Default Fresh air intake question

Newly installed high efficient furnace drawing fresh air from the basement utility room and crawlspace.

Isn't there something about being a certain distance from the gas water heater?

Fresh air intake question-p9210071-jpg

Fresh air intake question-p9210072-jpg
Reply With Quote
Need a home inspection in Pennsylvania? Check out InterNACHI's listing of Pennsylvania certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/23/13, 9:19 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
Certified Professional Inspector (CPI)
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 10,664
Default Re: Fresh air intake question

Quote:
Originally Posted by jhorton1 View Post
Newly installed high efficient furnace drawing fresh air from the basement utility room and crawlspace.

Isn't there something about being a certain distance from the gas water heater?

Attachment 68600

Attachment 68601
Yipper needs to be at least 10 feet separation



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
55 years in the Trades
Okla State License # 130
580-268-3340
Reply With Quote
  #3  
Old 9/23/13, 9:32 AM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
Certified Master Inspector ®
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 15,368
Default Re: Fresh air intake question

Quote:
Originally Posted by cbottger View Post
Yipper needs to be at least 10 feet separation
For combustion air?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE «

Jeff Pope
JPI Home Inspection Service
(661) 212-0738
Los Angeles, Santa Clarita & Antelope Valley CA
Reply With Quote
  #4  
Old 9/23/13, 9:56 AM
Juan C. Jimenez Juan C. Jimenez is offline
Certified Professional Inspector (CPI)
 
Join Date: Jan 2012
Location: central va
Posts: 7,690
Default Re: Fresh air intake question

Quote:
Originally Posted by cbottger View Post
Yipper needs to be at least 10 feet separation
I thought that was for the return air.



Juan Jimenez
A House on a Rock Home Inspections LLC
God. Family. Home.
804-269-4321
Richmond Home Inspector
Richmond Chimney Sweep
Richmond Radon Testing


Reply With Quote
  #5  
Old 9/23/13, 9:59 AM
Bob Elliott, 450.0002662's Avatar
Bob Elliott, 450.0002662 Bob Elliott, 450.0002662 is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2006
Location: Chicago
Posts: 37,730
Default Re: Fresh air intake question

10' separation is not possible in most utility closets .
I see them almost touching all the time however Charlie may have gotten confused by the question and been thinking return venting as follows below.......



311.3(6.3(c))Return-air inlets shall not be located within ten (10) feet (3,048 mm) from any appliance firebox or draft diverter in the same enclosed room or confined space.

So any firebox with an opening into the interior within 10 feet and in the same room as a return is considered hazardous.


My concern is always with air intakes on cat 4 units that are not utilizing air from the exterior in tight places with lack of ventilation or a different pressure zone.

see below......
(source unknown)

1) Exterior air, in the winter, is colder and denser. It therefore has a slightly higher oxygen content and the HE furnaces are designed to use the extra oxygen and burn cleaner, therefore, more efficiently.

2) By taking combustion air from the interior, you lower the air pressure inside and create a negative pressure condition in the house. This strains the furnace to get more air and also leads to more cold air leaks into the house.

Finally, why would you want to take interior air, that you have already spent money heating, and send it out the furnace? Think the old style fireplaces, with the combustion and draft air coming from the interior, vs. the newer type fireplaces with a sealed hearth and an exterior combustion air vent out the back of the chimney.

Last but not least you are drawing chemicals from the air into your components.
Reply With Quote
  #6  
Old 9/23/13, 10:12 AM
KEVIN WOOD, CMI KEVIN WOOD, CMI is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,820
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fresh air intake question

Nice Bob! I guess I will have to start saying (Unknown source too) This is getting retarded. I am sure Charley new about the 10 foot rule and was referring to the shared air.
Reply With Quote
  #7  
Old 9/23/13, 12:18 PM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Retired Member
 
Join Date: Jun 2005
Location: Nashville, TN
Posts: 10,557
Default Re: Fresh air intake question

That would probably be my least concern. The basement/crawlspace is an unconditioned space.

What troubles me is a high-efficiency condensing furnace installed:
without the fresh air intake hooked up.
No trap on the condensate drain.
Auxiliary drain is open. Both the un-trapped drain and the open fitting discharging air into the unconditioned space (resulting in building depressurization).
The condensate drain dumps on the floor (next to the dehumidifier).

Obviously an installation by "I have my head up my *** HVAC specialists".



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40 (Retired)
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
HVAC Certification EPA Cert#2046620
BPI# 5015804
Reply With Quote
  #8  
Old 9/23/13, 3:27 PM
Juan C. Jimenez Juan C. Jimenez is offline
Certified Professional Inspector (CPI)
 
Join Date: Jan 2012
Location: central va
Posts: 7,690
Default Re: Fresh air intake question

Did anyone else notice the upwards sloped drain pipe?



Juan Jimenez
A House on a Rock Home Inspections LLC
God. Family. Home.
804-269-4321
Richmond Home Inspector
Richmond Chimney Sweep
Richmond Radon Testing


Reply With Quote
  #9  
Old 9/23/13, 3:47 PM
Erik Schmidt Erik Schmidt is online now
Certified Professional Inspector (CPI)
 
Join Date: Nov 2012
Location: Edmonton Alberta
Posts: 2,379
Default Re: Fresh air intake question

Quote:
Originally Posted by jhorton1 View Post
Newly installed high efficient furnace drawing fresh air from the basement utility room and crawlspace.

Isn't there something about being a certain distance from the gas water heater?

Attachment 68600

Attachment 68601
The picture shows combustion air not fresh air. Combustion air should come from outside ideally, but some AHJs will allow it to be taken from inside if the furnace is not in an enclosed furnace room and the building is not overly tight. From what I can see in the pic if the furnace is inside the building envelope it is a code question, refer to AHJ. If it is in unconditioned space there is no issue, provided there is ventilation

Fresh air is outside air ducted directly into the return air duct, and is used to pressurize the building or replace exhausted air. A fresh air intake should be located on the outside somewhere where it will not get contaminated by exhausts or vents.

The 'ten foot' rule is about return air openings in the return air duct which can not be within 10 feet of the furnace if the furnace is in an open conditioned space, such as an undeveloped basement. Return air intakes are not permitted inside an enclosed furnace room.



Erik Schmidt


East Side Home Inspection
Edmonton Alberta
780 477 2666
Reply With Quote
  #10  
Old 9/23/13, 4:54 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
Certified Professional Inspector (CPI)
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 10,664
Default Re: Fresh air intake question

Ya I F up I was thinking return air not combustion air I was trying to get out the door 75 miles to first job



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
55 years in the Trades
Okla State License # 130
580-268-3340
Reply With Quote
  #11  
Old 9/23/13, 5:19 PM
Bob Elliott, 450.0002662's Avatar
Bob Elliott, 450.0002662 Bob Elliott, 450.0002662 is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2006
Location: Chicago
Posts: 37,730
Default Re: Fresh air intake question

Quote:
Originally Posted by eschmidt View Post
The picture shows combustion air not fresh air. Combustion air should come from outside ideally, but some AHJs will allow it to be taken from inside if the furnace is not in an enclosed furnace room and the building is not overly tight. From what I can see in the pic if the furnace is inside the building envelope it is a code question, refer to AHJ. If it is in unconditioned space there is no issue, provided there is ventilation

Fresh air is outside air ducted directly into the return air duct, and is used to pressurize the building or replace exhausted air. A fresh air intake should be located on the outside somewhere where it will not get contaminated by exhausts or vents.

The 'ten foot' rule is about return air openings in the return air duct which can not be within 10 feet of the furnace if the furnace is in an open conditioned space, such as an undeveloped basement. Return air intakes are not permitted inside an enclosed furnace room.
Best advice is to check manufacturer.
Some allow intake from indoors and others do not.

I always recommend external combustion air .
Reply With Quote
  #12  
Old 9/23/13, 5:32 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2007
Location: Minnesota & Northern Iowa
Posts: 30,942
Default Re: Fresh air intake question

Sample installation manual... begin reading bottom page 10... http://www.alpinehomeair.com/related...Q%202.2013.pdf



Jeffrey R. Jonas
Owatonna, Minnesota



"I am not a teacher, but an awakener."
- Robert Frost, American poet (1874-1963).

"We Respect Our Clients Right to Privacy"

Reply With Quote
  #13  
Old 9/23/13, 5:47 PM
Bob Elliott, 450.0002662's Avatar
Bob Elliott, 450.0002662 Bob Elliott, 450.0002662 is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2006
Location: Chicago
Posts: 37,730
Default Re: Fresh air intake question

Jeff ,the one in question is a cat 4.
Reply With Quote
Need a home inspection in Pennsylvania? Check out InterNACHI's listing of Pennsylvania certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 9/23/13, 6:01 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2007
Location: Minnesota & Northern Iowa
Posts: 30,942
Default Re: Fresh air intake question

Quote:
Originally Posted by belliott View Post
Jeff ,the one in question is a cat 4.
So is the one in my link...
Quote:
(Type FSP CATEGORY IV Direct or Non Direct Vent Air Furnace)
What's your point???

Did you bother to read the first few paragraphs?
Quote:
.....If this furnace is to be installed in the same space with other gas
appliances, such as a water heater, ensure there is an adequate
supply of combustion and ventilation air for the other appliances.
Refer to the latest edition of the National Fuel Gas Code NFPA 54/
ANSI Z223.1 (Section 5.3), or CSA B149.1-05 Installation Codes
(Sections 7.2, 7.3, or 7.4), or applicable provisions of the local
building codes for determining the combustion air requirements
for the appliances.
Most homes will require outside air be supplied to the furnace area
by means of ventilation grilles or ducts connecting directly to the
outdoors or spaces open to the outdoors such as attics or crawl
spaces.
The following information on air for combustion and ventilation is reproduced from the National.....



Jeffrey R. Jonas
Owatonna, Minnesota



"I am not a teacher, but an awakener."
- Robert Frost, American poet (1874-1963).

"We Respect Our Clients Right to Privacy"


Last edited by jjonas; 9/23/13 at 6:04 PM..
Reply With Quote
  #15  
Old 9/24/13, 5:23 AM
Joshua L. Frederick Joshua L. Frederick is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 4,826
Send a message via AIM to jfrederick
Default Re: Fresh air intake question

Quote:
Originally Posted by jjimenez View Post
Did anyone else notice the upwards sloped drain pipe?
Not to mention the wye also...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
What is this for? Fresh air intake or exhaust? jsafstrom Inspecting HVAC Systems 7 3/27/13 8:08 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 10:24 AM
Plumbing vent Routing Question kweiss Plumbing Inspections 7 11/1/06 10:57 PM
Rule of Thumb A/C sizing question from Practice Exam gliebig Inspecting HVAC Systems 9 5/25/06 2:38 AM
Question on Fresh air ducting rcross Inspecting HVAC Systems 10 1/25/06 2:25 PM

All times are GMT -4. The time now is 7:29 AM.
no new posts