  #1  
Old 5/19/17, 4:03 PM
Frank Blas Frank Blas is offline
Certified Professional Inspector (CPI)
 
Join Date: Jun 2015
Location: Charlotte, NC
Posts: 138
Default Verbiage for an old Heat Pump

How do you verbalize when a heat pump was manufactured in 1978?? Found water stains at the suspended ceiling panels (maybe at the fan coils?)but couldn't determine if it is an active leak. Agent is representing her nephew and wants it to be mentioned that it is beyond its life expectancy...I couldn't agree more.
Reply With Quote
Need a home inspection in Arizona? Check out InterNACHI's listing of Arizona certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/19/17, 4:35 PM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Certified Professional Inspector (CPI)
 
Join Date: Jun 2005
Location: Nashville, TN
Posts: 10,158
Default Re: Verbiage for an old Heat Pump

Unless otherwise just being old, tell your real estate agent to go back and read their own damn real estate contract.

So real estate agents have different standards for their family members?!

If you are not an HVAC service technician, you don't have nothing to say about it if you turn it on and it makes conditioned air.



"working together to get-IR-done" Chris Walsh
Bracebridge, Ontario:


David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #3  
Old 5/19/17, 4:45 PM
Joshua L. Frederick Joshua L. Frederick is online now
Certified Professional Inspector (CPI)
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 4,147
Send a message via AIM to jfrederick
Default Re: Verbiage for an old Heat Pump

Quote:
Originally Posted by dandersen View Post
So real estate agents have different standards for their family members?!
Lol, that's the first thing I thought of when I read it. What a joke.




http://northwestohiohomeinspector.com

Defiance home inspector
Northwest Ohio home inspector
Reply With Quote
  #4  
Old 5/19/17, 4:57 PM
Frank Blas Frank Blas is offline
Certified Professional Inspector (CPI)
 
Join Date: Jun 2015
Location: Charlotte, NC
Posts: 138
Default Re: Verbiage for an old Heat Pump

So a unit manufactured in 1978 has no concerns? Do you mention life expectancy at all? If you are dealing with a first time homebuyer who doesn't know to think about a unit's age do you just say "works great?"
Reply With Quote
  #5  
Old 5/19/17, 5:04 PM
Frank Blas Frank Blas is offline
Certified Professional Inspector (CPI)
 
Join Date: Jun 2015
Location: Charlotte, NC
Posts: 138
Default Re: Verbiage for an old Heat Pump

Your comment is a bit of a joke Joshua...you've known these things all along right? Another reason why these threads are becoming less used by people wanting to sharpen their skills...comments like yours.
Reply With Quote
  #6  
Old 5/19/17, 5:05 PM
Thomas Witt's Avatar
Thomas Witt Thomas Witt is offline
Certified Master Inspector ®
 
Join Date: Aug 2010
Location: Milan, Baltimore, Topanga Canyon
Posts: 4,775
Default Re: Verbiage for an old Heat Pump

Quote:
Originally Posted by fblas View Post
How do you verbalize when a heat pump was manufactured in 1978?? Found water stains at the suspended ceiling panels (maybe at the fan coils?)but couldn't determine if it is an active leak. Agent is representing her nephew and wants it to be mentioned that it is beyond its life expectancy...I couldn't agree more.
So if you couldn't agree more than say that.

I don't understand inspectors coming on this message board asking others how to write up what should be a typical comment.
First try writing a comment yourself, that's how you learn.
If you're unsure about how your comment is phrased then post it for feedback.
At least it shows you've made an effort on your own.



"To avoid criticism, say nothing, do nothing, be nothing"

E. Hubbard circa 1898
Reply With Quote
  #7  
Old 5/19/17, 5:11 PM
Thomas Witt's Avatar
Thomas Witt Thomas Witt is offline
Certified Master Inspector ®
 
Join Date: Aug 2010
Location: Milan, Baltimore, Topanga Canyon
Posts: 4,775
Default Re: Verbiage for an old Heat Pump

That's BS, of course you comment on the age of the unit as well as its function.



Quote:
Originally Posted by dandersen View Post
Unless otherwise just being old, tell your real estate agent to go back and read their own damn real estate contract.

So real estate agents have different standards for their family members?!

If you are not an HVAC service technician, you don't have nothing to say about it if you turn it on and it makes conditioned air.



"To avoid criticism, say nothing, do nothing, be nothing"

E. Hubbard circa 1898
Reply With Quote
  #8  
Old 5/19/17, 6:43 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
Certified Professional Inspector (CPI)
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 17,083
Default Re: Verbiage for an old Heat Pump

The HVAC system is functional but beyond its design life. We recommend that you budget for replacement



"So, what are your thoughts on the Flir One??"

Reply With Quote
  #9  
Old 5/19/17, 7:34 PM
Christopher Currins, CMI Christopher Currins, CMI is offline
Certified Master Inspector ®
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 16,708
Default Re: Verbiage for an old Heat Pump

Quote:
Originally Posted by bkelly2 View Post
The HVAC system is functional but beyond its design life. We recommend that you budget for replacement
It's really that simple.
Reply With Quote
  #10  
Old 5/19/17, 10:30 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
Certified Professional Inspector (CPI)
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 9,973
Default Re: Verbiage for an old Heat Pump

I have a canned statement in HIP that is highlighted on every inspection I do that has A/C

The average life expectancy of a standard A/C compressor is 15 years give or take. (Notice I stated Average).

Then I use this statement to ID the specific A/C ( The 3 ton split system A/C unit located adjacent to the north exterior wall was MFG in 2004 and was operated from its thermostat.) Then I expect the client to do the math.

In 20 years I have never had these two statements questioned. I personally think your not doing your client a service by not dating equipment. A large amount of my clients ask how old is the furnace/ A/C unit. I provide that information. I take a pic of the A/C unit with disconnect visible, a pic of the furnace with the cover removed and burners operating. I take a pic of both the A/C temp and the furnace temp along with several pics of my CFM meter measuring air flow at the supply registers close to the furnace and the most distant register.

That is my story boys and girls and I'm sticking to it.



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
Okla State License # 130
580-268-3340
Reply With Quote
  #11  
Old 5/20/17, 6:58 AM
Frank Blas Frank Blas is offline
Certified Professional Inspector (CPI)
 
Join Date: Jun 2015
Location: Charlotte, NC
Posts: 138
Default Re: Verbiage for an old Heat Pump

Great info, thanks.
Reply With Quote
  #12  
Old 5/20/17, 2:49 PM
Kenneth R. Brittain's Avatar
Kenneth R. Brittain Kenneth R. Brittain is online now
Certified Professional Inspector (CPI)
 
Join Date: Jul 2011
Location: Charlotte NC
Posts: 1,393
Default Re: Verbiage for an old Heat Pump

Hey Frank you should come to one of our local chapter meetings. You can meet local inspectors and ask question face to face and get straight answers from other inspectors in our market.

We meet the second Tuesday every month at 1201 Greenwood Cliff Road, Charlotte, NC 28204 (Mingle School of Real Estate & CRRA building) 7-9 PM.



Ken Brittain, CPI
Home Vue Inspection Services, llc
Inspecting Charlotte, Concord & Surrounding Cities
InterNACHI 11071502 NCHILB 3262
704-455-0482

Reply With Quote
  #13  
Old 5/20/17, 4:31 PM
Frank Blas Frank Blas is offline
Certified Professional Inspector (CPI)
 
Join Date: Jun 2015
Location: Charlotte, NC
Posts: 138
Default Re: Verbiage for an old Heat Pump

Hey Kenneth, will definitely consider that. I appreciate the offer and will reach out to you.
Reply With Quote
Need a home inspection in Arizona? Check out InterNACHI's listing of Arizona certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 5/20/17, 5:01 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 3,504
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Verbiage for an old Heat Pump

Why not write it up as if you would expect it to be written up if you were buying the house. What would you want the inspector to say.
Reply With Quote
  #15  
Old 5/20/17, 5:33 PM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Certified Professional Inspector (CPI)
 
Join Date: Jun 2005
Location: Nashville, TN
Posts: 10,158
Default Re: Verbiage for an old Heat Pump

Quote:
Originally Posted by fblas View Post
So a unit manufactured in 1978 has no concerns? Do you mention life expectancy at all? If you are dealing with a first time homebuyer who doesn't know to think about a unit's age do you just say "works great?"
And anyone else you doesn't agree...

I have been doing this for 27 Years and I have "not once" condemned an HVAC unit based upon it's birth certificate!

Not Once, have I received a call about a failed HVAC unit because due to it's age.

Every day a unit runs, the greater the odds that it will fail for some reason. Most failures can be repaired without replacement of the whole unit. Not always the best decision, but it can be fixed when it breaks.

If you call me because your 20yr old unit failed, and I inspected it and said it was fine...

It was fine at the time I looked at it. Congratulations, you managed to get 20 yrs out of it! What do you want from me? I'm not Jesus Christ. I can not resurrect Lazerous from the tomb!

I tell a crap load of clients not to repair a unit if they end up with a large cost repair. Especially R-22 units that the Government (my buddy Al Gore) decided to halt production of that Refrigerant. Don't just stop making those units, **** with the people who have to buy a new unit all over 6 oz of needed R-22! I tell them to invest the repair cost towards new equipment.

I have two Heat Pumps that are 18 yrs old.
None of you better come here and tell me they have to be changed because of their age, or I'll kick your *** all the way to the street (and it's a long way).

When I come across a really old unit. I tell my clients that they should be serviced twice a year for the rest of their life, or they won't last long.

And yes, I ask first time buyers (and millionaires just to get a rise out of them) if they can afford to replace the equipment next week after they closed on the house. If their Agent is putting them in that house with every last available dime, it's not going to be my issue to deal with. ( I don't get any clients like this, except REA's kids buying their first house. That's also why they are calling me. Otherwise they don't want me anywhere near their clients like that.)!

You know how Gruff I get sometimes!

If it is as old a Moses, I am addressing the "condition" of the equipment, not it's age.



"working together to get-IR-done" Chris Walsh
Bracebridge, Ontario:


David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


All times are GMT -4. The time now is 2:26 AM.
no new posts