The air temp here is a pretty constant 72F. The pool here is about 70 F and I'd like to turn it up about 5 degrees. The pool guy says he can't. I don't believe it. There's got to be a mixing valve somewhere. There's no control in the underground mechanical room that I can recognize as maybe controlling water temp.

This is the only control I can see without climbing onto the roof, and I don't have access permission. Does this look like a thermostatic control for water temp?
Attached Thumbnails
Pool temperature control-panels-1-jpg   Pool temperature control-panels-2-jpg   Pool temperature control-panels-3-jpg   Pool temperature control-panels-4-png  



Kenton Shepard, CMI Inspector/Instructor

InterNACHI Director of International Development
Director of Green Building
Builder: House of Horrors 1&2
Author: InterNACHI Narrative Library


Last edited by kshepard; 1/1/16 at 2:11 PM..
Reply With Quote
Need a home inspection in Colorado? Check out InterNACHI's listing of Colorado certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/1/16, 2:18 PM
Kenton Shepard, CMI's Avatar
Kenton Shepard, CMI Kenton Shepard, CMI is offline
Certified Master Inspector
 
Join Date: Aug 2004
Location: Lyons, CO
Posts: 6,278
Send a message via ICQ to kshepard
Default Re: Pool temperature control

The mechanical room. Pump not grounded that I can see. This thing going to kill me?
Attached Thumbnails
Pool temperature control-mechanical-1-jpg   Pool temperature control-mechanical-2-jpg   Pool temperature control-mechanical-3-jpg   Pool temperature control-mechanical-4-jpg   Pool temperature control-mechanical-5-jpg  




Kenton Shepard, CMI Inspector/Instructor

InterNACHI Director of International Development
Director of Green Building
Builder: House of Horrors 1&2
Author: InterNACHI Narrative Library

Reply With Quote
  #3  
Old 1/1/16, 4:11 PM
Ian W. Mayer, CMI's Avatar
Ian W. Mayer, CMI Ian W. Mayer, CMI is online now
Certified Master Inspector ®
 
Join Date: Jun 2014
Location: Los Angeles, CA
Posts: 3,550
Default Re: Pool temperature control

On a gas heater, it's pretty simple. On a solar heater as pictured, you, of course, are limited by what the sun does. But that said, solar heaters can be pretty effective when they're not leaking (and prone to leaks appears their biggest draw back). Most pool heaters I see are gas, and the few solar heaters I've seen didn't have an actual temperature control thermostat.

Pool pumps don't have to be grounded per se at the pump itself, they have to be bonded.

The electrical system as a whole should be grounded, and that fuse box looks pretty scary.
It looks like a shock hazard from here.
Reply With Quote
  #4  
Old 1/1/16, 4:28 PM
Kenton Shepard, CMI's Avatar
Kenton Shepard, CMI Kenton Shepard, CMI is offline
Certified Master Inspector
 
Join Date: Aug 2004
Location: Lyons, CO
Posts: 6,278
Send a message via ICQ to kshepard
Default Re: Pool temperature control

Quote:
Originally Posted by imayer View Post
On a gas heater, it's pretty simple. On a solar heater as pictured, you, of course, are limited by what the sun does. But that said, solar heaters can be pretty effective when they're not leaking (and prone to leaks appears their biggest draw back). Most pool heaters I see are gas, and the few solar heaters I've seen didn't have an actual temperature control thermostat.

Pool pumps don't have to be grounded per se at the pump itself, they have to be bonded.

The electrical system as a whole should be grounded, and that fuse box looks pretty scary.
It looks like a shock hazard from here.
There's no grounding or bonding of any electrical components on this property, or on most properties in Mexico.



Kenton Shepard, CMI Inspector/Instructor

InterNACHI Director of International Development
Director of Green Building
Builder: House of Horrors 1&2
Author: InterNACHI Narrative Library

Reply With Quote
  #5  
Old 1/1/16, 9:27 PM
Larry Kage, CMI Larry Kage, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: NW, MI
Posts: 16,441
Default Re: Pool temperature control

Quote:
...that fuse box looks pretty scary.
Are those wires soldered to the outside if the main cartrige fuses?

Pool temperature control-1-jpg




Awards Committee Member
SUBMIT YOUR AWARD NOMINATIONS HERE:
http://co.nachi.org/inachiawards/

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
____________________________________________

Larry Kage, CMI 2004-2017
State Licensed Builder since 1973
InterNACHI Lifetime Member
~retired~

The above post represents my personal opinion.
Reply With Quote
  #6  
Old 1/1/16, 11:33 PM
Chuck Evans, TREC 7657's Avatar
Chuck Evans, TREC 7657 Chuck Evans, TREC 7657 is online now
Certified Master Inspector ®
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 8,820
Default Re: Pool temperature control

Quote:
Originally Posted by lkage View Post
Are those wires soldered to the outside if the main cartrige fuses?

Attachment 115274
Probably just wedged between the fuse clip and the fuse.

Kenton, always let someone else enter the pool before you and don't touch the railing.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
TheWoodlandsHomeInspection.com


Houston, TX
_______________________
Awards Committee Member

SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #7  
Old 1/2/16, 12:30 AM
Kenton Shepard, CMI's Avatar
Kenton Shepard, CMI Kenton Shepard, CMI is offline
Certified Master Inspector
 
Join Date: Aug 2004
Location: Lyons, CO
Posts: 6,278
Send a message via ICQ to kshepard
Default Re: Pool temperature control

YAH, I have never seen wires placed across fuses like that. I don't know what it means. Mexican electrical is very unique.
For the first month here I could never figure out where the neutral conductor was coming off the pole. All I saw was the phase conductor. Finally I realized that the neutral and phase (hot) conductors were housed within the same conductor insulation. They appeared to be one wire coming off the pole.

Just inside my front door I have a dirt space where squirrels have tunneled in and now I look up from writing sometimes and see squirrels running across my floor. I would like to test my pool each time before swimming by tossing a squirrel in, but I can't seem to catch one.



Kenton Shepard, CMI Inspector/Instructor

InterNACHI Director of International Development
Director of Green Building
Builder: House of Horrors 1&2
Author: InterNACHI Narrative Library


Last edited by kshepard; 1/2/16 at 12:34 AM..
Reply With Quote
  #8  
Old 1/2/16, 9:33 AM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 71,041
Default Re: Pool temperature control

Quote:
Originally Posted by kshepard View Post
YAH, I have never seen wires placed across fuses like that. I don't know what it means.
It means there is no fuse.

Same as the old penny under a buss fuse trick. NO protection whatsoever.




As a Professional Home Inspector, I support the privacy of my clients.

You own your private information. I won't sell or give away yours, others do


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
  #9  
Old 1/2/16, 10:29 AM
Michael A. Clark, CMI's Avatar
Michael A. Clark, CMI Michael A. Clark, CMI is online now
Certified Master Inspector
 
Join Date: Apr 2012
Location: Almost Heaven, WV
Posts: 6,754
Default Re: Pool temperature control

Quote:
Originally Posted by mlarson View Post
It means there is no fuse.

Same as the old penny under a buss fuse trick. NO protection whatsoever.
This isn't totally accurate. The protection IS the wire.

In the absence of a fuse, when the wire melts in two, the circuit becomes open!




Michael A Clark, Certified Master Inspector®
Inspection Connection
St Albans, West Virginia

"Always tell the truth,
do what you say you will,
and do it Righter than Right...Always"

Facebook

Google Plus

www.charleston-home-inspector.com
www.icwvhomes.com

mclark@icwvhomes.com
Reply With Quote
  #10  
Old 1/2/16, 10:31 AM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 71,041
Default Re: Pool temperature control

Quote:
Originally Posted by mclark2 View Post
This isn't totally accurate. The protection IS the wire.

In the absence of a fuse, when the wire melts in two, the circuit becomes open!
And what is the clearing capability of of said wire?



As a Professional Home Inspector, I support the privacy of my clients.

You own your private information. I won't sell or give away yours, others do


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
  #11  
Old 1/3/16, 2:00 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is online now
Certified Master Inspector
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 9,558
Default Re: Pool temperature control

Quote:
Originally Posted by kshepard View Post
YAH, I have never seen wires placed across fuses like that. I don't know what it means. Mexican electrical is very unique.
For the first month here I could never figure out where the neutral conductor was coming off the pole. All I saw was the phase conductor. Finally I realized that the neutral and phase (hot) conductors were housed within the same conductor insulation. They appeared to be one wire coming off the pole.

Just inside my front door I have a dirt space where squirrels have tunneled in and now I look up from writing sometimes and see squirrels running across my floor. I would like to test my pool each time before swimming by tossing a squirrel in, but I can't seem to catch one.
I love fried squirrel!



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
Reply With Quote
  #12  
Old 1/3/16, 9:04 PM
Kenton Shepard, CMI's Avatar
Kenton Shepard, CMI Kenton Shepard, CMI is offline
Certified Master Inspector
 
Join Date: Aug 2004
Location: Lyons, CO
Posts: 6,278
Send a message via ICQ to kshepard
Default Re: Pool temperature control

Is using a squirrel as an electrical testing device an accepted ASTM inspection method?
I think it is in México. Association of Squirrel Testing Methods (ASTM)



Kenton Shepard, CMI Inspector/Instructor

InterNACHI Director of International Development
Director of Green Building
Builder: House of Horrors 1&2
Author: InterNACHI Narrative Library

Reply With Quote
  #13  
Old 1/3/16, 9:11 PM
Kenton Shepard, CMI's Avatar
Kenton Shepard, CMI Kenton Shepard, CMI is offline
Certified Master Inspector
 
Join Date: Aug 2004
Location: Lyons, CO
Posts: 6,278
Send a message via ICQ to kshepard
Default Re: Pool temperature control

Quote:
Originally Posted by mlarson View Post
It means there is no fuse.

Same as the old penny under a buss fuse trick. NO protection whatsoever.

I agree. I'm not going back into the pool until I ground the pump and replace the breaker with a GFCI type. If the fuses were bypassed because they kept blowing, that indicates to me that there's possibly some other electrical problem, although I'm guessing that the fuses were the original. OCPD and once the breaker was installed, they decided to bypass them with the wire.



Kenton Shepard, CMI Inspector/Instructor

InterNACHI Director of International Development
Director of Green Building
Builder: House of Horrors 1&2
Author: InterNACHI Narrative Library

Reply With Quote
Need a home inspection in Colorado? Check out InterNACHI's listing of Colorado certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/3/16, 9:32 PM
Kenton Shepard, CMI's Avatar
Kenton Shepard, CMI Kenton Shepard, CMI is offline
Certified Master Inspector
 
Join Date: Aug 2004
Location: Lyons, CO
Posts: 6,278
Send a message via ICQ to kshepard
Default Re: Pool temperature control

...and, as far as the temperature control, there should be something that's basically a TPR valve for water running through the tubes in the panel, and that valve would be set to open at a pre-determined temperature. And then there's be a mixing valve that controls the temperature of water entering the pool. This is pretty obviously a thermostat calibrated from 30 F to 110 F, so I don't see what else it could possibly control.
Attached Thumbnails
Pool temperature control-panels-3-jpg   Pool temperature control-panels-4-png  



Kenton Shepard, CMI Inspector/Instructor

InterNACHI Director of International Development
Director of Green Building
Builder: House of Horrors 1&2
Author: InterNACHI Narrative Library