Default Protruding Pipes From Ground

Anyone knows the purpose of those pipes?

1970 built bungalow, Crane gas boiler (owner said its original), pipes are situated close to boiler area. Owner refused to fill out the vendor's declaration.

My thought is an UST...
Attached Thumbnails
protruding-pipes-ground-img_0040.jpg   protruding-pipes-ground-img_0041.jpg  



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
Need a home inspection in Iowa? Check out InterNACHI's listing of Iowa certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/15/10, 6:01 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 29,027
Default Re: Protruding Pipes From Ground

Underground oil tank??



CMI 2004-2017 Retired

Awards Committee Member
Inachi Award Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #3  
Old 2/15/10, 6:07 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
Certified Professional Inspector (CPI)
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 7,274
Default Re: Protruding Pipes From Ground

Old fuel oil fill and vent lines?...wouldn't Jive with original gas boiler though....did it look original....as in 40 years old?



Jim McKee
Amherst, Ohio
440 225 8688
www.amhersthomeinspector.com
Reply With Quote
  #4  
Old 2/15/10, 6:12 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 29,027
Default Re: Protruding Pipes From Ground

Underground propane tank?
Seems to say 250 psi on the cap.?
Where did the pipe go to on the inside?



CMI 2004-2017 Retired

Awards Committee Member
Inachi Award Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #5  
Old 2/15/10, 6:20 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2007
Location: Minnesota & Northern Iowa
Posts: 29,228
Default Re: Protruding Pipes From Ground

I agree with others. Looks like a (buried ?) fuel oil tank filler pipe and vent. My guess would be the boiler was converted to gas burning. That would explain the sellers refusal to disclose. Trying to get off the hook for removal $$$.





Jeffrey R. Jonas
Owatonna, Minnesota



"I am not a teacher, but an awakener."
- Robert Frost, American poet (1874-1963).



Last edited by jjonas; 2/15/10 at 6:26 PM..
Reply With Quote
  #6  
Old 2/15/10, 6:24 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 29,027
Default Re: Protruding Pipes From Ground

JJ, removing oil tanks are not cheap, so that would be a good reason for non-disclosure as you say.



CMI 2004-2017 Retired

Awards Committee Member
Inachi Award Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #7  
Old 2/15/10, 6:27 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2007
Location: Minnesota & Northern Iowa
Posts: 29,228
Default Re: Protruding Pipes From Ground

Quote:
Originally Posted by mcyr View Post
JJ, removing oil tanks are not cheap, so that would be a good reason for non-disclosure as you say.
Exactly... why else would the seller refuse to disclose? Hoping no-one would catch it before the sale.



Jeffrey R. Jonas
Owatonna, Minnesota



"I am not a teacher, but an awakener."
- Robert Frost, American poet (1874-1963).


Reply With Quote
  #8  
Old 2/15/10, 6:30 PM
Wayne B. Wilson, TN 439's Avatar
Wayne B. Wilson, TN 439 Wayne B. Wilson, TN 439 is online now
Certified Professional Inspector (CPI)
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 18,509
Default Re: Protruding Pipes From Ground

Looks like a oil under ground tank, Was the boilr a gun type burner? may have been converted to gas back in the day
Reply With Quote
  #9  
Old 2/15/10, 7:19 PM
Marcel Gratton, CMI's Avatar
Marcel Gratton, CMI Marcel Gratton, CMI is offline
Certified Master Inspector ®
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 4,167
Default Re: Protruding Pipes From Ground

Quote:
Originally Posted by jmckee View Post
Old fuel oil fill and vent lines?...wouldn't Jive with original gas boiler though....did it look original....as in 40 years old?
The boiler didn't look 40 years old; it was a Crane which went out of business according to CDW Technical Reference Guide.

The fact that the vendor didn't want to fill out the vendor's declaration form, which incidentally had a question about UST, I will play safe and assume that a UST may be present and recommend further investigation prior to purchase to my client.



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #10  
Old 2/15/10, 7:23 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 29,027
Default Re: Protruding Pipes From Ground

I am lousy at acronyms, what is UST?



CMI 2004-2017 Retired

Awards Committee Member
Inachi Award Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #11  
Old 2/15/10, 7:24 PM
Marcel Gratton, CMI's Avatar
Marcel Gratton, CMI Marcel Gratton, CMI is offline
Certified Master Inspector ®
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 4,167
Default Re: Protruding Pipes From Ground

Thanks everyone for your prompt responses!

I will report these pipes as being from a suspected (UST) underground storage tank.

Regards,



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #12  
Old 2/15/10, 7:51 PM
Claude Lawrenson's Avatar
Claude Lawrenson Claude Lawrenson is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Dec 2003
Location: Tecumseh-Windsor, ON
Posts: 3,044
Send a message via Skype™ to clawrenson
Default Re: Protruding Pipes From Ground

TSSA - Standards
http://www.tssa.org/public/consumer/...umerHome04.asp

http://www.tssa.org/regulated/fuels/...p?loc3=fueloil



Cheers, Claude Lawrenson NACHI03121515
Inspection Support Services Inc.
"Those who can do. Those who CARE teach" and truly understand What do teachers make ?
Reply With Quote
  #13  
Old 2/15/10, 8:07 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 29,027
Default Re: Protruding Pipes From Ground

How to remove an underground oil tank.

First, you pump the oil out of it that people use to burn in their furnace, people around that do that.
Then, you dig it up and put it on the lawn.



Then you cut it in half.
Then you clean it and send it off to the incinerator.


Then the scrap yard takes the rest.




CMI 2004-2017 Retired

Awards Committee Member
Inachi Award Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
Need a home inspection in Iowa? Check out InterNACHI's listing of Iowa certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 2/15/10, 8:26 PM
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 5,103
Default Re: Protruding Pipes From Ground

Soil testing for signs of any old leakage? Didn't hear that mentioned. If the soil is contaminated it can get real expensive real fast.





Reply With Quote
  #15  
Old 2/15/10, 8:33 PM
Marcel Gratton, CMI's Avatar
Marcel Gratton, CMI Marcel Gratton, CMI is offline
Certified Master Inspector ®
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 4,167
Default Re: Protruding Pipes From Ground

Good info Claude, but it don't apply in Québec.

I will keep it though for when I cross the border to Ontario...

Regards,



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Hey Electricians... Can you help by proofing this new course? gromicko Electrical Inspections 69 10/15/08 6:14 AM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 11:39 AM

All times are GMT -4. The time now is 2:52 AM.
no new posts