Default Re: Weld County, Colorado On-Site Wastewater Treatment System Regulations Study Guide

The wall between a siphon or pump chamber and the previous chamber must be watertight (except for the intended opening).
Reply With Quote
Need a home inspection in Alabama? Check out InterNACHI's listing of Alabama certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #62  
Old 5/27/18, 10:57 PM
Nick Gromicko, CMI's Avatar
Nick Gromicko, CMI Nick Gromicko, CMI is online now
Active Poster
 
Join Date: Aug 2002
Location: Nederland, Colorado
Posts: 64,464
Default Re: Weld County, Colorado On-Site Wastewater Treatment System Regulations Study Guide

The tank must be anchored where ground water or floodwaters could cause instability or floatation.
Reply With Quote
  #63  
Old 5/27/18, 10:59 PM
Nick Gromicko, CMI's Avatar
Nick Gromicko, CMI Nick Gromicko, CMI is online now
Active Poster
 
Join Date: Aug 2002
Location: Nederland, Colorado
Posts: 64,464
Default Re: Weld County, Colorado On-Site Wastewater Treatment System Regulations Study Guide

If the manufacturer doesn't provide anchoring recommendations, the anchoring system must be designed by a P.E.
Reply With Quote
  #64  
Old 5/27/18, 11:00 PM
Nick Gromicko, CMI's Avatar
Nick Gromicko, CMI Nick Gromicko, CMI is online now
Active Poster
 
Join Date: Aug 2002
Location: Nederland, Colorado
Posts: 64,464
Default Re: Weld County, Colorado On-Site Wastewater Treatment System Regulations Study Guide

Tanks must be permanently and legibly marked including manufacturer, serial number, effective volume, maximum depth of earth cover, inlet and outlet identifications.
Reply With Quote
  #65  
Old 5/27/18, 11:01 PM
Nick Gromicko, CMI's Avatar
Nick Gromicko, CMI Nick Gromicko, CMI is online now
Active Poster
 
Join Date: Aug 2002
Location: Nederland, Colorado
Posts: 64,464
Default Re: Weld County, Colorado On-Site Wastewater Treatment System Regulations Study Guide

Number of Bedrooms. Tank Capacity
2 or 3 1,000 gallons
4 1,250 gallons
Each Additional 250 gallons
Reply With Quote
  #66  
Old 5/27/18, 11:03 PM
Nick Gromicko, CMI's Avatar
Nick Gromicko, CMI Nick Gromicko, CMI is online now
Active Poster
 
Join Date: Aug 2002
Location: Nederland, Colorado
Posts: 64,464
Default Re: Weld County, Colorado On-Site Wastewater Treatment System Regulations Study Guide

For multi-family and non-residential applications, a tank must be sized to permit detention of wastewater flows for at least 48 hours.
Reply With Quote
  #67  
Old 5/27/18, 11:05 PM
Nick Gromicko, CMI's Avatar
Nick Gromicko, CMI Nick Gromicko, CMI is online now
Active Poster
 
Join Date: Aug 2002
Location: Nederland, Colorado
Posts: 64,464
Default Re: Weld County, Colorado On-Site Wastewater Treatment System Regulations Study Guide

A septic tank must have tow or more compartments or more than one tank may be used in series. The first must hold no less than 1/2 of the required effective volume.
Reply With Quote
  #68  
Old 5/27/18, 11:05 PM
Nick Gromicko, CMI's Avatar
Nick Gromicko, CMI Nick Gromicko, CMI is online now
Active Poster
 
Join Date: Aug 2002
Location: Nederland, Colorado
Posts: 64,464
Default Re: Weld County, Colorado On-Site Wastewater Treatment System Regulations Study Guide

Inlet must be at least two inches higher than the outlet.
Reply With Quote
  #69  
Old 5/27/18, 11:07 PM
Nick Gromicko, CMI's Avatar
Nick Gromicko, CMI Nick Gromicko, CMI is online now
Active Poster
 
Join Date: Aug 2002
Location: Nederland, Colorado
Posts: 64,464
Default Re: Weld County, Colorado On-Site Wastewater Treatment System Regulations Study Guide

Inlet tees must extend above the surface of the liquid at least 5 inches. Must also extend a minimum of 8 inches below the liquid surface. However the inlet tee must not extend to a depth of more than 40 percent of the entire liquid depth.
Reply With Quote
  #70  
Old 5/27/18, 11:15 PM
Nick Gromicko, CMI's Avatar
Nick Gromicko, CMI Nick Gromicko, CMI is online now
Active Poster
 
Join Date: Aug 2002
Location: Nederland, Colorado
Posts: 64,464
Default Re: Weld County, Colorado On-Site Wastewater Treatment System Regulations Study Guide

The distance from the outlet invert to the underside of the tank top must be at least 10 inches.
Reply With Quote
  #71  
Old 5/27/18, 11:16 PM
Nick Gromicko, CMI's Avatar
Nick Gromicko, CMI Nick Gromicko, CMI is online now
Active Poster
 
Join Date: Aug 2002
Location: Nederland, Colorado
Posts: 64,464
Default Re: Weld County, Colorado On-Site Wastewater Treatment System Regulations Study Guide

Liquid depth must be a minimum of 30 inches and the maximum depth must not exceed tank length.
Reply With Quote
  #72  
Old 5/27/18, 11:18 PM
Nick Gromicko, CMI's Avatar
Nick Gromicko, CMI Nick Gromicko, CMI is online now
Active Poster
 
Join Date: Aug 2002
Location: Nederland, Colorado
Posts: 64,464
Default Re: Weld County, Colorado On-Site Wastewater Treatment System Regulations Study Guide

The transfer of liquid from the first compartment to the second must be made at a liquid depth (measured from liquid surface) of 35 and 40 percent of the liquid depth.
Reply With Quote
  #73  
Old 5/27/18, 11:20 PM
Nick Gromicko, CMI's Avatar
Nick Gromicko, CMI Nick Gromicko, CMI is online now
Active Poster
 
Join Date: Aug 2002
Location: Nederland, Colorado
Posts: 64,464
Default Re: Weld County, Colorado On-Site Wastewater Treatment System Regulations Study Guide

A tank must have a minimum of 25 square feet of liquid surface area and have at least a 6 foot separation between inlets and outlets.
Reply With Quote
Need a home inspection in Alabama? Check out InterNACHI's listing of Alabama certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #74  
Old 5/27/18, 11:22 PM
Nick Gromicko, CMI's Avatar
Nick Gromicko, CMI Nick Gromicko, CMI is online now
Active Poster
 
Join Date: Aug 2002
Location: Nederland, Colorado
Posts: 64,464
Default Re: Weld County, Colorado On-Site Wastewater Treatment System Regulations Study Guide

Metal septic tanks are prohibited.
Reply With Quote
  #75  
Old 5/27/18, 11:25 PM
Nick Gromicko, CMI's Avatar
Nick Gromicko, CMI Nick Gromicko, CMI is online now
Active Poster
 
Join Date: Aug 2002
Location: Nederland, Colorado
Posts: 64,464
Default Re: Weld County, Colorado On-Site Wastewater Treatment System Regulations Study Guide

Flexible pipe couplings (FERNCOs) are only permitted in the gravity flow portions of an OWTS.
Reply With Quote