Question Heating flue vent cap clearance (side wall)

What would be a recommended clearance for this boiler vent cap from a vinyl covered side wall. I can't find any thing myself online I am trying.
Attached Thumbnails
Heating flue vent cap clearance (side wall)-51def274-3769-476d-8daf-8b80642630d7-jpg  
Reply With Quote
Need a home inspection in District Of Columbia? Check out InterNACHI's listing of District Of Columbia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/21/18, 9:37 AM
David Wigger, #70000551's Avatar
David Wigger, #70000551 David Wigger, #70000551 is online now
Certified Professional Inspector (CPI)
 
Join Date: Jul 2006
Location: Jenks, OK
Posts: 181
Default Re: Heating flue vent cap clearance (side wall)

I would think the 2/10 would come into play. (Although there are no boilers in my neck of the woods.)
Attached Thumbnails
Heating flue vent cap clearance (side wall)-g2427-6-gas-vent-termination-clearance-jpg  
Reply With Quote
  #3  
Old 7/21/18, 10:02 AM
Joshua L. Frederick Joshua L. Frederick is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 4,715
Send a message via AIM to jfrederick
Default Re: Heating flue vent cap clearance (side wall)

As David graphic depicts, It's a potential drafting/safety issue, not a siding one.




http://northwestohiohomeinspector.com

Defiance home inspector
Northwest Ohio home inspector
Reply With Quote
  #4  
Old 7/22/18, 9:31 AM
Erik Schmidt Erik Schmidt is online now
Certified Professional Inspector (CPI)
 
Join Date: Nov 2012
Location: Edmonton Alberta
Posts: 2,333
Default Re: Heating flue vent cap clearance (side wall)

It would have to come from the manufacturer's installation instructions for venting. I was checking on a class III unit heater and it was 12 inches. The pic looks like it is too close for vinyl.



Erik Schmidt


East Side Home Inspection
Edmonton Alberta
780 477 2666
Reply With Quote
  #5  
Old 7/25/18, 8:00 PM
John Bowman's Avatar
John Bowman John Bowman is online now
Certified Professional Inspector (CPI)
 
Join Date: Dec 2003
Posts: 2,437
Default Re: Heating flue vent cap clearance (side wall)

Heating flue vent cap clearance (side wall)-guide-boilers-png


Great Book On Boilers. Just $25.00 Buy It Here




2010-Present NACBI Executive Director
2005-2009 NACHI Executive Director
National Association of Commercial Building Inspectors & Thermographers
Building Intelligence Center
Determine the Date of Manufacture of your HVAC and Water Heating equipment


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


All times are GMT -4. The time now is 12:35 PM.
no new posts