Here is a question I've always wanted more information on from you HVAC gurus.

When you find an AC unit installed with an extra coil of refrigerant line, why does the coil need to be horizontal? Is it just to help oil find its way back to the condenser/compressor? And is there any amount of extra coil which would be considered too much?
Attached Thumbnails
Refrigerant line coil-image-jpg  



Cameron Anderson
Integrity Home Inspection
Truth. In Real Estate.
Since 2004
Bachelor of Architecture, U of I, Urbana IL
Illinois Licensed Inspector

www.homeinspectionpeoria.com
Reply With Quote
Need a home inspection in Ohio? Check out InterNACHI's listing of Ohio certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/21/13, 12:08 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
Certified Professional Inspector (CPI)
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 10,712
Default Re: Refrigerant line coil

Quote:
Originally Posted by canderson5 View Post
Here is a question I've always wanted more information on from you HVAC gurus.

When you find an AC unit installed with an extra coil of refrigerant line, why does the coil need to be horizontal? Is it just to help oil find its way back to the condenser/compressor? And is there any amount of extra coil which would be considered too much?
That is a improper oil trap created in that suction line and the bigger the trap the more oil is prevented from returning to the compressor. That is not the kind of trap you want big or little.

There is a exceptable type P-trap installed in a suction line but it is placed in the line just as it exits the A-coil box and it is used when the condensing unit is installed above the A-coil such as the A-coil in a basement and the condenser at ground level a good distance between the two



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
55 years in the Trades
Okla State License # 130
580-268-3340
Reply With Quote
  #3  
Old 2/21/13, 12:28 AM
Cameron Anderson's Avatar
Cameron Anderson Cameron Anderson is offline
Certified Professional Inspector (CPI)
 
Join Date: Nov 2011
Location: Peoria, IL
Posts: 6,989
Default Re: Refrigerant line coil

So this coil of refrig line is being used as an oil trap? Does it make any difference what the distance is? Because the A coil is just to the right in the photo and the condenser is just outside the foundation wall to the left. Probably about a five foot distance between the two.



Cameron Anderson
Integrity Home Inspection
Truth. In Real Estate.
Since 2004
Bachelor of Architecture, U of I, Urbana IL
Illinois Licensed Inspector

www.homeinspectionpeoria.com
Reply With Quote
  #4  
Old 2/21/13, 12:38 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
Certified Professional Inspector (CPI)
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 10,712
Default Re: Refrigerant line coil

Quote:
Originally Posted by canderson5 View Post
So this coil of refrig line is being used as an oil trap? Does it make any difference what the distance is? Because the A coil is just to the right in the photo and the condenser is just outside the foundation wall to the left. Probably about a five foot distance between the two.
No difference on the distance as long as the A-coil is the same level or higher such as a attic install. The lines were probally a pre-charged line set and they did not stretch them out as they should have.



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
55 years in the Trades
Okla State License # 130
580-268-3340
Reply With Quote
  #5  
Old 2/21/13, 12:46 AM
Cameron Anderson's Avatar
Cameron Anderson Cameron Anderson is offline
Certified Professional Inspector (CPI)
 
Join Date: Nov 2011
Location: Peoria, IL
Posts: 6,989
Default Re: Refrigerant line coil

So is this always a defect when there is an extra coil? I don't see it often but I've never read about it being a defect.



Cameron Anderson
Integrity Home Inspection
Truth. In Real Estate.
Since 2004
Bachelor of Architecture, U of I, Urbana IL
Illinois Licensed Inspector

www.homeinspectionpeoria.com
Reply With Quote
  #6  
Old 2/21/13, 10:15 PM
Chad Norlen, CPI's Avatar
Chad Norlen, CPI Chad Norlen, CPI is offline
InterNACHI Member
 
Join Date: Nov 2011
Location: American Falls, ID
Posts: 351
Default Re: Refrigerant line coil

There are drawbacks to pre-fab linesets - they are just a convenience for the installer.



Chad Norlen

HVAC Journeyman - State of Idaho
EPA Certified Universal Technician
Reply With Quote
  #7  
Old 2/21/13, 10:29 PM
Cameron Anderson's Avatar
Cameron Anderson Cameron Anderson is offline
Certified Professional Inspector (CPI)
 
Join Date: Nov 2011
Location: Peoria, IL
Posts: 6,989
Default Re: Refrigerant line coil

Quote:
Originally Posted by cnorlen View Post
There are drawbacks to pre-fab linesets - they are just a convenience for the installer.
Thanks for the info guys. Good stuff.



Cameron Anderson
Integrity Home Inspection
Truth. In Real Estate.
Since 2004
Bachelor of Architecture, U of I, Urbana IL
Illinois Licensed Inspector

www.homeinspectionpeoria.com
Reply With Quote
  #8  
Old 2/22/13, 10:10 AM
Bryce W. Jeffrey, CMI's Avatar
Bryce W. Jeffrey, CMI Bryce W. Jeffrey, CMI is offline
Certified Master Inspector ®
 
Join Date: Mar 2007
Location: St. Thomas, On
Posts: 696
Default Re: Refrigerant line coil

Thank You. That is very interesting information.
Reply With Quote
  #9  
Old 2/22/13, 10:25 AM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Retired Member
 
Join Date: Jun 2005
Location: Nashville, TN
Posts: 10,595
Default Re: Refrigerant line coil

This line set is placed in a horizontal position so it "will not" create an oil trap.

Just in case someone thinks this is a defect, it is not. It is installed in accordance with equipment manufacturer's instructions.

HVAC systems should be designed to use the least quantity of refrigerant as possible otherwise problems arise. These pre-charge line sets increase the volume of the refrigerant needed for operation and can be problematic.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40 (Retired)
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
HVAC Certification EPA Cert#2046620
BPI# 5015804
Reply With Quote
  #10  
Old 2/22/13, 11:14 AM
Cameron Anderson's Avatar
Cameron Anderson Cameron Anderson is offline
Certified Professional Inspector (CPI)
 
Join Date: Nov 2011
Location: Peoria, IL
Posts: 6,989
Default Re: Refrigerant line coil

If the extra coil was vertical then it would trap oil and be considered a defect?

But either way, the extra coil is not the best installation and can lead to problems.


Are those correct?



Cameron Anderson
Integrity Home Inspection
Truth. In Real Estate.
Since 2004
Bachelor of Architecture, U of I, Urbana IL
Illinois Licensed Inspector

www.homeinspectionpeoria.com
Reply With Quote
  #11  
Old 2/22/13, 1:47 PM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Retired Member
 
Join Date: Jun 2005
Location: Nashville, TN
Posts: 10,595
Default Re: Refrigerant line coil

Cameron, if the extra coil is vertical it would be very problematic when refrigeration velocity fell during low load conditions.

Quote:
But either way, the extra coil is not the best installation and can lead to problems.
This is not a cut and dry, right or wrong.
The article posted indicate some of the reasons that they may not be desirable but it can also be noteworthy that commercial ice machines are designed with a specific line set if they use a remote condenser and if you modify it, you screw it up!

The article is basing its opinion upon installers that don't use certified HVAC technicians to start up the equipment once it's installed. These line sets are sealed and you simply bolt them onto the indoor and outdoor unit (breaking the seal). This eliminates having to evacuate the line set with a vacuum pump, eliminates potential water and air contamination, etc. but in any case in HVAC technician should evaluate the startup to ensure proper installation and charge.

As Charley pointed out, there's a lot of different ways you can install an HVAC split system. If you have the condensing unit on the roof and it's too high, you have to modify the piping design to ensure proper velocity to lift the oil back up to the compressor. If a startup technician isn't available to do this job, you don't have a clue what you just installed.

Any dip across the crawlspace of the refrigeration line causes a potential oil trap. It is noteworthy to put in your report but is not necessary to listed as a defect unless you know for a fact it is. And there's no way to tell the oil level in a compressor without cutting it off and dumping the oil out.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40 (Retired)
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
HVAC Certification EPA Cert#2046620
BPI# 5015804
Reply With Quote
  #12  
Old 2/22/13, 2:21 PM
Cameron Anderson's Avatar
Cameron Anderson Cameron Anderson is offline
Certified Professional Inspector (CPI)
 
Join Date: Nov 2011
Location: Peoria, IL
Posts: 6,989
Default Re: Refrigerant line coil

Thanks David, that's really good information to know.



Cameron Anderson
Integrity Home Inspection
Truth. In Real Estate.
Since 2004
Bachelor of Architecture, U of I, Urbana IL
Illinois Licensed Inspector

www.homeinspectionpeoria.com
Reply With Quote
  #13  
Old 2/22/13, 5:04 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
Certified Professional Inspector (CPI)
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 10,712
Default Re: Refrigerant line coil

Quote:
Originally Posted by dandersen View Post
This line set is placed in a horizontal position so it "will not" create an oil trap.

Just in case someone thinks this is a defect, it is not. It is installed in accordance with equipment manufacturer's instructions.

HVAC systems should be designed to use the least quantity of refrigerant as possible otherwise problems arise. These pre-charge line sets increase the volume of the refrigerant needed for operation and can be problematic.
That pic is strange as the loops in that line set do appear to be verticle not horizional the pic appears to be looking down into a cavity I must be getting old



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
55 years in the Trades
Okla State License # 130
580-268-3340
Reply With Quote
Need a home inspection in Ohio? Check out InterNACHI's listing of Ohio certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 2/22/13, 6:12 PM
Cameron Anderson's Avatar
Cameron Anderson Cameron Anderson is offline
Certified Professional Inspector (CPI)
 
Join Date: Nov 2011
Location: Peoria, IL
Posts: 6,989
Default Re: Refrigerant line coil

Quote:
Originally Posted by cbottger View Post
That pic is strange as the loops in that line set do appear to be verticle not horizional the pic appears to be looking down into a cavity I must be getting old
I squatted down a little to get the shot. The coil was hanging just below a duct at the ceiling.



Cameron Anderson
Integrity Home Inspection
Truth. In Real Estate.
Since 2004
Bachelor of Architecture, U of I, Urbana IL
Illinois Licensed Inspector

www.homeinspectionpeoria.com
Reply With Quote
  #15  
Old 2/22/13, 6:52 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
Certified Professional Inspector (CPI)
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 10,712
Default Re: Refrigerant line coil

Quote:
Originally Posted by canderson5 View Post
I squatted down a little to get the shot. The coil was hanging just below a duct at the ceiling.
Ok but was the coils in the line set vertical or horizontal



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
55 years in the Trades
Okla State License # 130
580-268-3340
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Slope of waste drain line. mlong Plumbing Inspections 7 12/12/16 3:25 PM
Poor line sizing? sfogarty Inspecting HVAC Systems 11 1/26/11 9:38 PM
Water heater line bmoree Plumbing Inspections 7 1/21/11 5:28 PM
Can sellers lie about a broken sewer line? gromicko Legislation, Licensing, Ethics & Legal Issues for Inspectors 1 7/15/08 12:18 PM

All times are GMT -4. The time now is 4:21 PM.
no new posts