Default Copper gas tubing at manufactured fireplace

Anyone know of a requirement to sleeve copper gas tubing where it enters the sheet metal enclosure of a manufactured fireplace? I see it sometimes and suspect that certain jurisdictions require it, but I can't find a code to require it in the IRC. Personally I don't see the need for a sleeve there.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Award Winner 2016, 2015, 2014, 2013, 2012, 2011, 2010.
Ph: 704-351-1776
www.aohomeinspection.com

Reply With Quote
Need a home inspection in Maryland? Check out InterNACHI's listing of Maryland certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/9/12, 3:00 PM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Jun 2005
Location: Nashville, TN
Posts: 10,304
Default Re: Copper gas tubing at manufactured fireplace

This is not a code compliance message board...

However, I feel that:

All plumbing penetrations should be sleeved (in my opinion), if they are subject to potential damage.

But there are a lot of "Barney Fife Inspectors" that can help you out here...



"working together to get-IR-done" Chris Walsh
Bracebridge, Ontario:


David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #3  
Old 7/9/12, 4:05 PM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
Certified Master Inspector
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 14,684
Default Re: Copper gas tubing at manufactured fireplace

Not required in my jurisdiction, because copper is not allowed for natural gas distribution



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 7/9/12, 4:30 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
Certified Master Inspector
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 10,282
Send a message via Yahoo to jfunderburk
Default Re: Copper gas tubing at manufactured fireplace

Quote:
Originally Posted by dandersen View Post
This is not a code compliance message board...

However, I feel that:

All plumbing penetrations should be sleeved (in my opinion), if they are subject to potential damage.

But there are a lot of "Barney Fife Inspectors" that can help you out here...
Some inspectors around here write it up. I'm not sure why. There is no vibration so what is the potential damage possibility? There is no exposure to corrosive materials, no chance of a galvanic reaction.

I don't believe in recommending repair based on 'Joe's Law.'



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Award Winner 2016, 2015, 2014, 2013, 2012, 2011, 2010.
Ph: 704-351-1776
www.aohomeinspection.com

Reply With Quote
  #5  
Old 7/9/12, 4:31 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
Certified Master Inspector
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 10,282
Send a message via Yahoo to jfunderburk
Default Re: Copper gas tubing at manufactured fireplace

That same pipe likely touches various other materials as it snakes through the house. Why sleeve it here?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Award Winner 2016, 2015, 2014, 2013, 2012, 2011, 2010.
Ph: 704-351-1776
www.aohomeinspection.com

Reply With Quote
  #6  
Old 7/9/12, 8:23 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2004
Location: this side of Texas dirt, another successful day
Posts: 4,511
Default Re: Copper gas tubing at manufactured fireplace

not sure if this is what you needed

regardless of gas supply pipe material
most mfr require seal at entry through firebox
check install instructions ymmv
Attached Thumbnails
Copper gas tubing at manufactured fireplace-gas-line-firebox-sealed-jpg  



badair

ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

National Association of Commercial Building Inspectors & Thermographers™ Member ID 12011-14TX

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #7  
Old 7/9/12, 8:59 PM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Jun 2005
Location: Nashville, TN
Posts: 10,304
Default Re: Copper gas tubing at manufactured fireplace

Quote:
Originally Posted by jfunderburk View Post
That same pipe likely touches various other materials as it snakes through the house. Why sleeve it here?
Why is the damn sewer line sleeved?

1. It's not ours to question why.
2. It's not our damn job to determine what the code is.



"working together to get-IR-done" Chris Walsh
Bracebridge, Ontario:


David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #8  
Old 7/10/12, 12:46 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
Certified Professional Inspector (CPI)
 
Join Date: Jan 2005
Location: Mt Pleasant SC
Posts: 3,405
Default Re: Copper gas tubing at manufactured fireplace

Could be a habit since they sleeve it for csst. CSST manuf now recommends keeping the pipe a certain distance from other metal. The prefab metal boxes usually have an electrical outlet underneath that may be bonded to the fireplace.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Fort Mill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #9  
Old 7/10/12, 10:05 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
Certified Master Inspector
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 10,282
Send a message via Yahoo to jfunderburk
Default Re: Copper gas tubing at manufactured fireplace

Quote:
Originally Posted by dandersen View Post
Why is the damn sewer line sleeved?


To prevent direct contact from the foundation on the sewer pipe. Reduce the possibility of cracking. But I digress.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Award Winner 2016, 2015, 2014, 2013, 2012, 2011, 2010.
Ph: 704-351-1776
www.aohomeinspection.com

Reply With Quote
  #10  
Old 7/10/12, 10:07 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
Certified Master Inspector
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 10,282
Send a message via Yahoo to jfunderburk
Default Re: Copper gas tubing at manufactured fireplace

I ask because a local inspector inspected a property I did a pre-listing inspection on and he wrote up the absence of a sleeve on a copper gas tube (Bruce, he has a name similar to yours). Seems like we all agree there is no requirement (other than possibly the fireplace manufacturer's).



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Award Winner 2016, 2015, 2014, 2013, 2012, 2011, 2010.
Ph: 704-351-1776
www.aohomeinspection.com

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Total galvanic reaction? jtribuzio Plumbing Inspections 19 4/3/10 3:18 AM
copper bar Unregistered AskNACHI.org Inspection Questions Forum 14 6/28/09 11:10 PM
10 Yrs old house Soft Copper tubing in attic for fireplace? crichiii Plumbing Inspections 2 6/6/08 6:42 PM
10 Yrs old house Soft Copper tubing in attic for fireplace? crichiii Plumbing Inspections 2 6/6/08 1:23 AM

All times are GMT -4. The time now is 6:43 PM.
no new posts