Old 9/16/10, 12:58 AM
Kenny Rigler Kenny Rigler is offline
Default Furnace and WH in Bedroom Closet
Hey Guys-
This was in a townhouse where they installed the furnace and water heater in a closet off of the upstairs master bedroom. The closet space was only about 2'x8'x8'. At first I was going to write it up for not enough combustion air and for being off a sleeping area. There was another metal pipe that ran into the closet from the attic above, which at the time of the inspection, I wasn't sure what it was. I now realize that is was probably for combustion air to be pulled from the attic above. Is this application okay then? The fourth picture shows the pipe which runs next to the water heater and then terminates at about 2' off the floor. The last picture shows the furnace/water heater flue in the middle (yes I caught the combustible clearance) and the combustion air pipe on the right going through the ceiling. There was no access to the attic and it did not appear to come out of the roof. Thanks.
Kenny
Furnace and WH in Bedroom Closet-img_8849-jpg   Furnace and WH in Bedroom Closet-img_8848-jpg   Furnace and WH in Bedroom Closet-img_8847b-jpg   Furnace and WH in Bedroom Closet-img_8765b-jpg   Furnace and WH in Bedroom Closet-img_8767-jpg
Rigler Home Inspections
Hays, KS 67601
785-656-0272
Need a home inspection in Alaska? Check out InterNACHI's listing of Alaska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
Old 9/16/10, 1:23 AM
Bob Elliott, 450.0002662's Avatar
Bob Elliott, 450.0002662 Bob Elliott, 450.0002662 is online now
Default Re: Furnace and WH in Bedroom Closet
G2406.2 (303.3) Prohibited locations.
Appliances shall not be located in, or obtain combustion air from, any of the following rooms or spaces:
1. Sleeping rooms.
2. Bathrooms.
3. Toilet rooms.
4. Storage closets.
Exceptions:
1. Direct-vent appliances that obtain all combustion air directly from the outdoors.
2. Vented room heaters, wall furnaces, vented decorative appliances and decorative appliances for installation in vented solid fuel-burning fireplaces, provided that the room meets the required volume criteria of Section G2407.5.
3. A single wall-mounted unvented room heater equipped with an oxygen depletion safety shutoff system and installed in a bathroom, provided that the input rating does not exceed 6,000 Btu/h (1.76kW) and the bathroom meets the required volume criteria of Section G2407.5.
4. A single wall-mounted unvented room heater equipped with an oxygen depletion safety shutoff system and installed in a bedroom, provided that the input rating does not exceed 10,000 Btu/h (2.93 kW) and the bedroom meets the required volume criteria of Section G2407.5.
5. Appliances installed in an enclosure in which all combustion air is taken from the outdoors, in accordance with Section G2407.6. Access to such enclosure shall be through a solid weather-stripped door, equipped with an approved self-closing device.
Old 9/16/10, 1:31 AM
Christopher Currins, CMI Christopher Currins, CMI is offline
Certified Master Inspector ®
So if the attic is properly vented this can be accepted as outdoor air. The door in this closet would be the issue.?
Old 9/16/10, 2:29 AM
Chuck Evans's Avatar
From what I see in the photo and your description the combustion air provision is not proper based on current IRC standards. Should be two ducts one terminating within 12 inches of the ceiling and one terminating within 12 inches of the floor.
SECTION M1703
ALL AIR FROM OUTDOORS
M1703.1 Outdoor air.
Where the space in which fuel-burning appliances are located does not meet the criterion for indoor air specified in Section M1702, outside combustion air shall be supplied as specified in Section M1703.2.
M1703.2 Two openings or ducts.
Outside combustion air shall be supplied through openings or ducts, as illustrated in Figures M1703.2(1), M1703.2(2), M1703.2(3) and M1703.2(4). One opening shall be within 12 inches (305 mm) of the top of the enclosure, and one within 12 inches (305 mm) of the bottom of the enclosure. Openings are permitted to connect to spaces directly communicating with the outdoors, such as ventilated crawl spaces or ventilated attic spaces. The same duct or opening shall not serve both combustion air openings. The duct serving the upper opening shall be level or extend upward from the appliance space.
M1703.2.1 Size of openings.
Where communicating with the outdoors by means of vertical ducts, each opening shall have a free area of at least 1 square inch per 4,000 Btu/h (0.550 mm2/W) of total input rating of all appliances in the space. Where horizontal ducts are used, each opening shall have a free area of at least 1 square inch per 2,000 Btu/h (0.275 mm2/W) of total input of all appliances in the space. Ducts shall be of the same minimum cross-sectional area as
the required free area of the openings towhich they connect. The minimum cross-sectional dimension of rectangular air ducts shall be 3 inches (76 mm).
M1703.3Attic combustion air.
Combustion air obtained from an attic area, as illustrated in FigureM1703.2(3), shall be in accordance with the following:
1. The attic ventilation shall be sufficient to provide the required volume of combustion air.
2. The combustion air opening shall be provided with a metal sleeve extending from the appliance enclosure to at least 6 inches (152 mm) above the top of the ceiling joists and ceiling insulation.
3. An inlet air duct within an outlet air duct shall be an acceptable means of supplying attic combustion air to an appliance room provided that the inlet duct extends at least 12 inches (305 mm) above the top of the outlet duct
in the attic space, as illustrated in Figure M1703.3.
4. The end of ducts that terminate in an attic shall not be screened.
Chuck Evans (TREC #7657)
The Woodlands Home Inspections
Magnolia TX Home Inspections & Thermography
Houston, TX
_______________________
Awards Committee Member
Old 9/16/10, 10:48 AM
Thanks for the replies and thanks for the code reference Chuck. I agree...not enough openings. "The same duct or opening shall not serve both combustion air openings" (M1703.2). In this case, they used the same pipe and from everything I could see, it was not an inlet air duct within an outlet air duct installation. And besides, either way, the openings do not meet the required 1 square inch per 4,000 Btu input. Along with that, the door was not weatherstripped with a self-closing device and there was certainly not 12" of total clearance space on the sides of the furnace. I'll write it up as not meeting todays safety recommendations for combustion air. Thanks for the help!
Kenny
Hays, KS 67601
785-656-0272
Old 9/21/10, 10:49 PM
Kenneth Dolin, HI-59's Avatar
Kenneth Dolin, HI-59 Kenneth Dolin, HI-59 is offline
wow, did they at least put a CO detector in the room?
Ken Dolin
CMI
Kenco Home Inspections
WWW.Kenco.org
State of Florida Licensed Home Inspector HI 59
Old 9/21/10, 11:31 PM
That is correct Chris.
Old 9/21/10, 11:32 PM
Kenny
One square inch per 1000 btu.
Old 9/26/10, 11:26 AM
Dan Bowers, CMI, ACI's Avatar
Dan Bowers, CMI, ACI Dan Bowers, CMI, ACI is online now
You guys are getting to be real nitpickers and alarmists.
If you leave the bedroom windows open all the time and the take the door to the master bedroom off this could work and not be a big issue.
Try to start thinking outside the box. Remember our whole goal is to help close the deal, so all the commissioned folks can get paid.
Old 5/15/18, 12:52 AM
John Paul de Oliveira's Avatar
John Paul de Oliveira John Paul de Oliveira is offline
This blast from the past from Dan prompted me to bring forward the thread. LOL
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing, Ethics & Legal Issues for Inspectors 52 7/11/17 4:34 PM
Furnace in a bedroom closet rbrady Inspecting HVAC Systems 14 6/17/08 12:08 AM
Furnace and water heater in a bedroom closet tlorenz Interior Inspections 19 5/26/08 9:44 PM
Return in Furnace closet dmacy Inspecting HVAC Systems 2 2/24/08 4:30 PM
Fininshed bedroom in basement next furnace cyezza Inspecting HVAC Systems 9 11/28/06 6:41 AM