Talking Hydrostatic Pressure Test

Currently I'm working under a 600mm pipe laying project in Middle East. We had finished the pipe laying work and now come to the final stage of the work.

Previously we have done and passed the 1st pressure test along the pipe laying sections. As per requested by the authority, we need to complete another pressure test (9 Bars) by testing the whole pipe length before we can divert the water supply to the new laid pipe.

We have tuned the pressure to 9 bars and maintained for 24 hours. However the pressure was dropped to 7 bars and extra 400 liters of water was pump into the water pipe. The pressure test was failed but we could not locate any leakage along the pipeline.

Information for my pipeline:

Pipe Diameter : 600mm Ductile Iron Pipe
Pipe Length : 1500m
Pressure : 9 Bars
Allowable water tolerance : 180 liter/km/24hrs
Highest Elevation : 41.225m
Lowest Elevation : 34.384m
Pressure Gauge : 37.781m (End of pipeline)
Valve Chamber : 2 nos. Air Valve, 2 nos. Washout Valve, 2 nos. Butterfly Valve

My subcontractor had fixed the pressure gauge at the end point of the pipe instead of the lowest point. Thus I'm seeking help here since this is the first pipe laying project for me. Kindly provide me any advice or guidelines before I redo or conduct the pressure test.

For the second pressure test, the specification is almost the same except,

Pipe Length : 19000m (approx.)
Highest Elevation : 49.368m
Lowest Elevation : 30.749m
Valve Chamber : Total 42 nos. 15 nos Air Valve, 16 nos Wash Out Valve, 11 nos Butterfly Valve.

Thanks for your time and help.
Reply With Quote
  #2  
Old 6/5/07, 12:00 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 17,178
Default Re: Hydrostatic Pressure Test

You lost 7 bars of pressure and 400 litres of water? You have a leak.
Reply With Quote
  #3  
Old 6/5/07, 1:31 PM
Paul Sabados Paul Sabados is offline
Active Poster
 
Join Date: Sep 2003
Location: Olathe, KS
Posts: 2,186
Please Note: psabados is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hydrostatic Pressure Test

Big project. 24 inch pipe almost a mile long 4920' Volume lost about a 105 gallons and a pressure drop of 29 psi. Not exactly a home project with a one inch supply line.

Sounds like a trap or a bubble around one of the valves. Poor purge of the line before the test. Did anyone do a volume calculation and a metering of the water placed into the line?

Paul
Reply With Quote
  #4  
Old 6/5/07, 1:49 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 17,178
Default Re: Hydrostatic Pressure Test

Ah my mistake 2 bar loss, but with that amount of water added I still vote leak. Check the valves again, packing and any test plates. Is the line under test attached to an existing line at any point?
Reply With Quote
  #5  
Old 6/5/07, 2:10 PM
Paul Sabados Paul Sabados is offline
Active Poster
 
Join Date: Sep 2003
Location: Olathe, KS
Posts: 2,186
Please Note: psabados is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hydrostatic Pressure Test

Wow, that a volume of about 115,500 gallons of water. Loss of product was about 1/10 of 1 %. One single leak at that rate would create a loss around 0.072 gpm. or 9 ozs a minute. What also is not in the equation is water temperature, what temp was the water at at the start and what was the final temp, expansion and contraction. We're just assuming standard temp and pressure through out the test. Middle east location hot days cold nights.

No leak, someone messing around At the top of the thread
Reply With Quote
  #6  
Old 6/5/07, 2:37 PM
Peter G. Siposs Peter G. Siposs is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Liberty Lake, WA
Posts: 243
Send a message via Yahoo to psiposs
Default Re: Hydrostatic Pressure Test

I agree with the temperature change. This would allow for a pressure difference in that massive amount of area.
Need data before and after.



Peter Siposs
Absolute Home Inspections
Home, Mold, IAQ, Radon, & Lead Based Paint
Liberty Lake, WA
Serving Eastern WA & Northern ID
Nachi# 05100181
peter@absolute-home-inspections.com
Reply With Quote
  #7  
Old 6/5/07, 2:45 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 17,178
Default Re: Hydrostatic Pressure Test

And the percentage of pressure loss is?
Reply With Quote
  #8  
Old 6/5/07, 2:50 PM
Paul Sabados Paul Sabados is offline
Active Poster
 
Join Date: Sep 2003
Location: Olathe, KS
Posts: 2,186
Please Note: psabados is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hydrostatic Pressure Test

About the same as the amount of gas expelled from a belch after chugging a 6 pack of beer
Reply With Quote
  #9  
Old 6/5/07, 2:55 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 17,178
Default Re: Hydrostatic Pressure Test


The thermal coefficient of expansion of water is 0.00021 per 1░ Celsius at 20░ Celsius.

Last edited by bkelly2; 6/5/07 at 2:59 PM..
Reply With Quote
  #10  
Old 6/5/07, 3:58 PM
Edward D. Wend Edward D. Wend is offline
New User
 
Join Date: Jun 2007
Posts: 2
Please Note: Edward D. Wend is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hydrostatic Pressure Test

There is no record for temperature. However the ambient temperature is between 39-41░ Celsius. Most of the pipeline is backfilled and covered except the valve chamber areas. No leakage of the water in the previous tests (tested between chamber). Thus, we had inspected the connection between the valve chamber and water pipe. However there is no sign of water leakage.

In order to find out the possible leakage point, we had re-adjusted the pressure back to the 9 Bars. Two readings were taken at both ends of the water pipeline. One of butterfly at the middle of the pipeline was closed. From this, we hope that we can narrow down the search for the leakage.


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
water pressure test msaxton Plumbing Inspections 28 11/30/16 10:05 PM
Moisture in slabs mcyr Structural Inspections 7 8/20/07 7:33 PM
bbbb mcyr Structural Inspections 1 8/19/07 10:26 PM
air pressure test vs. hydrostatic pressure mcyr Plumbing Inspections 22 7/11/06 6:11 PM

All times are GMT -4. The time now is 1:47 PM.
no new posts