Cool A/C Disconnect question

Hello evryone ! I have a quick question regarding an A/C unit at an Inspection today. Sorry I don't have a pic but I will describe it the best I can.

The A/C unit has no disconnect next to it. There is a breaker for the A/C unit in the Service Panel located approx. 30 feet away on the same wall. The panel itself is a Square D all in one(Meter and panel) and is kind of a b**ch to open if you are not familiar with this type. Anyway, back to my question. Does there need to be a disconnect closer to the A/C unit?

I know the IRC and NEC state that the disconnect needs to be in sight of the condensor. I am recommending having a disconnect installed next to the unit.



Rick Slocum
NACHI # 04072697
Whitewood , SD 57793
ABSOLUTE Home Inspection Service
Reply With Quote
  #2  
Old 9/20/06, 8:18 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
Certified Professional Inspector (CPI)
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 16,497
Default Re: A/C Disconnect question

Richard, if you are familiar with the IRC and NEC with regards to this situation, how did you come up with your recommendation?



"This should really be posted in the EMERGENCY FORUM"

Reply With Quote
  #3  
Old 9/20/06, 8:28 PM
Richard D. Slocum's Avatar
Richard D. Slocum Richard D. Slocum is offline
Certified Professional Inspector (CPI)
 
Join Date: Jul 2004
Location: Whitewood ,SD 57793
Posts: 236
Default Re: A/C Disconnect question

Hi Brian. My recommendation is based on the fact that the disconnect isn't TRUELY in sight of the condenser. Even though I know and the Client knows that there is a breaker in the Service panel (which is located on the same wall and in sight of the condenser) dedicated to the A/C.

Would you have done anything differently? I am always trying to learn something from you guys out there!

Rick



Rick Slocum
NACHI # 04072697
Whitewood , SD 57793
ABSOLUTE Home Inspection Service
Reply With Quote
  #4  
Old 9/20/06, 8:33 PM
tgodfrey tgodfrey is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Dunsford, ON
Posts: 8
Default Re: A/C Disconnect question

It is my belief that the disconnect should be in sight of the unit and within 5' I'm not 100% on this. Anyone else?
Reply With Quote
  #5  
Old 9/20/06, 8:44 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
Certified Professional Inspector (CPI)
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 16,497
Default Re: A/C Disconnect question

I think you did the right thing Richard a disconnect needs to be insight for the condenser. I initially did not read your question correctly



"This should really be posted in the EMERGENCY FORUM"

Reply With Quote
  #6  
Old 9/20/06, 8:57 PM
Richard D. Slocum's Avatar
Richard D. Slocum Richard D. Slocum is offline
Certified Professional Inspector (CPI)
 
Join Date: Jul 2004
Location: Whitewood ,SD 57793
Posts: 236
Default Re: A/C Disconnect question

No prob Brian. Thanks for the input!



Rick Slocum
NACHI # 04072697
Whitewood , SD 57793
ABSOLUTE Home Inspection Service
Reply With Quote
  #7  
Old 9/20/06, 8:58 PM
Richard D. Slocum's Avatar
Richard D. Slocum Richard D. Slocum is offline
Certified Professional Inspector (CPI)
 
Join Date: Jul 2004
Location: Whitewood ,SD 57793
Posts: 236
Default Re: A/C Disconnect question

Thanks Thaine!



Rick Slocum
NACHI # 04072697
Whitewood , SD 57793
ABSOLUTE Home Inspection Service
Reply With Quote
  #8  
Old 9/20/06, 9:10 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
Certified Professional Inspector (CPI)
 
Join Date: Jul 2004
Location: Boerne, TX
Posts: 4,863
Default Re: A/C Disconnect question

A breaker in a service panel 30 feet away would be just fine by me and I would not even remotely think to write that up as deficient in any way. Anything more would really be nit-picking I think. Wouldn't you say the attached example is OK?
Attachment 5664

Last edited by mboyett; 4/9/09 at 10:38 PM..
Reply With Quote
  #9  
Old 9/20/06, 9:25 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
Certified Professional Inspector (CPI)
 
Join Date: Sep 2005
Location: McKinney, TX
Posts: 9,475
Send a message via Skype™ to pabernathy
Default Re: A/C Disconnect question

Hey Guys,

In this application if the outside unit is on the same wall as a exterior panel and " Within Sight" then it should be fine.

Keep in mind that their is a limit to within sight....it is 50' and no more.....check out how the NEC defines " In Sight From" to up to 50'.....so keep that in mind.....their is STILL a limit to "within sight"



Paul W. Abernathy,CMI
NFPA 70 (NEC) Code Making Panel 5 and 17 Committee Member
Visit www.ElectricalCodeAcademy.com
Videos On Demand -Inspecting Electrical Panels https://electricalcodeacademy.pivots...l-panel-/55034 Get $2.00 Off Coupon Code - NACHI2016


Disclaimer - All my posts on this forum are of my own personal opinion and represent Electrical Code Academy, Inc.
Reply With Quote
  #10  
Old 9/20/06, 9:32 PM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 13,666
Default Re: A/C Disconnect question

I'm with Michael and Paul here. A breaker in a panel is a disconnect. If it's within site, there's no need to add another.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 9/21/06, 12:13 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
Certified Professional Inspector (CPI)
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 16,497
Default Re: A/C Disconnect question

Quote:
Originally Posted by mboyett
A breaker in a service panel 30 feet away would be just fine by me and I would not even remotely think to write that up as deficient in any way. Anything more would really be nit-picking I think. Wouldn't you say the attached example is OK?
Attachment 5664
That is a service disconnect is it not? So yes that is ok by me.


What does the IRC say about condensers? I do not think the breaker in the main panel counts for condensers does it? I do not think even a lockable breaker counts. Hey, I have already miss read this post once, so what do I know.



"This should really be posted in the EMERGENCY FORUM"

Reply With Quote
  #12  
Old 9/21/06, 12:32 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
Certified Professional Inspector (CPI)
 
Join Date: Jul 2004
Location: Boerne, TX
Posts: 4,863
Default Re: A/C Disconnect question

One, I do believe a breaker in a main panel within sight of the condenser is sufficient. I can't find a reference to that in the IRC right now but I'll keep looking. Two, I think the original question was asking if it was OK that the breaker that was admittedly within 30 feet of the condenser was behind a panel cover and therefore 'not within sight'...that's where I was going with my 'nit-picking' remark.
Reply With Quote
  #13  
Old 9/21/06, 12:41 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
Certified Professional Inspector (CPI)
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 16,497
Default Re: A/C Disconnect question

I read it that way too at first Michael. But I think the IRC frowns on a breaker in the main panel being the service disconnect. But, I have been wrong before.



"This should really be posted in the EMERGENCY FORUM"

Reply With Quote
  #14  
Old 9/21/06, 1:07 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
Certified Professional Inspector (CPI)
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 16,497
Default Re: A/C Disconnect question

And I am wrong again, 03 IRC T4001.5 covers it. As long as it is in sight.



"This should really be posted in the EMERGENCY FORUM"

Reply With Quote
  #15  
Old 9/21/06, 1:12 AM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 13,666
Default Re: A/C Disconnect question

Quote:
Originally Posted by bkelly2
And I am wrong again, 03 IRC T4001.5 covers it. As long as it is in sight.
Yep. A disconnect can be a breaker, switch, pull-out, etc., etc., and it doesn't matter if it's in a service panel, remote panel, switch or fuse box or whatever. It just needs to be accessible and within sight.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Service disconnect question wsiegel Electrical Inspections 3 8/28/07 10:59 AM
Well pump disconnect sfalvey Plumbing Inspections 0 11/17/06 1:23 AM
100 Amp Meter, 200 Amp Disconnect jweinberg Electrical Inspections 8 8/15/06 1:32 PM

All times are GMT -4. The time now is 10:14 AM.
no new posts