Default Heat pump operation

Home has a 2 ton Carrier air source heat pump. 17 years old

Temperature at time of the inspection was 15 degrees. It was operating in the heat mode and heating properly.

I do not get how it was extracting heat from the outside air at 15 degrees.

Mine is set at 30 degrees and it is a 2008 unit.

I do not understand how the exterior unit can take 15 degree air and operate properly.

I also tried in emergency heat mode and it operated.
Reply With Quote
Find an InterNACHI certified Indiana Home Inspector (and anywhere else in North America)
  #2  
Old 1/2/10, 2:46 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
Certified Professional Inspector (CPI)
 
Join Date: Jan 2005
Location: Mt Pleasant SC
Posts: 3,402
Default Re: Heat pump operation

What do you mean by "mine is set to 30 degrees" ?

Is that when it switches over to an aux heat source?

Heat pump operation depends on the type of refrigerant, the newer R410 is much better since it is used in units that have other advanced designs.

At 15 deg F, some heat can be absorbed from the exterior but most likely it was running in regular and aux heat strip mode at the same time if you had good warm air. If you had the t-stat up over 2 degrees it would have been running the electric strips also unless programmed out via a special t-stat that also uses an exterior temp sensor. Some units can even sense that the house is not gaining any heat and will add in the aux strips even at a one degree t-stat command.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Fort Mill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #3  
Old 1/2/10, 3:51 PM
David C. Macy, CMI's Avatar
David C. Macy, CMI David C. Macy, CMI is online now
Certified Master Inspector
 
Join Date: Jan 2004
Location: NE. OH
Posts: 4,829
Default Re: Heat pump operation

Quote:
Originally Posted by bking View Post
What do you mean by "mine is set to 30 degrees" ?

Is that when it switches over to an aux heat source?

Heat pump operation depends on the type of refrigerant, the newer R410 is much better since it is used in units that have other advanced designs.

At 15 deg F, some heat can be absorbed from the exterior but most likely it was running in regular and aux heat strip mode at the same time if you had good warm air. If you had the t-stat up over 2 degrees it would have been running the electric strips also unless programmed out via a special t-stat that also uses an exterior temp sensor. Some units can even sense that the house is not gaining any heat and will add in the aux strips even at a one degree t-stat command.
Yes, my unit switches over to gas.

The thermostat at this home indicated it was running in normal heat mode. The heat pump was running when I arrived and I tried turning up 10 degrees to see if the aux heat would automatically turn on. It did not.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing, Ethics & Legal Issues for Inspectors 52 7/11/17 3:34 PM
Radiant ceiling heat? bmargiotti Inspecting HVAC Systems 17 7/27/13 5:20 PM
Heat pump in a 80+ year old masonry house jskrypka Inspecting HVAC Systems 9 11/25/06 10:47 PM
Question on my heat pump dbush Inspecting HVAC Systems 7 3/12/06 12:15 AM
Armstrong heat pump -- good or bad? skipswift Inspecting HVAC Systems 3 2/13/06 9:17 PM

All times are GMT -4. The time now is 2:41 AM.
no new posts