Default Range hood vent pipe material

This vent pipe is connected directly to the exterior of the building. Is the pipe material okay, or should it be smooth wall galvanized steel, stainless steel, or copper? The NFPA recommends this type of material over open topped broiler in residential applications. Does a stove fall under the category of open topped broiler?
Attached Thumbnails
Range hood vent pipe material-img_5305-jpg   Range hood vent pipe material-img_5304-jpg  
Reply With Quote
Need a home inspection in Louisiana? Check out InterNACHI's listing of Louisiana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/29/11, 8:49 AM
KEVIN WOOD, CMI KEVIN WOOD, CMI is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,820
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Range hood vent pipe material

The coil needs to be stretched according to proper practice of the flex hose. I would mention this and explain why there is a problem with the installation.

Last edited by kwood; 12/29/11 at 1:15 PM..
Reply With Quote
  #3  
Old 12/29/11, 9:28 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2004
Location: this side of Texas dirt, another successful day
Posts: 4,537
Default Re: Range hood vent pipe material

Quote:
Originally Posted by kwood View Post
The coil needs to be strecthed according to proper practice. I would mention this and explain why there is a problem with the installation.
the problem is the duct material is not allowed with either exhaust system no matter how far you stretch it or how neatly it's installed

SECTION M1503
RANGE HOODS
M1503.1 General. Range hoods shall discharge to the outdoors
through a single-wall duct. The duct serving the hood
shall have a smooth interior surface, shall be air tight and shall
be equipped with a backdraft damper. Ducts serving range
hoods shall not terminate in an attic or crawl space or areas
inside the building.
Exception: Where installed in accordance with the manufacturer's
installation instructions, and where mechanical or
natural ventilation is otherwise provided, listed and labeled
ductless range hoods shall not be required to discharge to
the outdoors.
M1503.2 Duct material. Single-wall ducts serving range
hoods shall be constructed of galvanized steel, stainless steel or
copper.
Exception: Ducts for domestic kitchen cooking appliances
equipped with down-draft exhaust systems shall be permitted
to be constructed of schedule 40 PVC pipe provided that
the installation complies with all of the following:
1. The duct shall be installed under a concrete slab
poured on grade; and
2. The underfloor trench in which the duct is installed
shall be completely backfilled with sand or gravel; and
3. The PVC duct shall extend not more than 1 inch (25
mm) above the indoor concrete floor surface; and
4. The PVC duct shall extend not more than 1 inch (25
mm) above grade outside of the building; and
5. The PVC ducts shall be solvent cemented.
M1503.3 Kitchen exhaust rates. Where domestic kitchen
cooking appliances are equipped with ducted range hoods or
down-draft exhaust systems, the fans shall be sized in accordance
with Section MI507.3.
SECTION M1504
INSTALLATION OF MICROWAVE OVENS
M1504.1 Installation of microwave oven over a cooking
appliance. The installation of a listed and labeled cooking
335
EXHAUST SYSTEMS
appliance or microwave oven over a listed and labeled cooking
appliance shall conform to the terms of the upper appliance's
listing and label and the manufacturer's installation instructions.
The microwave oven shall conform to UL 923.
SECTION M1505
OVERHEAD EXHAUST HOODS
M1505.1 General. Domestic open-top broiler units shall be
provided with a metal exhaust hood, not less than 28 gage, with
1/4 inch (6 mm) between the hood and the underside of combustible
material or cabinets. A clearance of at least 24 inches (610
mm) shall be maintained between the cooking surface and the
combustible material or cabinet. The hood shall be at least as
wide as the broiler unit and shall extend over the entire unit.
Such exhaust hood shall discharge to the outdoors and shall be
equipped with a backdraft damper or other means to control
infiltrationlexfiltration when not in operation. Broiler units
incorporating an integral exhaust system, and listed and
labeled for use without an exhaust hood, need not be provided
with an exhaust hood.
SECTION M1506
EXHAUST DUCTS
M1506.1 Ducts. Where exhaust duct construction is not specified
in this chapter, such construction shall comply with Chapter
16.



badair

ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS/Stucco-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

National Association of Commercial Building Inspectors & Thermographers™ Member ID 12011-14TX

life is the random lottery of events followed by numerous narrow escapes...accept the good


Father Sky
Mother Earth
Children of the Universe
Forever Free
Always at Peace
Reply With Quote
  #4  
Old 12/29/11, 9:40 AM
John Gromkoski's Avatar
John Gromkoski John Gromkoski is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 1,083
Please Note: jgromkoski is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Range hood vent pipe material

Barry, what code is it that you are referencing?
Reply With Quote
  #5  
Old 12/29/11, 9:52 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
Certified Master Inspector
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 10,926
Send a message via Yahoo to jfunderburk
Default Re: Range hood vent pipe material

Quote:
Originally Posted by jgromkoski View Post
Barry, what code is it that you are referencing?
International Mechanical Code



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
T. Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Award Winner 2018, 2017, 2016, 2015, 2014, 2013, 2012, 2011, 2010.
Ph: 704-351-1776
www.aohomeinspection.com

Reply With Quote
  #6  
Old 12/29/11, 9:52 AM
KEVIN WOOD, CMI KEVIN WOOD, CMI is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,820
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Range hood vent pipe material

John it does not matter what code it is we can only recommend what was OK at the time. I do not agree to leave it like this and once you mention it needs to be stretched we hope that the person they call will correct it properly. We can say it would be best if it was solid metal according to proper practice today. M1506.1 Ducts. Where exhaust duct construction is not specified
in this chapter, such construction shall comply with Chapter
16. This is from the IRC 2006 also.

Last edited by kwood; 12/29/11 at 9:56 AM..
Reply With Quote
  #7  
Old 12/29/11, 9:59 AM
John Gromkoski's Avatar
John Gromkoski John Gromkoski is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 1,083
Please Note: jgromkoski is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Range hood vent pipe material

I reported it does not meet current standards and may not be as safe as current standard material and installation practice. Thanks for the help.
Reply With Quote
  #8  
Old 12/29/11, 10:01 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2004
Location: this side of Texas dirt, another successful day
Posts: 4,537
Default Re: Range hood vent pipe material

2012 irc it's basically the same in all previous versions

corrugated or accordion style is not smooth wall, "gunk" (inspectorspeak) will build up on the ridges/irregularities and become a combustion-fire hazard, therefore not allowed for this application



badair

ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS/Stucco-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

National Association of Commercial Building Inspectors & Thermographers™ Member ID 12011-14TX

life is the random lottery of events followed by numerous narrow escapes...accept the good


Father Sky
Mother Earth
Children of the Universe
Forever Free
Always at Peace
Reply With Quote
  #9  
Old 12/29/11, 10:08 AM
KEVIN WOOD, CMI KEVIN WOOD, CMI is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,820
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Range hood vent pipe material

I should also mention that a manufacturer is making flex duct fire proof!
That being said Yes I would agree with the grease problem as Barry is pointed out.

Last edited by kwood; 12/29/11 at 10:33 AM..
Reply With Quote
  #10  
Old 12/29/11, 10:09 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2004
Location: this side of Texas dirt, another successful day
Posts: 4,537
Default Re: Range hood vent pipe material

Quote:
Originally Posted by kwood View Post
John it does not matter what code it is we can only recommend what was OK at the time. I do not agree to leave it like this and once you mention it needs to be stretched we hope that the person they call will correct it properly. We can say it would be best if it was solid metal according to proper practice today. M1506.1 Ducts. Where exhaust duct construction is not specified
in this chapter, such construction shall comply with Chapter
16. This is from the IRC 2006 also.
where is it allowed in 16

i'm not saying the code has to be quoted in a report but knowing what is not allowed is an automatic noted deficiency that requires removal and replacement with proper materials

any less is just another logo certified soft report



badair

ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS/Stucco-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

National Association of Commercial Building Inspectors & Thermographers™ Member ID 12011-14TX

life is the random lottery of events followed by numerous narrow escapes...accept the good


Father Sky
Mother Earth
Children of the Universe
Forever Free
Always at Peace
Reply With Quote
  #11  
Old 12/29/11, 10:29 AM
James F. McKee's Avatar
James F. McKee James F. McKee is online now
Certified Professional Inspector (CPI)
 
Join Date: Feb 2007
Location: Lorain Ohio
Posts: 7,369
Default Re: Range hood vent pipe material

looks like the jiffy pop exploded....



Jim McKee
Lorain, Ohio
440 225 8688
www.classicinspector.com
Reply With Quote
  #12  
Old 12/29/11, 10:29 AM
KEVIN WOOD, CMI KEVIN WOOD, CMI is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,820
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Range hood vent pipe material

I was referring to the design of the duct in question. It is designed to be stretched in the manufactured installation guidelines. I was not saying that this is acceptable.
M1503.1 General.
The AHJ may allow it and this is sad but that is why we are in this business. This could be an outside wall side exhaust hood that presents no danger.
Reply With Quote
  #13  
Old 12/29/11, 11:49 AM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 75,030
Default Re: Range hood vent pipe material

Quote:
Originally Posted by kwood View Post
I was referring to the design of the duct in question. It is designed to be stretched in the manufactured installation guidelines. I was not saying that this is acceptable.
M1503.1 General.
The AHJ may allow it and this is sad but that is why we are in this business. This could be an outside wall side exhaust hood that presents no danger.
I disagree.

Slinkys are a grease trap.

The client needs to be made aware of the potential hazard and that they can not be cleaned.

My non CMI opinion of course.



As a Professional Home Inspector, I support the privacy of my clients.

You own your private information. I won't sell or give away yours, others do


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
Need a home inspection in Louisiana? Check out InterNACHI's listing of Louisiana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/29/11, 12:18 PM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Retired Member
 
Join Date: Jun 2005
Location: Nashville, TN
Posts: 10,595
Default Re: Range hood vent pipe material

Quote:
This could be an outside wall side exhaust hood that presents no danger.
That makes about as much sense to me as the need to "stretch it out more"...

But then I'm not a CMI either!

Look at what I've been missing all these years!?

You have to have 26ga metal duct go through the garage wall to your HVAC equipment, but "foil" duct is OK directly above the stove...



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40 (Retired)
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
HVAC Certification EPA Cert#2046620
BPI# 5015804
Reply With Quote
  #15  
Old 12/29/11, 12:31 PM
KEVIN WOOD, CMI KEVIN WOOD, CMI is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,820
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Range hood vent pipe material

I did not say it was OK!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help - Polybutylene Pipes Rick G Plumbing Inspections 45 6/26/13 5:21 PM
Pellet stove help chellickson General Inspection Discussion 23 8/19/10 2:23 AM
Outside Hot Water Heater With Vent Pipe Outside Kitchen Window bwilliams Plumbing Inspections 4 12/9/08 12:10 AM
Direct vent WH with draft hood dpeterson Plumbing Inspections 9 12/30/06 4:35 PM
Asbestos Vent Pipe??? psmothers Plumbing Inspections 17 5/22/06 3:14 AM

All times are GMT -4. The time now is 11:44 PM.
no new posts