that won't break the bank. Something like Works, Good, Better, and Best.
Good luck.



CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #9  
Old 1/31/10, 8:04 PM
Gordon I. Kay Gordon I. Kay is offline
New User
 
Join Date: Jan 2009
Location: Olkanagan Valley British Columbiia Canada eh
Posts: 50
Please Note: gkay is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Basement Heat

You're on the right track Stan. A return air would definately help. You would have to adjust the supply registers seasonally because you would not need as much air flow in the summer to keep the basement cool.
Reply With Quote
  #10  
Old 1/31/10, 11:16 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is online now
Certified Master Inspector
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 9,542
Default Re: Basement Heat

Three air vents does not seem enough to me. It needs to be more like five for 1220 sq. ft. I am not much on installing return air in the basement. If the main level is big enough it will work. If you do install a return air in the basement, make it where you can close it shut during the summer or you will have a very cool basement.
Reply With Quote
  #11  
Old 2/1/10, 10:50 AM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Jun 2005
Location: Nashville, TN
Posts: 10,275
Default Re: Basement Heat

Quote:
Three air vents does not seem enough to me.
Three air vents are more than enough.

Here again we are talking about supply, not the return.

And again, the heating/cooling load in a basement is not the same as 1200 ft.▓ on the first floor above! As well as only two thirds of the basement is finished.

Adding five registers in the basement will really screw things up on the first floor!

Let's skip the facts and just have a friendly discussion about what's going on.

We want to heat the basement with the HVAC system on the first floor. We are "cutting in" to the air duct that happens to be located in the basement (for the first floor).

Our goal is to push enough hot supply air into the basement to perform multiple complete air changes per hour to warm things up.

The air in the basement is cold, the supply air registers are located up high, hot air rises...

No return located in the basement.

How can we expect to force hot air into the basement and expect "cold air to rise" up to the first floor where the return air register is located and leave the hot air behind? Cold air doesn't rise. Hot air doesn't mix with cold air.

If we don't get the cold air back to the return register we will pressurize the basement and force the cold air out, however air leakage in a basement happens up high (because most of things are underground) so instead of blowing the cold air out (at the floor)and replacing it with hot air from the furnace, we blow the hot air (that is stratified at the ceiling) out the band joists and other openings located above grade.

Quote:
Dave, I understand all of that. My furnace is properly sized. I know that basements are figured different than above ground floors. I know zone heating would also do the trick. I'm looking for friendly conversation on the matter. It's Sunday and I'm kicking the thought around. You could of said, a return air vent would be your next logical step. That would of been fine with me. Thanks for your comments guys. Stan
I'm sorry I only pointed out specific facts for you to consider without having a "friendly conversation" on Sunday afternoon.

Considering how much you understand about your HVAC system, I don't understand why your "kicking the thought around".

"A return air vent would be your next logical step".



"working together to get-IR-done" Chris Walsh
Bracebridge, Ontario:


David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #12  
Old 2/1/10, 5:37 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is online now
Certified Master Inspector
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 9,542
Default Re: Basement Heat

Would it not be logical that no matter if the area is finished it still needs heat. Heat rises so the heat would not be wasted and would compensate the drop of air flow upstairs. You would want to run a separate trunk for the two vents added and not just tap off the upstairs ducts. In central Missouri we seldom run returns in basements and we are not experiencing any problems. I guess everybody has their way of doing things.
Reply With Quote
  #13  
Old 2/1/10, 6:21 PM
Linas Dapkus, CMI's Avatar
Linas Dapkus, CMI Linas Dapkus, CMI is online now
Certified Master Inspector ®
 
Join Date: Mar 2006
Location: Lockport, IL.
Posts: 12,391
Default Re: Basement Heat

Hey Stan, Dave is an HVAC guy. He's pretty close and may be able to help you out on a boring Sunday. Give him a call, he's got a mean bark but he don't bite.



Linas Dapkus, CMI & LEO wannabe
Dapkus Home Inspections
Go away Rosie. You haven't had anything useful to say since you lost your mind when Trump won.
You are such a loser.


For God so loved the world that he gave his one and only Son, that whoever believes in him shall not perish but have eternal life.
TRUMP/PENCE 2020

https://i.imgflip.com/1z058y.jpg
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
something else to chew on john bubber Structural Inspections 1355 9/1/17 5:32 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing, Ethics & Legal Issues for Inspectors 52 7/11/17 4:34 PM
Renovating Your Basement for Livability mkyriacou Canadian Home Inspectors 0 10/22/09 12:45 PM
Site grading and drainage wdevries Canadian Home Inspectors 5 10/6/09 11:23 PM
Options in selecting materials for basement construction wdevries Canadian Home Inspectors 2 8/4/08 2:30 PM

All times are GMT -4. The time now is 5:15 PM.
no new posts