  #1  
Old 1/27/13, 2:04 PM
Merc Man Merc Man is offline
New User
 
Join Date: Dec 2010
Posts: 4
Please Note: Merc Man is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Air Admittance Valve

When my lift pump in my basement runs it sucks the water out of the trap for my upstairs bath tub. I was told on this forum that my venting is bad. To replace my venting would be a nightmare. I have been told to install a Air Admittance Valve but I'm not sure if I would install it at the upstairs bath tub before the trap or at the lift station in the basement. I'm hopeful that someone here can help me. Thanks, Jim
Reply With Quote
Need a home inspection in Hawaii? Check out InterNACHI's listing of Hawaii certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/28/13, 12:15 PM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 70,366
Default Re: Air Admittance Valve

At the tub. Tub is not currently adequately vented.



As a Professional Home Inspector, I support the privacy of my clients.



www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
  #3  
Old 1/28/13, 2:38 PM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
Certified Master Inspector
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 14,558
Default Re: Air Admittance Valve

Quote:
Originally Posted by mlarson View Post
At the tub. Tub is not currently adequately vented.
I would add, at the highest point possible, preferably above the flood line of any fixture on the vent line...



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE «
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 1/28/13, 2:52 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2007
Location: Minnesota & Northern Iowa
Posts: 29,375
Default Re: Air Admittance Valve

Never assume...

Make sure it is installed on the correct side of the P-trap!




Jeffrey R. Jonas
Owatonna, Minnesota



"I am not a teacher, but an awakener."
- Robert Frost, American poet (1874-1963).

"We Respect Our Clients Right to Privacy"

Reply With Quote
  #5  
Old 1/28/13, 9:24 PM
Merc Man Merc Man is offline
New User
 
Join Date: Dec 2010
Posts: 4
Please Note: Merc Man is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Air Admittance Valve

So if I install it according to your sketch...when the lift pump runs in the basement and pushes the gray water or sewage out to the septic tank, the Air Admittance Valve will open and suck air and the water will stay in the trap? I'm not sure what the flood line is, could you explain? Thanks so much for helping me out. I hope this works!! Jim
Reply With Quote
  #6  
Old 1/30/13, 3:20 PM
Mark S. Tyson, CGC1516843 Mark S. Tyson, CGC1516843 is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Fort Pierce, Fl.
Posts: 459
Default Re: Air Admittance Valve

Quote:
Originally Posted by Merc Man View Post
So if I install it according to your sketch...when the lift pump runs in the basement and pushes the gray water or sewage out to the septic tank, the Air Admittance Valve will open and suck air and the water will stay in the trap? I'm not sure what the flood line is, could you explain? Thanks so much for helping me out. I hope this works!! Jim
Individual and branch-type air admittance valves shall be located a minimum of 4 inches above the the horizontal branch drain or fixture being vented. Stack-type air admittance valves shall be located no less than 6 inches above the flood level rim of the highest fixture being vented. If the bathroom contains a vanity that would be the ideal location.



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
  #7  
Old 1/30/13, 10:42 PM
Merc Man Merc Man is offline
New User
 
Join Date: Dec 2010
Posts: 4
Please Note: Merc Man is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question for Mike S.Tyson Air Admittance Valve

So even though it does not suck the water out of the bath room sink trap it would still work to keep water in the trap in the tub? If so that would be so much easier as I wouldn't have to get in behind the tub to make the installation. Please advise and I can't thank you enough for educating me on this. Jim
Reply With Quote
  #8  
Old 1/31/13, 10:02 AM
Michael A. Clark, CMI's Avatar
Michael A. Clark, CMI Michael A. Clark, CMI is offline
Certified Master Inspector
 
Join Date: Apr 2012
Location: Almost Heaven, WV
Posts: 6,663
Default Re: Air Admittance Valve

Quote:
Originally Posted by Merc Man View Post
So if I install it according to your sketch...when the lift pump runs in the basement and pushes the gray water or sewage out to the septic tank, the Air Admittance Valve will open and suck air and the water will stay in the trap? I'm not sure what the flood line is, could you explain? Thanks so much for helping me out. I hope this works!! Jim
The vent or aav should be downstream of the trap. The pump will suck air thru the valve instead of sucking water out of the trap.




Michael A Clark, Certified Master Inspector«
Inspection Connection
St Albans, West Virginia

"Always tell the truth,
do what you say you will,
and do it Righter than Right...Always"

Facebook

Google Plus

www.charleston-home-inspector.com
www.icwvhomes.com

mclark@icwvhomes.com
Reply With Quote
  #9  
Old 1/31/13, 10:26 AM
Mark S. Tyson, CGC1516843 Mark S. Tyson, CGC1516843 is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Fort Pierce, Fl.
Posts: 459
Default Re: Question for Mike S.Tyson Air Admittance Valve

Quote:
Originally Posted by Merc Man View Post
So even though it does not suck the water out of the bath room sink trap it would still work to keep water in the trap in the tub? If so that would be so much easier as I wouldn't have to get in behind the tub to make the installation. Please advise and I can't thank you enough for educating me on this. Jim
The trap at the tub is the lowest water seal at the bathroom. When the sump is activated it is sucking the water out of the trap and then gains air or vent, by placing the AAV at the vanity you will now have introduced air or vent to the lateral.
I find it unusual that the waste system was installed with out a vent through the roof or an AAV. Before doing anything you should inspect for a failed AAV or that the through the roof vent has not become blocked i.e. bird nest or some other foreign matter.
If adding an AAV becomes necessary the vanity is where it should be located as that is the highest fixture in the system being vented



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing, Ethics & Legal Issues for Inspectors 52 7/11/17 3:34 PM
Unusual Things I have found rcooke Canadian Home Inspectors 896 4/3/17 7:26 AM
Air Admittance valve? 2 traps aharper1 Plumbing Inspections 5 9/24/06 7:42 PM
Proper use of an air admittance valve? cceccarelli Plumbing Inspections 5 5/12/06 6:16 PM

All times are GMT -4. The time now is 4:46 PM.
no new posts