Default Re: Inuslation on suction line

Quote:
Originally Posted by bhoagland View Post
For those of you guys that are really into A/C I want to know how it is significant (worth noting as a defect) if two feet of insulation is damaged or even missing from the soil to the condensing unit on the suction line with respect to the functionality of the system.
I thought we were talking "significant" defects. I personally would not mention it as it will not affect the operation of the a/c unit at all. If two feet or even six inches were exposed on the inside of the home I would mention it due to the fact that condensation will form and be a nuisance.
Reply With Quote
Find an InterNACHI certified Alabama Home Inspector (and anywhere else in North America)
  #17  
Old 12/7/09, 6:20 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
Certified Master Inspector ®
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,817
Default Re: Inuslation on suction line

Quote:
Originally Posted by dandersen View Post
No he is not.
He is talking about the piping inside the unit.
David,

Calm down, Bud.

He stated the last two feet. I had thought he was referring to the piping from the building to the condenser.
Reply With Quote
  #18  
Old 4/28/16, 3:00 PM
Kenton Shepard, CMI's Avatar
Kenton Shepard, CMI Kenton Shepard, CMI is online now
Certified Master Inspector
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 6,571
Send a message via ICQ to kshepard
Default Re: Inuslation on suction line

I just talked to HVAC companies in CA and FL, and they pretty much agreed with David. This is how I'm describing it in that part of the House of Horrors:

The concern with insulation missing from the AC suction lines is condensation. At the exterior, this condensation evaporates, so it affects nothing. The likelihood of damage resulting from condensation due to missing insulation depends on the climate zone in which the home is located and the location (inside the home) of the missing insulation. Damage is more likely in humid climates, and in confined spaces containing moisture absorbent materials, and that have minimal air movement.
The loss in efficiency is very slight compared to a dirty condenser unit or dirty evaporator coils.



Kenton Shepard, CMI Inspector/Instructor


Designer/Builder: House of Horrors 1&2
Author: InterNACHI Narrative Library


Last edited by kshepard; 4/28/16 at 3:08 PM..
Reply With Quote
  #19  
Old 4/28/16, 7:15 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
Certified Professional Inspector (CPI)
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 10,623
Default Re: Inuslation on suction line

Quote:
Originally Posted by kshepard View Post
I just talked to HVAC companies in CA and FL, and they pretty much agreed with David. This is how I'm describing it in that part of the House of Horrors:

The concern with insulation missing from the AC suction lines is condensation. At the exterior, this condensation evaporates, so it affects nothing. The likelihood of damage resulting from condensation due to missing insulation depends on the climate zone in which the home is located and the location (inside the home) of the missing insulation. Damage is more likely in humid climates, and in confined spaces containing moisture absorbent materials, and that have minimal air movement.
The loss in efficiency is very slight compared to a dirty condenser unit or dirty evaporator coils.
Ya picked a poor topic to discuss. missing insulation is to me more of a cosmetic issue. So did you ask those same HVAC contractors why they all install insulation at the exterior condensing unit when they first installed the unit . If its not so important why put it there in the first place.

Kenton the temp of the returning Freon is what helps to cool the winding's in the compressor. The cooler the compressor operates generally speaking the longer its longevity. The shorter the exterior suction line is not much of a issue the longer the suction line and with exposure to 100+ degree temp shining on that bare copper the warmer the Freon to the compressor . I have a policy that I write up missing insulation where ever it was installed. I don't make a big stink out it and most of the time it never gets replaced, sometimes it does



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
55 years in the Trades
Okla State License # 130
580-268-3340
Reply With Quote
  #20  
Old 4/28/16, 7:31 PM
Kenton Shepard, CMI's Avatar
Kenton Shepard, CMI Kenton Shepard, CMI is online now
Certified Master Inspector
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 6,571
Send a message via ICQ to kshepard
Default Re: Inuslation on suction line

Quote:
Originally Posted by cbottger View Post
Ya picked a poor topic to discuss. missing insulation is to me more of a cosmetic issue. So did you ask those same HVAC contractors why they all install insulation at the exterior condensing unit when they first installed the unit . If its not so important why put it there in the first place.

Kenton the temp of the returning Freon is what helps to cool the winding's in the compressor. The cooler the compressor operates generally speaking the longer its longevity. The shorter the exterior suction line is not much of a issue the longer the suction line and with exposure to 100+ degree temp shining on that bare copper the warmer the Freon to the compressor . I have a policy that I write up missing insulation where ever it was installed. I don't make a big stink out it and most of the time it never gets replaced, sometimes it does
Well Charlie... most of us see it, so it needs to be addressed somehow. Cosmetic issue was what two out of three called it. None mentioned the returning Freon temp, though.



Kenton Shepard, CMI Inspector/Instructor


Designer/Builder: House of Horrors 1&2
Author: InterNACHI Narrative Library

Reply With Quote
  #21  
Old 4/28/16, 8:57 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
Certified Professional Inspector (CPI)
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 10,623
Default Re: Inuslation on suction line

Quote:
Originally Posted by kshepard View Post
Well Charlie... most of us see it, so it needs to be addressed somehow. Cosmetic issue was what two out of three called it. None mentioned the returning Freon temp, though.
Not many of us still around that have 40 years experience working on those system



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
55 years in the Trades
Okla State License # 130
580-268-3340
Reply With Quote
  #22  
Old 4/29/16, 10:43 AM
Erik Schmidt Erik Schmidt is online now
Certified Professional Inspector (CPI)
 
Join Date: Nov 2012
Location: Edmonton Alberta
Posts: 2,360
Default Re: Inuslation on suction line

Quote:
Originally Posted by kshepard View Post
Cosmetic issue was what two out of three called it.
Haha so that's how its done! I guess OJ really was innocent.



Erik Schmidt


East Side Home Inspection
Edmonton Alberta
780 477 2666
Reply With Quote
  #23  
Old 4/29/16, 11:46 AM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Retired Member
 
Join Date: Jun 2005
Location: Nashville, TN
Posts: 10,540
Default Re: Inuslation on suction line

No insulation on the suction line is one thing, but 2' between the house and unit is not a concern to me in air conditioning.

If you compare the 4' inside the condenser with high speed 130F air pulled across it...
And that pipe is not insulated by the mfg.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40 (Retired)
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
HVAC Certification EPA Cert#2046620
BPI# 5015804
Reply With Quote
  #24  
Old 4/30/16, 10:00 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
Certified Professional Inspector (CPI)
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 10,623
Default Re: Inuslation on suction line

Quote:
Originally Posted by dandersen View Post
No insulation on the suction line is one thing, but 2' between the house and unit is not a concern to me in air conditioning.

If you compare the 4' inside the condenser with high speed 130F air pulled across it...
And that pipe is not insulated by the mfg.
Come on Dave you know there is not 4 feet of suction line inside that unit and the two feet between the wall and the unit is no big deal unless its on the west side of the home besides it makes the job look like a amateur install.



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
55 years in the Trades
Okla State License # 130
580-268-3340
Reply With Quote
  #25  
Old 4/30/16, 3:10 PM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Retired Member
 
Join Date: Jun 2005
Location: Nashville, TN
Posts: 10,540
Default Re: Inuslation on suction line

I agree, but there is a perception and bad reporting that this missing insulation has a significant impact on equipment performance. And it does not.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40 (Retired)
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
HVAC Certification EPA Cert#2046620
BPI# 5015804
Reply With Quote
  #26  
Old 4/30/16, 10:23 PM
Dan Bowers, CMI, ACI's Avatar
Dan Bowers, CMI, ACI Dan Bowers, CMI, ACI is online now
Certified Master Inspector
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 10,079
Default Re: Inuslation on suction line

As David said not a significant consideration outside as it was described, but as Charley said we report it ... without making a stink over it..



Dan Bowers, CMI
Licensed Contractor / Builder
Certified IAQ2 Mold Inspector
Licensed HVAC Service Technician
EDI Certified Stucco / EIFS Inspector
Certified Commercial Building Inspector
iNACHI – US Member of the Year 2010
ITC / FLIR - Level I Infrared Thermographer
FHA - 203k Inspector / Compliance Inspector
ICC Code Inspector (Plmbg, Elec, Mech, Bldg)

Last edited by dbowers; 5/1/16 at 1:36 PM..
Reply With Quote
  #27  
Old 5/3/16, 10:12 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 17,179
Default Re: Inuslation on suction line

It's probably less then ten bucks to fix. It is also noted on the Termite report.
Reply With Quote
  #28  
Old 6/10/18, 10:11 PM
Rodney Whitehouse, RBI-1223 Rodney Whitehouse, RBI-1223 is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Nov 2003
Location: Summerville, SC
Posts: 17
Default Re: Inuslation on suction line

https://www.bobvila.com/articles/rep...n-maximize-ac/
Reply With Quote
Need a home inspection in Alabama? Check out InterNACHI's listing of Alabama certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #29  
Old 6/11/18, 2:32 PM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Retired Member
 
Join Date: Jun 2005
Location: Nashville, TN
Posts: 10,540
Default Re: Inuslation on suction line

Quote:
Originally Posted by rwhitehouse View Post

No, that is BS!



The only part of the refrigerant line that is insulated is the suction line. The suction line is downstream of the evaporator (which does the cooling). "Superheat" that occurs in the suction line is after that cooling coil and has no effect on the evaporator to cool.



Measure the temperature at the coil and then at the condensing unit. This temperature rise does not effect the operating temp of the evap coil.



The only thing it could do is to lower the maximum design operating temperature (the outdoor temperature when your HVAC unit runs at 100% capacity. Generally 95 - 98 F),, but no where near 10 degrees. even at the reduced capacity, you will never notice it because the sensible heat ratio changes and lowers the latent heat and keeps you cool due to increased evaporative cooling.



They are not talking insulated vs. not insulated. They want you to remove and replace the insulation to save money. You can't save money when your savings takes 23 years to recover and the unit won't last that long...



This is the psychosomatic comfort perception I have talked about.



Quote:
The result: it not only looks better, but both air conditioning units seem to be running less often and cooling more quickly! In the future, you can be sure that we’re adding “inspect pipe insulation” to our annual to-do list for air conditioning maintenance.

"Seems to be..." is not a measured condition. It's a perception in your mind without basis. "I feel better because I think I did something..."



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40 (Retired)
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
HVAC Certification EPA Cert#2046620
BPI# 5015804
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing, Ethics & Legal Issues for Inspectors 52 7/11/17 4:34 PM
AC suction line kgrabowski Inspecting HVAC Systems 8 8/27/09 11:54 PM
Suction line bend lprinzi Inspecting HVAC Systems 6 2/7/09 2:57 PM
Sweating Suction Line mbirenbaum Inspecting HVAC Systems 2 9/1/08 11:20 PM

All times are GMT -4. The time now is 5:10 PM.
no new posts