Default Boiler expansion tank

Can a boiler expansion tank be postioned up or sideways besides down?

Edit: ...and be operated properly?




Awards Committee Member
SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
____________________________________________

Larry Kage, CMI 2004-2017
State Licensed Builder since 1973
InterNACHI Lifetime Member
~retired~

The above post represents my personal opinion.

Last edited by lkage; 8/29/12 at 10:27 PM.. Reason: added...and be operated properly.
Reply With Quote
Need a home inspection in Virginia? Check out InterNACHI's listing of Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/29/12, 10:11 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2007
Location: Minnesota & Northern Iowa
Posts: 29,375
Default Re: Boiler expansion tank

Quote:
Originally Posted by lkage View Post
Can a boiler expansion tank be postioned up or sideways besides down?
Not sure what you mean by 'down'? Got a pic? I would assume it all depends on how the tank was manufactured. Typically I see them installed 'laying down' like in the first pic from the OP... https://www.nachi.org/forum/f20/why-e...-boiler-43447/



Jeffrey R. Jonas
Owatonna, Minnesota



"I am not a teacher, but an awakener."
- Robert Frost, American poet (1874-1963).

"We Respect Our Clients Right to Privacy"

Reply With Quote
  #3  
Old 8/29/12, 10:20 PM
Larry Kage, CMI Larry Kage, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: NW, MI
Posts: 16,175
Default Re: Boiler expansion tank

I'm talking about a bladder type expansion tank.

Like these: (#1 down, #2 sideways, #3 down)








Awards Committee Member
SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
____________________________________________

Larry Kage, CMI 2004-2017
State Licensed Builder since 1973
InterNACHI Lifetime Member
~retired~

The above post represents my personal opinion.
Reply With Quote
  #4  
Old 8/29/12, 11:47 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2007
Location: Minnesota & Northern Iowa
Posts: 29,375
Default Re: Boiler expansion tank

Okay... gotcha. I usually see them in the "up" position, but I don't think it really matters. I was trained that in the up position, any water entering the tank can drain back out by gravity. Seems like there was something about the diaphram failing also, but it's been too long ago. I see less and less boilers every year. I don't miss them at all. Sorry I wasn't much help.



Jeffrey R. Jonas
Owatonna, Minnesota



"I am not a teacher, but an awakener."
- Robert Frost, American poet (1874-1963).

"We Respect Our Clients Right to Privacy"

Reply With Quote
  #5  
Old 8/30/12, 12:19 AM
Joseph Hagarty, CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty, CMI is offline
Certified Master Inspector
 
Join Date: Jan 2003
Location: Boulder, Colorado
Posts: 7,417
Default Re: Boiler expansion tank

i have seen expansion tanks installed Up, Down, Sideways....
but.....
what position is Up, Down or Sideways



Joe Hagarty
mrdryervent@gmail.com

Cell: (484) 883-7018
InterNACHI
Boulder, Colorado

National President / NACHI (2003-2004)
NACHI Education Committee Member
Certified CMI Master Inspector Instructor
PA NACHI Certified Inspector # 01102902
PA Licensed Radon Inspector # 2080
PA Licensed Pesticide Applicator # 700884
Delaware Licensed Home Inspector # H4-071
Reply With Quote
  #6  
Old 8/30/12, 1:35 AM
Cameron Anderson's Avatar
Cameron Anderson Cameron Anderson is offline
Certified Professional Inspector (CPI)
 
Join Date: Nov 2011
Location: Peoria, IL
Posts: 6,989
Default Re: Boiler expansion tank

I've seen them in every position too, but mostly down. Ask Charlie if it matters, I would guess it may be according to manufacturer's specs.



Cameron Anderson
Integrity Home Inspection
Truth. In Real Estate.
Since 2004
Bachelor of Architecture, U of I, Urbana IL
Illinois Licensed Inspector
www.aaintegrityhomeinspection.com

www.homeinspectionpeoria.com
Reply With Quote
  #7  
Old 8/30/12, 12:24 PM
Larry Kage, CMI Larry Kage, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: NW, MI
Posts: 16,175
Default Re: Boiler expansion tank

Okay, I think it depends on where the put the air scoop.

Here is a Taco Air Scoop:





Awards Committee Member
SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
____________________________________________

Larry Kage, CMI 2004-2017
State Licensed Builder since 1973
InterNACHI Lifetime Member
~retired~

The above post represents my personal opinion.

Last edited by lkage; 8/30/12 at 12:28 PM..
Reply With Quote
  #8  
Old 8/30/12, 12:27 PM
Larry Kage, CMI Larry Kage, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: NW, MI
Posts: 16,175
Default Re: Boiler expansion tank





Awards Committee Member
SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
____________________________________________

Larry Kage, CMI 2004-2017
State Licensed Builder since 1973
InterNACHI Lifetime Member
~retired~

The above post represents my personal opinion.
Reply With Quote
  #9  
Old 8/30/12, 1:19 PM
John Gromkoski's Avatar
John Gromkoski John Gromkoski is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 1,081
Please Note: jgromkoski is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Boiler expansion tank

The primary requirement is that they be adequately supported.
Reply With Quote
  #10  
Old 8/30/12, 4:13 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,915
Default Re: Boiler expansion tank

Quote:
Originally Posted by lkage View Post
Okay, I think it depends on where the put the air scoop.

Here is a Taco Air Scoop:

I agree, the bladder should work in all positions. The air scoop makes a difference.

Any idea why they are almost always down?
Reply With Quote
  #11  
Old 8/30/12, 7:34 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 29,167
Default Re: Boiler expansion tank

I believe that the most standard installation of bladder expansion tanks on a closed hydronic system would be in the hanging position high above the boiler.

One picture Larry posted could possibly be a steel pressure tank.

Steel Expansion Tanks

The steel tanks are not the most popular – but they are still used in some of the older systems. In this unit the air and the water will touch each other and the air will compress when the water is being heated. The air is than compressed inside of the loop system to create the cushion. It will absorb the excess pressure.
Bladder Expansion Tank

In this tank the air and the water are separated through the use of a diaphragm. This tank is used in the newer systems including the ones equipped with a hydronic loop. The loop helps to control the pressure and must stay at the right level in order to work properly. It helps to install this before the suction side of the circulator pump that is in the supply side of the unit.
Because the bladder expansion tank will absorb the excess pressure inside of the hydronic loop it would help to add the make up water for the unit and hydronic loop close to where the tank is. This will help to keep the pressure relief valve, hydronic loop, and expansion tank at the right settings and with no excess pressure build up.
http://boilerinstallations.blogsavy....n-water-tanks/



CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #12  
Old 8/30/12, 9:13 PM
Larry Kage, CMI Larry Kage, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: NW, MI
Posts: 16,175
Default Re: Boiler expansion tank

Quote:
Originally Posted by mroberson View Post
I agree, the bladder should work in all positions. The air scoop makes a difference.

Any idea why they are almost always down?

The guys in the field that I talked to say it is because when they get waterlogged they are quite heavy and it is easier to remove from the down position.




Awards Committee Member
SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
____________________________________________

Larry Kage, CMI 2004-2017
State Licensed Builder since 1973
InterNACHI Lifetime Member
~retired~

The above post represents my personal opinion.
Reply With Quote
  #13  
Old 8/30/12, 11:11 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
Certified Professional Inspector (CPI)
 
Join Date: Aug 2006
Location: Chicago
Posts: 37,435
Default Re: Boiler expansion tank

Although these expansion tanks are meant to be installed vertically, they may also be installed horizontally if properly supported. The RX-60 and larger Radiant Extrol expansion tanks must be installed vertically on the ground and piping can be used to connect them to the air purger and float vent.
http://www.pexuniverse.com/content/h...expansion-tank
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Expansion Tank On A Hot Water Heater rmarton Plumbing Inspections 6 2/28/10 3:41 PM
Why is an expansion tank above the boiler? bgromicko Inspecting HVAC Systems 4 9/21/09 11:12 AM
Make $50.00 More Profit per Inspection with Septic Tanks ebeahm1 Ancillary Inspection Services 6 8/20/09 1:38 PM
Water heater expansion tank jfrederick Plumbing Inspections 3 11/17/08 3:35 PM
Water heater expansion tank jfrederick Plumbing Inspections 0 11/17/08 8:18 AM

All times are GMT -4. The time now is 4:51 PM.
no new posts