Old 1/26/11, 7:42 AM
Joshua L. Frederick Joshua L. Frederick is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 4,753
Send a message via AIM to jfrederick
Default Exterior tankless water heater vent clearance

Bosch tankless water heater vent approx. 5' below kitchen window. What's the proper clearance? Safety Concern? (Black vent hood to the right of AC unit).

Thanks in advance.
Attached Thumbnails
Exterior tankless water heater vent clearance-2023-laurelwood-defiance-019-jpg  
Reply With Quote
Need a home inspection in Massachusetts? Check out InterNACHI's listing of Massachusetts certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/26/11, 7:58 AM
Wayne B. Wilson, TN 439's Avatar
Wayne B. Wilson, TN 439 Wayne B. Wilson, TN 439 is online now
Certified Professional Inspector (CPI)
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 19,453
Default Re: Exterior tankless water heater vent clearance

I would not think that would be allowed just because of possible blockage if i am seeing things right.



Wayne Wilson CMI
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490
https://www.myhomeinspection.net/


Reply With Quote
  #3  
Old 1/26/11, 9:10 AM
KEVIN WOOD, CMI KEVIN WOOD, CMI is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,820
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exterior tankless water heater vent clearance

According to the standards of installation. This is not safe and needs to be away from window or the window must be secured or fixed.
I do agree that it can be blocked or even have a barbeque placed in the front. Clearance to windows and doors is generaly 5-6 feet but can be as low as 3 feet according to your authority having the final say.
Reply With Quote
  #4  
Old 1/26/11, 3:04 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,587
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exterior tankless water heater vent clearance

Quote:
Originally Posted by jfrederick View Post
Bosch tankless water heater vent approx. 5' below kitchen window. What's the proper clearance? Safety Concern? (Black vent hood to the right of AC unit).

Thanks in advance.
May be alright for the window but snow may cover the vent in that location.
See: http://www.boschhotwater.com/Portals...ual11_2009.pdf
Reply With Quote
  #5  
Old 1/26/11, 3:45 PM
KEVIN WOOD, CMI KEVIN WOOD, CMI is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,820
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exterior tankless water heater vent clearance

Brian it depends on "Propane or natural gas".
Since we don't know what model it is I exercised caution and picked Propane. Plus I don't care what the installation tells me. I know from experience three to five feet is safe and acceptable by most jurisdictions. This is what I go by.
Reply With Quote
  #6  
Old 1/26/11, 8:26 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,587
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exterior tankless water heater vent clearance

Quote:
Originally Posted by kwood View Post
Brian it depends on "Propane or natural gas".
Since we don't know what model it is I exercised caution and picked Propane. Plus I don't care what the installation tells me. I know from experience three to five feet is safe and acceptable by most jurisdictions. This is what I go by.
I didn't see any distinction made in that sample installation brochure. Why did you indicate there is a difference?
Reply With Quote
  #7  
Old 1/26/11, 10:32 PM
KEVIN WOOD, CMI KEVIN WOOD, CMI is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,820
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exterior tankless water heater vent clearance

Well documented inherent Dangers of Propane over natural gas.
Natural gas is plumbed in by gas techs.
Propane can and is done sometimes by home owners.Sometimes the bottle is put in the basement.This is why we take this into consideration when making recommendations.
The five to six foot rule away from doors and open windows is on the eye of caution only,not a code or rule.Most will allow you to fallow the codes but this does not mean it is a good idea.
Reply With Quote
  #8  
Old 1/26/11, 10:51 PM
Robert Smith Robert Smith is offline
InterNACHI Member
 
Join Date: Jun 2010
Location: Michigan
Posts: 1,259
Default Re: Exterior tankless water heater vent clearance

Anyone think when the AC is running it my hamper proper venting of the WH?




INSPECTIONLOGOS.COM

"I can keep explaining it for you, but I can't understand it for you".
Nick G.
Monroe Home Inspection
Reply With Quote
  #9  
Old 1/27/11, 3:48 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,587
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exterior tankless water heater vent clearance

Quote:
Originally Posted by kwood View Post
Well documented inherent Dangers of Propane over natural gas.
Natural gas is plumbed in by gas techs.
Propane can and is done sometimes by home owners.Sometimes the bottle is put in the basement.This is why we take this into consideration when making recommendations.
The five to six foot rule away from doors and open windows is on the eye of caution only,not a code or rule.Most will allow you to fallow the codes but this does not mean it is a good idea.
Very odd! Not allowed here!

What kind of documentation?

Last edited by Brian A. MacNeish; 1/27/11 at 3:52 AM..
Reply With Quote
  #10  
Old 1/27/11, 7:07 AM
KEVIN WOOD, CMI KEVIN WOOD, CMI is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,820
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exterior tankless water heater vent clearance

Propane is heavy and will sit in pockets in your basement. You cant smell it unless you sniff the floor. It travels quickly with air movement. The installation shows its being installed in the basement.
It can be installed by the homeowner.
The tanks can be played with.
The tank can be installed inside by amature.
CO detectors may be placed too high to be effective.
CO detectors may not be sensitive enough.
If you take any safety training on Propane, natural gas and oil
you can bet your intructors will explain more to you.
All this because you say it can be installed according to code.
Remember as inspectors we don't even mention codes.
How many installers do you know fallow logic and not manufacturer installation?
Just because it says you can have 18 inches clearance from combustibles
will you try to go as close as 18 inches?
Reply With Quote
  #11  
Old 1/27/11, 7:54 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 73,882
Default Re: Exterior tankless water heater vent clearance

Yes propane is heavier that air but that has nothing to do with the question at hand.

And Propane "bottles" are not allowed inside homes here either.



As a Professional Home Inspector, I support the privacy of my clients.

You own your private information. I won't sell or give away yours, others do


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
  #12  
Old 1/27/11, 9:44 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
Certified Master Inspector ®
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 10,454
Default Re: Exterior tankless water heater vent clearance

12 inches (US) 36 inches (Can) according to the manufacturer's document that Brian posted. Clearance requirements for listed appliances will be in the manufacturer's installation documentation. Just make sure you reference the right document for the model installed.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
The Woodlands Home Inspections
Magnolia TX Home Inspections & Thermography


Houston, TX
_______________________
Awards Committee Member

SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #13  
Old 1/31/11, 11:46 PM
Allan Gallatin, #53277 Allan Gallatin, #53277 is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Trail BC
Posts: 193
Default Re: Exterior tankless water heater vent clearance

Quote:
Originally Posted by kwood View Post
Propane is heavy and will sit in pockets in your basement. You cant smell it unless you sniff the floor. It travels quickly with air movement. The installation shows its being installed in the basement.
It can be installed by the homeowner.
The tanks can be played with.
The tank can be installed inside by amature.
CO detectors may be placed too high to be effective.
CO detectors may not be sensitive enough.
If you take any safety training on Propane, natural gas and oil
you can bet your intructors will explain more to you.
All this because you say it can be installed according to code.
Remember as inspectors we don't even mention codes.
How many installers do you know fallow logic and not manufacturer installation?
Just because it says you can have 18 inches clearance from combustibles
will you try to go as close as 18 inches?
Yes , this is for sure ! Has been in many articles years ago when propane was causing homes to blow up due to being heavier than air . It stayed low in the basement and built volume until the furnace pilot light ignited it .



galaxyhomeinspections.com



An amateur built the Ark !
Professionals built the Titanic !
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water heater vent pipe...Question dnasser Inspecting HVAC Systems 4 11/27/10 12:59 PM
Blackened area around water heater vent jfrederick Plumbing Inspections 6 9/29/10 11:59 PM
Site grading and drainage wdevries Canadian Home Inspectors 5 10/6/09 10:23 PM
Hot Water Heater djohnson6 Plumbing Inspections 12 12/28/06 9:18 PM

All times are GMT -4. The time now is 3:51 PM.
no new posts