Question Is flex gas line allowed to run from basement to 2nd floor furnace??

House was built in 2001 - Sewell, NJ (south NJ)

there is a flexible yellow gas line that runs from the basement up to the 2nd floor furnace in the attic

Is this code compliant?? if not now, any way to find out if it was back in 2001?

Any help/info would be greatly appreciated

I am a homeowner, not an inspector---thanks!!

Eric
Reply With Quote
Need a home inspection in Mississippi? Check out InterNACHI's listing of Mississippi certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/2/13, 7:52 PM
Larry Kage, CMI Larry Kage, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: NW, MI
Posts: 16,170
Default Re: Is flex gas line allowed to run from basement to 2nd floor furnace??

It sounds like CSST (Corrugated Stainless Steel Tubing) and if designed, installed and bonded correctly shouldn't be a problem.

http://www.gastite.com/page.php?pg=t...s&idlink=link6




Awards Committee Member
SUBMIT YOUR AWARD NOMINATIONS HERE

The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
____________________________________________

Larry Kage, CMI 2004-2017
State Licensed Builder since 1973
InterNACHI Lifetime Member
~retired~

The above post represents my personal opinion.

Last edited by lkage; 4/2/13 at 7:56 PM..
Reply With Quote
  #3  
Old 4/2/13, 9:44 PM
Eric Flocco Eric Flocco is offline
New User
 
Join Date: Apr 2013
Posts: 6
Please Note: Eric Flocco is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is flex gas line allowed to run from basement to 2nd floor furnace??

Thank you Mr. Cage for the reply and the link - very helpful

Eric
Reply With Quote
  #4  
Old 4/2/13, 10:00 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
Certified Professional Inspector (CPI)
 
Join Date: Aug 2006
Location: Chicago
Posts: 37,435
Default Re: Is flex gas line allowed to run from basement to 2nd floor furnace??

Read what Larry gave you and make sure it is bonded.
Reply With Quote
  #5  
Old 4/2/13, 10:08 PM
Gary Farnsworth, CMI's Avatar
Gary Farnsworth, CMI Gary Farnsworth, CMI is offline
Certified Master Inspector
 
Join Date: Mar 2008
Location: Olathe, KS
Posts: 6,179
Default Re: Is flex gas line allowed to run from basement to 2nd floor furnace??

Check local codes. Here, it cannot run through a wall. That is for solid black pipe.



Certified Master Inspector, Retired
Formerly Serving the Greater Kansas City Metro Area
Lifetime InterNACHI Member
"If opportunity doesn't knock, build a door"--Milton Berle
Reply With Quote
  #6  
Old 4/2/13, 10:22 PM
Jamin M. Jones's Avatar
Jamin M. Jones Jamin M. Jones is offline
InterNACHI Member
 
Join Date: Jun 2012
Posts: 138
Default Is flex gas line allowed to run from basement to 2nd floor furnace??

It's called "Trac Pipe" and was very common until maybe 2009 They now use a black product called "Counterstrike" here is the guide for the yellow stuff. Should have all detail and installation factoids you want. http://www.tracpipe.co.za/DIGuide.pdf
Reply With Quote
  #7  
Old 4/2/13, 10:24 PM
Jamin M. Jones's Avatar
Jamin M. Jones Jamin M. Jones is offline
InterNACHI Member
 
Join Date: Jun 2012
Posts: 138
Default Is flex gas line allowed to run from basement to 2nd floor furnace??

The yellow had some sort of lighting strike issue if not grounded properly.
Reply With Quote
  #8  
Old 4/2/13, 10:27 PM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
Certified Master Inspector
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 14,558
Default Re: Is flex gas line allowed to run from basement to 2nd floor furnace??

Quote:
Originally Posted by gfarnsworth View Post
Check local codes. Here, it cannot run through a wall. That is for solid black pipe.
CSST can run through walls, just like black pipe.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE «
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 4/3/13, 12:04 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
Certified Professional Inspector (CPI)
 
Join Date: Aug 2006
Location: Chicago
Posts: 37,435
Default Re: Is flex gas line allowed to run from basement to 2nd floor furnace??

Great stuff.
When it runs behind your living room wall no anchors are needed.

Just drywall screw it in and the screw self seals it.

If burglers enter you just yank the screw and light a match and have fun watching them run.

lol seriously though it never caught on real big here and I am glad of it.
Reply With Quote
  #10  
Old 4/3/13, 11:39 AM
Eric Flocco Eric Flocco is offline
New User
 
Join Date: Apr 2013
Posts: 6
Please Note: Eric Flocco is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is flex gas line allowed to run from basement to 2nd floor furnace??

Thanks again for all the input - i spoke with the local inspector who confirmed it was installed to code

can't thank you all enough for helping - great site!!

Eric
Reply With Quote
  #11  
Old 4/3/13, 1:32 PM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 70,366
Default Re: Is flex gas line allowed to run from basement to 2nd floor furnace??

Quote:
Originally Posted by gfarnsworth View Post
Check local codes. Here, it cannot run through a wall. That is for solid black pipe.
Also, no fittings are allowed to be concealed for ANY type of gas pipe in my area even when the fitting is rated for concealment.

Don't ask how I know.



As a Professional Home Inspector, I support the privacy of my clients.



www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
  #12  
Old 4/3/13, 1:36 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
Certified Professional Inspector (CPI)
 
Join Date: Aug 2006
Location: Chicago
Posts: 37,435
Default Re: Is flex gas line allowed to run from basement to 2nd floor furnace??

Quote:
Originally Posted by mlarson View Post
Also, no fittings are allowed to be concealed for ANY type of gas pipe in my area even when the fitting is rated for concealment.

Don't ask how I know.
I assume you mean flex as it would need to have allowances for regular elbows and tee's.
Reply With Quote
  #13  
Old 4/3/13, 1:57 PM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 70,366
Default Re: Is flex gas line allowed to run from basement to 2nd floor furnace??

Quote:
Originally Posted by belliott View Post
I assume you mean flex as it would need to have allowances for regular elbows and tee's.
When I said ANY, I meant it.

From my local AHJ.



As a Professional Home Inspector, I support the privacy of my clients.



www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
Need a home inspection in Mississippi? Check out InterNACHI's listing of Mississippi certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 4/3/13, 3:06 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
Certified Professional Inspector (CPI)
 
Join Date: Aug 2006
Location: Chicago
Posts: 37,435
Default Re: Is flex gas line allowed to run from basement to 2nd floor furnace??

Quote:
Originally Posted by mlarson View Post
When I said ANY, I meant it.

From my local AHJ.
So when they pipe high rises they find 20 story long pipe...
Must be some pretty bad az plumbers up north.
Reply With Quote
  #15  
Old 4/3/13, 3:07 PM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 70,366
Default Re: Is flex gas line allowed to run from basement to 2nd floor furnace??

Quote:
Originally Posted by belliott View Post
So when they pipe high rises they find 20 story long pipe...
Must be some pretty bad az plumbers up north.
Listen, I think my AHJ is wrong that doesn't mean I can ignore what he says.



As a Professional Home Inspector, I support the privacy of my clients.



www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gas flex line in crawl space Richard Seay Plumbing Inspections 19 8/12/08 8:12 PM
Basement Bathroom Venting Question Sean M. Jeric Plumbing Inspections 4 3/20/07 11:56 PM
Exposed Flex Gas Line jfunderburk Plumbing Inspections 20 5/11/06 1:44 AM
TPRV line and condensate line marriage ccarrington Plumbing Inspections 3 4/29/06 7:59 AM

All times are GMT -4. The time now is 3:03 PM.
no new posts