Default Supply vs. Return Register Placement

New construction in Houston area with conditioned attic space. The attached picture shows the close proximity of the return air duct to one of the supply ducts in the master bedroom (spacing is about 24 inches and they are both somewhat tucked into a corner). Both my client and I think they are too close, but the builder is resisting.

I'm looking for an authoritative source / citation that addresses minimum required separation and what the minimum is. I suspect that it's in the ACCA Manual D, but I don't have it. Any help is appreciated.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
TheWoodlandsHomeInspection.com


Houston, TX
_______________________
Awards Committee Member

SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.

Last edited by cevans; 2/7/14 at 9:23 PM..
Reply With Quote
Need a home inspection in Michigan? Check out InterNACHI's listing of Michigan certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/25/10, 5:33 PM
Larry Kage, CMI Larry Kage, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: NW, MI
Posts: 16,055
Default Re: Supply vs. Return Register Placement

Crank the heat way up and break out you IR imager...




Awards Committee Member
SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
____________________________________________

Larry Kage, CMI 2004-2017
State Licensed Builder since 1973
InterNACHI Lifetime Member
~retired~

The above post represents my personal opinion.
Reply With Quote
  #3  
Old 2/25/10, 7:03 PM
James F. McKee's Avatar
James F. McKee James F. McKee is online now
Certified Professional Inspector (CPI)
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 7,274
Default Re: Supply vs. Return Register Placement

Quote:
Originally Posted by lkage View Post
Crank the heat way up and break out you IR imager...

that should do it....



Jim McKee
Amherst, Ohio
440 225 8688
www.amhersthomeinspector.com
Reply With Quote
  #4  
Old 2/25/10, 8:07 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
Certified Professional Inspector (CPI)
 
Join Date: Aug 2006
Location: Chicago
Posts: 37,398
Default Re: Supply vs. Return Register Placement

I do have a file somewhere as this issue came up for me last year.
Till then ,I am pretty sure it is wrong.
Will post when found.
Reply With Quote
  #5  
Old 2/25/10, 8:58 PM
mklein's Avatar
mklein mklein is offline
InterNACHI Member
 
Join Date: Dec 2009
Posts: 91
Default Re: Supply vs. Return Register Placement

From what I can see, the louvers on the diffuser are aimed away from the return grille. In which case, the supply air should be blown away from the return. In fact, blowing air away from the return could enhance the air flow toward the return.

In general, though, all diffusers have throws that are vary with supply air flow. The throw is the distance the air will flow before reaching a terminal velocity of 50 fpm. In designing supply air systems, the goal is not to have the return air opening toward the outer edge of the throw. That means that the supply air diffuser is usually placed as far away from the return as possible. That being said, one manufacturer used to make a supply air diffuser that had the return in the middle of the diffuser. The theory was that the movement of the supply air helped pull air toward the return air opening. I believe it didn't succeed because of the logistics of installing the diffusers.

I will also add that no matter how return air diffusers are designed, they usually do not work as designed. The only ones that have a chance of working right are ducted ones. Even then, most of these systems are not balanced, and return air systems need to be balanced just as supply air systems do.



Matthew Klein, P.E., M.B.A.

Criterium Engineers

PO Box 181503
Cincinnati, OH 45018-1503
Phone: 513-474-9600
FAX: 888-747-0427
E-mail: Criterium-Cincinnati@fuse.net
Website: www.Criterium-Cincinnati.com
Reply With Quote
  #6  
Old 2/25/10, 9:59 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,587
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Supply vs. Return Register Placement

Quote:
Originally Posted by cevans View Post
New construction in Houston area with conditioned attic space. The attached picture shows the close proximity of the return air duct to one of the supply ducts in the master bedroom (spacing is about 24 inches and they are both somewhat tucked into a corner). Both my client and I think they are too close, but the builder is resisting.

I'm looking for an authoritative source / citation that addresses minimum required separation and what the minimum is. I suspect that it's in the ACCA Manual D, but I don't have it. Any help is appreciated.

SHEESH!!!! All that is needed is common sense!! Try the analogy of a short circuit in an electrical circuit. The power isn't getting where it needs to be.

In this case, the conditioned air is not getting where it needs to be.......it's being short-circuited back to the return. Try using a bit of smoke from a smoke pencil when the system is running.
Reply With Quote
  #7  
Old 2/25/10, 10:57 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
Retired Member
 
Join Date: Jul 2004
Location: Boerne, TX
Posts: 4,898
Default Re: Supply vs. Return Register Placement

Chuck, are you sure that return air grill is ducted to the AHU? It might just be a transfer or jumper duct to a nearby hallway to help equalize pressure and allow a path for air to get back to a hall and eventually a return when the door is closed to that room. If so, then I wouldn't think the location shown would be an issue. If it is ducted to the AHU then take a look at this document.

2004_09TechTalk_ReturnGrillLocations.pdf
Reply With Quote
  #8  
Old 2/25/10, 11:16 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Jul 2008
Location: My house
Posts: 9,833
Default Re: Supply vs. Return Register Placement

thanks michael for the input...
Reply With Quote
  #9  
Old 2/26/10, 2:54 AM
Chuck Evans, TREC 7657's Avatar
Chuck Evans, TREC 7657 Chuck Evans, TREC 7657 is offline
Certified Master Inspector ®
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 8,138
Default Re: Supply vs. Return Register Placement

Quote:
Originally Posted by mboyett View Post
Chuck, are you sure that return air grill is ducted to the AHU? It might just be a transfer or jumper duct to a nearby hallway to help equalize pressure and allow a path for air to get back to a hall and eventually a return when the door is closed to that room. If so, then I wouldn't think the location shown would be an issue. If it is ducted to the AHU then take a look at this document.

Attachment 35241
Thanks Michael. Yes it is an actual return that is ducted back to the return plenum. Not a jumper or transfer duct.

BTW: I did come across this document which is an interesting resource http://www.energy.ca.gov/efficiency/...rocedures.html

I guess one thing that could be done to test the affect that the proximity of the supply to the return may be to place a temp probe in the suspect return duct and another in a non-suspect return duct with the system operating and compare the temperatures to see if the suspect return air temperature is being significantly influenced by the supply (i.e., when the heat is running is the return air temperature inside this duct higher than other return ducts). YES - I know that this goes beyond the normal scope of a home inspection.

Thought I would share another "interesting" duct location from this house. Note the location of the fresh air intake duct in this picture (yes they used an exhaust duct and placed silicone caulk in the louver pivots to hold the louvers open). The intake is placed directly above the hot discharge of the condensing unit (remember this is southeast Texas).



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
TheWoodlandsHomeInspection.com


Houston, TX
_______________________
Awards Committee Member

SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.

Last edited by cevans; 2/7/14 at 9:23 PM..
Reply With Quote
  #10  
Old 2/26/10, 6:55 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,587
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Supply vs. Return Register Placement

Quote:
Originally Posted by mboyett View Post
Chuck, are you sure that return air grill is ducted to the AHU? It might just be a transfer or jumper duct to a nearby hallway to help equalize pressure and allow a path for air to get back to a hall and eventually a return when the door is closed to that room. If so, then I wouldn't think the location shown would be an issue. If it is ducted to the AHU then take a look at this document.

Attachment 35241
Are there other supply grilles in the room?

If not..........These two grilles are tucked into a small remote corner. There is no way any amount of the supply air, especially if heated, will make it out into the room. IT'S BAD DESIGN.......plain and simple!!!!
Reply With Quote
  #11  
Old 2/26/10, 7:43 PM
Chuck Evans, TREC 7657's Avatar
Chuck Evans, TREC 7657 Chuck Evans, TREC 7657 is offline
Certified Master Inspector ®
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 8,138
Default Re: Supply vs. Return Register Placement

There is a second supply in this room



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
TheWoodlandsHomeInspection.com


Houston, TX
_______________________
Awards Committee Member

SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #12  
Old 2/27/10, 12:07 AM
mklein's Avatar
mklein mklein is offline
InterNACHI Member
 
Join Date: Dec 2009
Posts: 91
Default Re: Supply vs. Return Register Placement

I have to wonder if some people do not understand how ceiling diffusers work. If they are designed properly, the air blows out along the ceiling. To get an idea of the air flow pattern for a single throw diffuser, look at Figure 14 in this article: http://www.hdgrant.com/hpacart.pdf. The louver direction dictates which direction the air flows. If you look closely at the photo, you can see that the louvers are aimed away from the return grille. If you look at Figure 14 in the article, you can see that if the diffuser is working correctly, that is designed with the proper air flow for the diffuser, then the return air grille is in an optimal location in the room.

If you want to verify what is going on in the room, use a smoke tube to visualize the air flow. It is probably one of the most under-rated diagnostic tools out there.



Matthew Klein, P.E., M.B.A.

Criterium Engineers

PO Box 181503
Cincinnati, OH 45018-1503
Phone: 513-474-9600
FAX: 888-747-0427
E-mail: Criterium-Cincinnati@fuse.net
Website: www.Criterium-Cincinnati.com
Reply With Quote
  #13  
Old 2/27/10, 11:29 AM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Jun 2005
Location: Nashville, TN
Posts: 10,218
Default Re: Supply vs. Return Register Placement



Example of "throw" (ignore the ceiling leak...).



"working together to get-IR-done" Chris Walsh
Bracebridge, Ontario:


David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing, Ethics & Legal Issues for Inspectors 52 7/11/17 3:34 PM
HELP! What do you call a 3 prong male plug with a cord. gromicko Electrical Inspections 5 1/9/09 12:33 AM
How To Stop Your Home Inspection Clients From Suing You! rray General Inspection Discussion 17 6/4/08 2:22 PM
Water Heater supply and return reversed dosborne Plumbing Inspections 3 8/5/07 2:08 PM
Water supply pipes and drain pipes running through return air ducts? aharper1 Inspecting HVAC Systems 3 9/26/06 12:09 PM

All times are GMT -4. The time now is 1:10 PM.
no new posts