Direct vent question

I had a direct vent today on a 50 gal State Water heater that I have question on. The vent itself makes more of a loop going up then down and through the wall. The pipe loops up about a foot or so before turning down and exiting out. Will this configuration draft properly? The owners manual was there and I looked through it and it gave clearances and a diagram. It did not specifically caution against doing a loop rather than an elbow. Doing some more research online, most install directions show right angle configurations. I did not see any signs of condensate or corrosion. It was installed in 07.
Any qualified expertise appreciated.
Direct vent.jpg

Direct vent 1.jpg

https://encrypted-tbn1.gstatic.com/images?q=tbn:ANd9GcTJ6jFt3BmdjgKJimiVHqN6fM_4bE1rbAqBfTUdmugf2b7K3bCR

Carson Dunlop says no.

Not only is that loop wrong, but I’m pretty sure that isn’t a flexible b-vent.Did you check?

How it should be

https://encrypted-tbn2.gstatic.com/images?q=tbn:ANd9GcQO3FQ6xDcSW8AG9YK1FoVGXd6pEqMOkcFR_dOQb0yh35OHdD5Y

I’m with Jaun on this one!!

As far as I know a ‘direct vent’ always means that draft is provided by a fan. So this is not a direct vent. And it is totally wrong because of the loop, (no dips allowed) it doesn’t matter if it is B vent or not, that thing could kill somebody.