Default Atypical Water Heater Configuration

I inspected an 11,000+ square foot house yesterday that had a water heater setup that I had not encountered before. It had a pair of 199,900 BTU/hr tankless units installed conventionally on one area of the house, but the other installation paired a similar tankless unit with a 6 gallon 120v electric tank type unit with a circulating pump. The electric water heater was plugged into power.

What would be the rationale for supplying power to the electric water heater or even having it in this configuration? Does the rate of flow from the circulating pump not activate the flow switch on the tankless unit unless there is demand? I've seen tankless systems with circulating pumps, but not combined with a live electric tank unit.
Attached Thumbnails
Atypical Water Heater Configuration-p1100121-jpg   Atypical Water Heater Configuration-p1100125-jpg  



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
The Woodlands Home Inspections
Magnolia TX Home Inspections & Thermography


Houston, TX
_______________________
Awards Committee Member

SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/12/19, 10:53 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 27,529
Default Re: Atypical Water Heater Configuration

Sounds like a large home and it takes a long time to get warm water to the taps .I expect this system gives them hot water almost instantly to all hot taps .
Reply With Quote
  #3  
Old 1/12/19, 12:30 PM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 75,022
Default Re: Atypical Water Heater Configuration

Think of it as a buffer and a source of higher flow.

I bit unconventional but I could call the original installer and see if they would provide a better explanation.

Not a defect but I would be curious too.



As a Professional Home Inspector, I support the privacy of my clients.

You own your private information. I won't sell or give away yours, others do


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
  #4  
Old 1/12/19, 1:30 PM
Emmanuel J. Scanlan, TREC# 7593 Emmanuel J. Scanlan, TREC# 7593 is offline
Certified Professional Inspector (CPI)
 
Join Date: Dec 2004
Location: Josephine, TX
Posts: 7,846
Default Re: Atypical Water Heater Configuration

Quote:
Originally Posted by cevans View Post
I inspected an 11,000+ square foot house yesterday that had a water heater setup that I had not encountered before. It had a pair of 199,900 BTU/hr tankless units installed conventionally on one area of the house, but the other installation paired a similar tankless unit with a 6 gallon 120v electric tank type unit with a circulating pump. The electric water heater was plugged into power.

What would be the rationale for supplying power to the electric water heater or even having it in this configuration? Does the rate of flow from the circulating pump not activate the flow switch on the tankless unit unless there is demand? I've seen tankless systems with circulating pumps, but not combined with a live electric tank unit.

That appears to be a Grundfos Comfort System series pump with a timer. They have an approximate 6 GPM flow rate with almost immediate max flow when activated. The Rinnai WH only requires <1 GPM flow to turn the burners on and around .25 GPM flow to keep them on.


The only possibilities I would think of is to have a ready source of hot water during the timer off times until the WH kicks in. It could be enough to warm the path until the tankless flow is in the line. Also that Grundfos pump has a 36 - 150 Degree F operating range. Your Winter design temps have been set at 28 Degrees in your area. Being in the attic I would expect they could actually reach that low and long enough to damage the pump. Having the tank running would provide a ready source of hot water (and heat) to prevent that. I see they foamed the attic but is there a source of conditioned air there? Did the plumbing go in before the Plumber knew it would be foamed? Was the foam application correct and the outer envelope sealed properly? I've seen them foam attics and screw up with penetrations to the exterior.

It would be interesting to have the installer take on why they did it or even one of our own Professional Plumbers on the board chime in.



Knowledge is power, but sharing knowledge brings peace!

http://www.psinspection.com

TREC License# 7593
ICC Residential Combination Inspector
#5247015-R5 (Electrical, Mechanical, Plumbing and Building)
Professional Real Estate Inspections for the counties of Collin, Rockwall, Hunt, Dallas, Tarrant, Kaufman and all surrounding areas. If you want the the best you will find it with PS Inspection & Property Services LLC!

Last edited by escanlan; 1/12/19 at 1:38 PM..
Reply With Quote
  #5  
Old 1/12/19, 2:02 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2004
Location: this side of Texas dirt, another successful day
Posts: 4,537
Default Re: Atypical Water Heater Configuration

http://www.chandlerdesignbuild.com/f...hbDecJan08.pdf



badair

ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS/Stucco-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

National Association of Commercial Building Inspectors & Thermographers™ Member ID 12011-14TX

life is the random lottery of events followed by numerous narrow escapes...accept the good


Father Sky
Mother Earth
Children of the Universe
Forever Free
Always at Peace
Reply With Quote
  #6  
Old 1/12/19, 2:07 PM
Emmanuel J. Scanlan, TREC# 7593 Emmanuel J. Scanlan, TREC# 7593 is offline
Certified Professional Inspector (CPI)
 
Join Date: Dec 2004
Location: Josephine, TX
Posts: 7,846
Default Re: Atypical Water Heater Configuration

Quote:
Originally Posted by badair View Post

Good stuff Barry!! Don't want to anger Mom do we?



Knowledge is power, but sharing knowledge brings peace!

http://www.psinspection.com

TREC License# 7593
ICC Residential Combination Inspector
#5247015-R5 (Electrical, Mechanical, Plumbing and Building)
Professional Real Estate Inspections for the counties of Collin, Rockwall, Hunt, Dallas, Tarrant, Kaufman and all surrounding areas. If you want the the best you will find it with PS Inspection & Property Services LLC!

Last edited by escanlan; 1/12/19 at 2:14 PM..
Reply With Quote
  #7  
Old 1/12/19, 4:06 PM
Larry Kage, CMI's Avatar
Larry Kage, CMI Larry Kage, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: NW, MI
Posts: 18,529
Default Re: Atypical Water Heater Configuration

Quote:
Originally Posted by badair View Post
Barry's the man! Thanks for the information sought.




Awards Committee Officer
SUBMIT YOUR AWARD NOMINATIONS HERE:
http://co.nachi.org/inachiawards/

The InterNACHI Awards Committee is the final authority of the issuance of any award the committee offers and any rules interpretation updates.
____________________________________________

Larry Kage, CMI Lifetime Member
State Licensed Builder since 1973
InterNACHI Lifetime Member
~retired~

The above post represents my personal opinion.
Reply With Quote
  #8  
Old 1/12/19, 8:45 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is online now
Certified Master Inspector ®
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 10,771
Default Re: Atypical Water Heater Configuration

Thanks, guys.

I'm very familiar with using circulating pumps to minimize wait time for hot water in large houses, but this was the first I've seen a tankless unit paired with a tank type water heater.

Barry - You nailed it. I googled it but didn't get a hit, so you obviously did a better job with keyword selection. Thanks!

Manny - The house was built in 2014 and was designed with an unvented attic assembly (like everyone else, they forgot to ventilate the garage attic, though they did isolate it). It only had four HVAC systems all HE condensing type, along with the primary water heaters, but you'll note that they forgot about insulating the hot water lines with the circulating pump. It was an interesting place with high-end home automation features. I could control all of the thermostats from a central control panel near the kitchen. The actual thermostats all had remote sensors and were clustered in a closet in the second-floor laundry room. Property taxes are a mere $75K/year.
Attached Thumbnails
Atypical Water Heater Configuration-p1100006-jpg  



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
The Woodlands Home Inspections
Magnolia TX Home Inspections & Thermography


Houston, TX
_______________________
Awards Committee Member

SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #9  
Old 1/12/19, 9:29 PM
Dave Fetty, CMI's Avatar
Dave Fetty, CMI Dave Fetty, CMI is online now
Certified Master Inspector ®
 
Join Date: Feb 2014
Location: Naples all SWFL
Posts: 12,066
Default Re: Atypical Water Heater Configuration

Great thread... thanks guys!




Dave Fetty Certified Master Inspector
Florida Home Inspection And Property Services LLC
www.FHIAPS.COM
www.NaplesBestInspector.com
www.FortMyersInspector.com
Naples, Marco Island, Ft. Myers, Bonita Springs, Estero, Cape Coral
Dfetty@FHIAPS.COM
http://https://www.facebook.com/pages/Flori...2450912?ref=hl
Florida Radon Measurement Technician R2547
(239)339-7380
Reply With Quote
  #10  
Old 1/12/19, 11:40 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is online now
Certified Master Inspector ®
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 10,771
Default Re: Atypical Water Heater Configuration

Quote:
Originally Posted by badair View Post
hey Chuck
close plmb friend, prior encounter, saved docs w/link for future & dyslexia help
hope you & yours are thriving!
Thanks Bear. I still learn something new every day.

We're doing great. Prepping for a big move soon.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
The Woodlands Home Inspections
Magnolia TX Home Inspections & Thermography


Houston, TX
_______________________
Awards Committee Member

SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


All times are GMT -4. The time now is 12:32 PM.
no new posts