Default HVAC testing at 60 Degrees F

During an inspection today, I used the thermostat to start the A/C for a few minutes at 60 Degrees F. I do this to see if the compressor fires, not to test the temperature differential. After a minute or two, the circuit breaker tripped off, it is my understanding of A/C principals that the compressor should not be run for a long time at low temperatures and that a short test like this will not run HIGH amps and should not trip the breaker? Any input from a A/C guru?
Thanks George
Reply With Quote
Need a home inspection in North Carolina? Check out InterNACHI's listing of North Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/16/10, 1:28 AM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
Certified Master Inspector ®
 
Join Date: Nov 2005
Location: Merriam, Kansas
Posts: 1,965
Default Re: HVAC testing at 60 Degrees F

I am not a AC guru. That should not happen. Defer the system to a
HVAC contractor.



Mid America Property Inspections, Inc.
Shawnee, KS 66216
www.mapii.com
NACHI # 05110992
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #3  
Old 3/16/10, 2:05 AM
George F. Fransway George F. Fransway is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Tucson, AZ
Posts: 43
Default Re: HVAC testing at 60 Degrees F

Thanks
Reply With Quote
  #4  
Old 3/16/10, 10:42 AM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
Certified Master Inspector
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 14,618
Default Re: HVAC testing at 60 Degrees F

A tripping breaker is an indication of a failing compressor. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 3/16/10, 12:06 PM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Jun 2005
Location: Nashville, TN
Posts: 10,275
Default Re: HVAC testing at 60 Degrees F

Put a little oil and liquid refrigerant on top of that compressor piston and watch the amperage go up!

Do you know what a low ambient control is?

You may have locked up the compressor. Locked rotor average tends to trip circuit breakers.

Anyone testing air conditioning under low ambient conditions, I highly recommend that you do it from outside the house, not at the thermostat.

You can turn the circuit breaker off when you hear the compressor about to jump out of the condensing unit.



"working together to get-IR-done" Chris Walsh
Bracebridge, Ontario:


David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #6  
Old 3/16/10, 1:16 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,587
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC testing at 60 Degrees F

Quote:
Originally Posted by dandersen View Post
(1) Put a little oil and liquid refrigerant on top of that compressor piston and watch the amperage go up!

Do you know what a low ambient control is?

You may have locked up the compressor. Locked rotor average tends to trip circuit breakers. (Locked rotor amperage tends to trip circuit breakers.)

Anyone testing air conditioning under low ambient conditions, I highly recommend that you do it from outside the house, not at the thermostat.

You can turn the circuit breaker off when you hear the compressor about to jump out of the condensing unit.
(1) Shouldn't the accumulator catch this if the unit is only run momentarily?
Reply With Quote
  #7  
Old 3/16/10, 4:30 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC testing at 60 Degrees F

The compressor crankcase heater may have failed and the refrigerant migrated to the compressor oil. Start up under that condition could lead to compressor pulling in foaming oil and locking up.
Reply With Quote
  #8  
Old 3/16/10, 4:51 PM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Jun 2005
Location: Nashville, TN
Posts: 10,275
Default Re: HVAC testing at 60 Degrees F

Not many a/c units have a crankcase heater!

It costs too much!

Only Heat Pumps do.



"working together to get-IR-done" Chris Walsh
Bracebridge, Ontario:


David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #9  
Old 3/16/10, 5:13 PM
Brian K. Smith's Avatar
Brian K. Smith Brian K. Smith is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Ripon,CA
Posts: 1,439
Send a message via AIM to bsmith2
Default Re: HVAC testing at 60 Degrees F

my question why even take the chance?
Reply With Quote
  #10  
Old 3/19/10, 1:23 AM
George F. Fransway George F. Fransway is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Tucson, AZ
Posts: 43
Default Re: HVAC testing at 60 Degrees F

good input thanks to all. george
Reply With Quote
  #11  
Old 3/19/10, 1:33 AM
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 5,103
Default Re: HVAC testing at 60 Degrees F

Quote:
Originally Posted by Brian A. MacNeish View Post
(1) Shouldn't the accumulator catch this if the unit is only run momentarily?
He didn't say it was a Heat pump. He said it was an HVAC which leads me to believe it was a standard air conditioner which does not have an accumulator (heat pumps do).





Reply With Quote
  #12  
Old 3/19/10, 6:59 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,587
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC testing at 60 Degrees F

Quote:
Originally Posted by dedwards View Post
He didn't say it was a Heat pump. He said it was an HVAC which leads me to believe it was a standard air conditioner which does not have an accumulator (heat pumps do).
I live in a cool/cold climate. Just about everything I see up here is HP/AC.
Reply With Quote
  #13  
Old 3/19/10, 2:13 PM
C. Scott Justason's Avatar
C. Scott Justason C. Scott Justason is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Eastern Iowa
Posts: 616
Default Re: HVAC testing at 60 Degrees F

Quote:
Originally Posted by dandersen View Post
Put a little oil and liquid refrigerant on top of that compressor piston and watch the amperage go up!

Do you know what a low ambient control is?

You may have locked up the compressor. Locked rotor average tends to trip circuit breakers.

Anyone testing air conditioning under low ambient conditions, I highly recommend that you do it from outside the house, not at the thermostat.

You can turn the circuit breaker off when you hear the compressor about to jump out of the condensing unit.
60 degrees is not a low ambient condition. I don't care where your from.
Reply With Quote
Need a home inspection in North Carolina? Check out InterNACHI's listing of North Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 3/19/10, 3:06 PM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Jun 2005
Location: Nashville, TN
Posts: 10,275
Default Re: HVAC testing at 60 Degrees F

Somebody thinks so.

What's your point?

Please enlighten me as to what a low ambient condition actually is...

I happen to be from the South (at this point in my life) and it gets down to about 21° at night and up to 60 during the day.
Do you think this is okey-dokey to run an air conditioner at 10 o'clock in the morning when it reaches 60?

70 psig is the design operating temperature for R-22 refrigerant.

What's the saturation temperature at this pressure at atmospheric conditions at sea level?

Now please enlighten us as to what the saturation pressure is at 32°F for R-22 refrigerant.

What's the pressure difference?

Does a freezing evaporator coil not potentially cause refrigeration slugging?

At what outdoor temperature does refrigeration pressures on the high side fall to a point where the back pressure falls below the freezing temperature? Don't tell me it depends on the equipment.

Is it just slightly possible that cool outdoor air and no load in the house may cause a "low ambient condition"?

Please keep in mind that no one here is required to be certified to put a set of refrigeration gauges on an air-conditioning unit.
Please explain how everyone here will know when a low ambient condition exists without installing a set of refrigeration gauges!?



"working together to get-IR-done" Chris Walsh
Bracebridge, Ontario:


David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission

Last edited by dandersen; 3/19/10 at 3:19 PM..
Reply With Quote
  #15  
Old 3/19/10, 7:23 PM
Mark Nahrgang, C.R.I.'s Avatar
Mark Nahrgang, C.R.I. Mark Nahrgang, C.R.I. is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,746
Default Re: HVAC testing at 60 Degrees F

Quote:
2.5. Cooling
I. The inspector shall inspect:
A. the central cooling equipment using normal operating controls.
II. The inspector is not required to:
A. determine the uniformity, temperature, flow, balance, distribution, size, capacity, BTU, or supply adequacy of the cooling system.
B. inspect window units, through-wall units, or electronic air filters.
C. operate equipment or systems if exterior temperature is below 60 degrees Fahrenheit, or when other circumstances are not conducive to safe operation, or may damage the equipment.
D. inspect or determine thermostat calibration, cooling anticipation, or automatic setbacks or clocks.
E. examine electrical current, coolant fluids or gases, or coolant leakage.
60 degrees is fine. My personal rule of thumb is 65 just to be on the safe side, but I've been known to fudge on that for a degree or two. Most of the AC operator manual I've seen actually list values less than either (down in the 50-55 range).

The breaker tripped because of a system problem, not an inspection problem.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing, Ethics & Legal Issues for Inspectors 52 7/11/17 4:34 PM
Testing HVAC if Temperture is below 60 degrees dnasser Inspecting HVAC Systems 4 4/14/09 12:44 AM
Well Water Testing in Coeur d’Alene, ID 83815 rspriggs Ancillary Inspection Services 0 1/9/09 4:31 AM
Moisture in slabs mcyr Structural Inspections 7 8/20/07 8:33 PM
bbbb mcyr Structural Inspections 1 8/19/07 11:26 PM

All times are GMT -4. The time now is 12:56 AM.
no new posts