Default Gas meter in bedroom?

Never saw this one before, and I can't find any info about it. Are gas meters allowed in bedrooms?
Attached Thumbnails
gas-meter-bedroom-g-meter-bedroom.jpg  
Reply With Quote
Need a home inspection in Georgia? Check out InterNACHI's listing of Georgia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/30/12, 5:43 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 29,164
Default Re: Gas meter in bedroom?

You got to be kidding.
Those people crazy or what? Gas Meters have vents on them, how did it smell?



CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #3  
Old 5/30/12, 5:47 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
Certified Professional Inspector (CPI)
 
Join Date: Aug 2006
Location: Chicago
Posts: 37,435
Default Re: Gas meter in bedroom?

Why not?
Meters are not supposed to leak.

If it was a gas using appliance that would be different however if it was leaking it would effect the entire home not just the bedroom.

Here is Peoples gas code though you may wish to check local..

Meter Installation Requirements
Peoples Energy recommends that meters supplied from medium
pressure service pipes be installed outside of the building.
For medium-pressure areas in Chicago, service regulators shall
be installed. Peoples Energy’s practice is to install both the
regulators and meters outside of the structure. An outside
installation makes it easier for Peoples Energy to maintain meters
and regulators while freeing up interior space for customer use.
Gas meters shall be located:
1. In a ventilated and readily accessible area.
2. At least 3’ from sources of ignition (including electrical circuit
breaker boxes, meters, and receptacles) or any sources of
heat that may damage the meter for inside installations.
3. A minimum of 12” above ground for outside meter installations.
(See Figure 3 on Page 8.)
4. Away from obstructions, such as downspouts and windows.
Meters will be installed only after the following:
1. All inside piping (house piping and building service pipe)
has been pressure tested for tightness and approved by Peoples
Energy field service personnel.
2. House piping is properly supported, sized, and capped (or
plugged), and floor (or unit) locations are identified.
Gas meters will not be installed in these instances:
1. In locations that interfere with pedestrian or vehicular traffic
flow.
2. Under an interior stairway that is the sole exit or is designated
as an emergency exit.
3. Under fire escapes.
4. Directly above or below an operable window.
5. Higher than 7’ to ensure meters can be easily read and
maintained. (See Figure 23 on Page 53.)
6. In a space occupied by another owner or tenant
Reply With Quote
  #4  
Old 5/30/12, 5:48 PM
Marcel Gratton, CMI's Avatar
Marcel Gratton, CMI Marcel Gratton, CMI is offline
Certified Master Inspector ®
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 4,197
Default Re: Gas meter in bedroom?

It is being discussed at: http://www.inspectionnews.net/home_i...s-bedroom.html



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #5  
Old 5/30/12, 6:11 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,353
Please Note: bsmith is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas meter in bedroom?

Marcel - that discussion is dealing more with the fact that the bedroom itself is illegal. No smell from the gas meter, but the laundry hamper was ripe LOL!!!
Reply With Quote
  #6  
Old 5/30/12, 6:12 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,353
Please Note: bsmith is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas meter in bedroom?

Bob - I couldn't find a reason why it shouldn't be there, but it still doesn't seem right.
Reply With Quote
  #7  
Old 5/30/12, 6:18 PM
Michael Larson's Avatar
Michael Larson Michael Larson is online now
Certified Professional Inspector (CPI)
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 70,366
Default Re: Gas meter in bedroom?

Quote:
Originally Posted by bsmith View Post
Bob - I couldn't find a reason why it shouldn't be there, but it still doesn't seem right.
It should at least be vented to the exterior.

The local gas provider likely has specific requirements for meters located in doors.



As a Professional Home Inspector, I support the privacy of my clients.



www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Call me


Reply With Quote
  #8  
Old 5/30/12, 6:27 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 29,164
Default Re: Gas meter in bedroom?

Doesn't this say it all?

Gas meters shall be located:

1. In a ventilated and readily accessible area.
2. At least 3’ from sources of ignition (including electrical circuit
breaker boxes, meters, and receptacles) or any sources of
heat that may damage the meter for inside installations.
3. A minimum of 12” above ground for outside meter installations.
(See Figure 3 on Page 8.)
4. Away from obstructions, such as downspouts and windows.
Meters will be installed only after the following:
1. All inside piping (house piping and building service pipe)
has been pressure tested for tightness and approved by Peoples
Energy field service personnel.
2. House piping is properly supported, sized, and capped (or
plugged), and floor (or unit) locations are identified.

Gas meters will not be installed in these instances:
1. In locations that interfere with pedestrian or vehicular traffic
flow.
2. Under an interior stairway that is the sole exit or is designated
as an emergency exit.
3. Under fire escapes.
4. Directly above or below an operable window.
5. Higher than 7’ to ensure meters can be easily read and
maintained. (See Figure 23 on Page 53.)
6. In a space occupied by another owner or tenant




Gas regulators can leak gas when there are spikes in pressure.



CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.

Last edited by mcyr; 5/30/12 at 6:48 PM..
Reply With Quote
  #9  
Old 5/30/12, 7:18 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
Certified Professional Inspector (CPI)
 
Join Date: Aug 2006
Location: Chicago
Posts: 37,435
Default Re: Gas meter in bedroom?

I see meters in homes all the time and mine is in the home also.
They read remotely.

Check local codes for more.
Marcel the last part about owner or tenant I take to mean because of access.
Reply With Quote
  #10  
Old 5/30/12, 7:30 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 29,164
Default Re: Gas meter in bedroom?

I would write them up if seen inside.



CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #11  
Old 5/30/12, 7:50 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,353
Please Note: bsmith is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas meter in bedroom?

Fairly common to see them inside in this area, just not in a bedroom.
Reply With Quote
  #12  
Old 5/30/12, 7:52 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 29,164
Default Re: Gas meter in bedroom?

Not up here.



CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #13  
Old 5/30/12, 8:00 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 29,164
Default Re: Gas meter in bedroom?

Never stopped to think about some meters not having the regulator at hand on top of it.

I guess it is legal as long as the regulator is remote.

§ 192.353 Customer meters and regulators: Location.

(a) Each meter and service regulator, whether inside or outside a building, must be installed in a readily accessible location and be protected from corrosion and other damage, including, if installed outside a building, vehicular damage that may be anticipated. However, the upstream regulator in a series may be buried.

(b) Each service regulator installed within a building must be located as near as practical to the point of service line entrance.

(c) Each meter installed within a building must be located in a ventilated place and not less than 3 feet (914 millimeters) from any source of ignition or any source of heat which might damage the meter.

(d) Where feasible, the upstream regulator in a series must be located outside the building, unless it is located in a separate metering or regulating building.



CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
Need a home inspection in Georgia? Check out InterNACHI's listing of Georgia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 5/30/12, 8:07 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 29,164
Default Re: Gas meter in bedroom?

http://search.yahoo.com/r/_ylt=A0oG7...nStandards.pdf

4.3.2.1 An inside meter set assembly must be located as near as practical to the point where the
service line enters the building.
(A) The meter set assembly must not be installed in unventilated or confined space; it must
always be readily accessible.




CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers.
Reply With Quote
  #15  
Old 5/30/12, 8:15 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
Certified Professional Inspector (CPI)
 
Join Date: Aug 2006
Location: Chicago
Posts: 37,435
Default Re: Gas meter in bedroom?

Most common I see in many homes (50's/60"s ) is walled off with hatch (similar to picture) with glass bock and facing the gangway for the meter reader.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
gas meter dyoung General Inspection Discussion 20 3/1/10 3:25 PM
Gas Meter dyoung AskNACHI.org Inspection Questions Forum 7 2/25/10 9:06 PM
CPSC -----> Recall on electric meter panels pbolliger Electrical Inspections 0 10/15/09 11:23 PM

All times are GMT -4. The time now is 3:00 PM.
no new posts