  #1  
Old 10/31/12, 11:07 PM
Joseph Hagarty, CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty, CMI is offline
Certified Master Inspector
 
Join Date: Jan 2003
Location: Boulder, Colorado
Posts: 7,417
Default Main Water Shutoff

Access could not initially be found....
(behind wall kmounted TV)

Access provided for one valve only...
not the check valve, meter or regulator....

Is there a minimum requirement for access to Plumbing isolation?
Attached Files
File Type: pdf 5 x 7 in.pdf (92.1 KB, 752 views)



Joe Hagarty
mrdryervent@gmail.com

Cell: (484) 883-7018
InterNACHI
Boulder, Colorado

National President / NACHI (2003-2004)
NACHI Education Committee Member
Certified CMI Master Inspector Instructor
PA NACHI Certified Inspector # 01102902
PA Licensed Radon Inspector # 2080
PA Licensed Pesticide Applicator # 700884
Delaware Licensed Home Inspector # H4-071
Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/1/12, 8:07 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2004
Location: this side of Texas dirt, another successful day
Posts: 4,512
Default Re: Main Water Shutoff

disguising decorator

if the occupant remembers the location when needed it's a non-issue

i routinely find a variety of occupants crap blocking all types of system access elec panels, wh, hvac etc...

report whatever was/wasn't inspected/accessed/operated and move on



badair

ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

National Association of Commercial Building Inspectors & Thermographers™ Member ID 12011-14TX

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #3  
Old 11/1/12, 2:31 PM
Joseph Hagarty, CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty, CMI is offline
Certified Master Inspector
 
Join Date: Jan 2003
Location: Boulder, Colorado
Posts: 7,417
Default Re: Main Water Shutoff

Quote:
Originally Posted by badair View Post
disguising decorator

if the occupant remembers the location when needed it's a non-issue

i routinely find a variety of occupants crap blocking all types of system access elec panels, wh, hvac etc...

report whatever was/wasn't inspected/accessed/operated and move on
Huh??

Question is:
Is there a minimum (code) requirement for access to Plumbing isolation?
or..
is access to service / operate plumbing isolation valves provided merely as a courtesy with no code requirement...?



Joe Hagarty
mrdryervent@gmail.com

Cell: (484) 883-7018
InterNACHI
Boulder, Colorado

National President / NACHI (2003-2004)
NACHI Education Committee Member
Certified CMI Master Inspector Instructor
PA NACHI Certified Inspector # 01102902
PA Licensed Radon Inspector # 2080
PA Licensed Pesticide Applicator # 700884
Delaware Licensed Home Inspector # H4-071
Reply With Quote
  #4  
Old 11/1/12, 11:15 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
Certified Professional Inspector (CPI)
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 10,106
Default Re: Main Water Shutoff

Okla only requires to Id the location of the shut off and or absence of your milage may vary

Could of found it with the Ir Camera



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
Okla State License # 130
580-268-3340
Reply With Quote
  #5  
Old 11/2/12, 4:15 AM
Joseph Hagarty, CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty, CMI is offline
Certified Master Inspector
 
Join Date: Jan 2003
Location: Boulder, Colorado
Posts: 7,417
Default Re: Main Water Shutoff

Quote:
Originally Posted by cbottger View Post
Could of found it with the Ir Camera
Yes,
but the Homeowner was not willing to pay for that.
(We do not offer additional services for FREE)



Joe Hagarty
mrdryervent@gmail.com

Cell: (484) 883-7018
InterNACHI
Boulder, Colorado

National President / NACHI (2003-2004)
NACHI Education Committee Member
Certified CMI Master Inspector Instructor
PA NACHI Certified Inspector # 01102902
PA Licensed Radon Inspector # 2080
PA Licensed Pesticide Applicator # 700884
Delaware Licensed Home Inspector # H4-071
Reply With Quote
  #6  
Old 11/2/12, 7:59 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
Certified Professional Inspector (CPI)
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 10,106
Default Re: Main Water Shutoff

Quote:
Originally Posted by jhagarty View Post
Yes,
but the Homeowner was not willing to pay for that.
(We do not offer additional services for FREE)
Do you charge extra for placing a thermometer in the oven. IR is just another tool some people understand marketing and some don't. For being on the education committee your education has a hole in it



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
Okla State License # 130
580-268-3340
Reply With Quote
  #7  
Old 11/2/12, 6:26 PM
Joseph Hagarty, CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty, CMI is offline
Certified Master Inspector
 
Join Date: Jan 2003
Location: Boulder, Colorado
Posts: 7,417
Default Re: Main Water Shutoff

The question seems to be lost...

I am inspecting for Buyer...
Seller hired a Contractor 5 Years ago to finish basement...
Permits were pulled and Inspections were completed...
When I asked the Homeowner where the Access to the Water Main and Sewer Cleanout were, no access and no idea where they are located...
He called the Contractor...
... suggestion is that access is not required...

so back to the original question....
are isolation valves and cleanouts required by code to be readily accessible...
or may they be concealed...?



Joe Hagarty
mrdryervent@gmail.com

Cell: (484) 883-7018
InterNACHI
Boulder, Colorado

National President / NACHI (2003-2004)
NACHI Education Committee Member
Certified CMI Master Inspector Instructor
PA NACHI Certified Inspector # 01102902
PA Licensed Radon Inspector # 2080
PA Licensed Pesticide Applicator # 700884
Delaware Licensed Home Inspector # H4-071
Reply With Quote
  #8  
Old 11/2/12, 8:21 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2004
Location: this side of Texas dirt, another successful day
Posts: 4,512
Default Re: Main Water Shutoff

no code required for a general home inspector

"all main utility electric, gas and water shut offs/disconnects shall be readily accessible"

many munis with locked smart meters are going to:
It is a homeowner’s responsibility to install and maintain a separate water cut-off valve, and it is highly recommended that you know where your home’s water shut-off valve is located for quick and easy access when needed. The water shut-off valve is generally located between the City’s water meter box and the front of your home, sometimes directly beside the water meter box or adjacent to the home.

It is also important to check that the water meter box and water shut-off valve are separate because the City of xyz is gradually implementing a new automated water meter reading system that requires locked water meter lids.


a provided access panel within the subject property as depicted would meet this requirement



badair

ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

National Association of Commercial Building Inspectors & Thermographers™ Member ID 12011-14TX

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #9  
Old 11/2/12, 10:17 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
Certified Professional Inspector (CPI)
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 10,106
Default Re: Main Water Shutoff

Sorry just call me Mikie

Okla does require shut off valves by state requirements on gas and water I can not image Pa not doing the same but stranger things have happed



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
Okla State License # 130
580-268-3340
Reply With Quote
  #10  
Old 11/2/12, 10:33 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
Certified Professional Inspector (CPI)
 
Join Date: Aug 2006
Location: Chicago
Posts: 37,435
Default Re: Main Water Shutoff

Around here some do not have a main shutoff in the home with access through a Buffalo key at the street.
Water meters must be requested or they estimate your bill.
Reply With Quote
  #11  
Old 11/2/12, 10:34 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2004
Location: this side of Texas dirt, another successful day
Posts: 4,512
Default Re: Main Water Shutoff

Quote:
Originally Posted by cbottger View Post
stranger things have happened
the "Dirty Dozen" have proof and memories you've been involved ;~)



badair

ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

National Association of Commercial Building Inspectors & Thermographers™ Member ID 12011-14TX

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #12  
Old 11/2/12, 10:35 PM
Joseph Hagarty, CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty, CMI is offline
Certified Master Inspector
 
Join Date: Jan 2003
Location: Boulder, Colorado
Posts: 7,417
Default Re: Main Water Shutoff

I have kicked the question back to the Municipal Inspector...
He issued the Permit...
He Inspected the Work....
and Signed Off on the Completion...

It is what it is now......



Joe Hagarty
mrdryervent@gmail.com

Cell: (484) 883-7018
InterNACHI
Boulder, Colorado

National President / NACHI (2003-2004)
NACHI Education Committee Member
Certified CMI Master Inspector Instructor
PA NACHI Certified Inspector # 01102902
PA Licensed Radon Inspector # 2080
PA Licensed Pesticide Applicator # 700884
Delaware Licensed Home Inspector # H4-071
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What might cause this many cracks? bhamilton Structural Inspections 18 4/24/15 7:19 AM
Site grading and drainage wdevries Canadian Home Inspectors 5 10/6/09 10:23 PM
Need Help On Chimney Liners Nick Scibetta Exterior Inspections 13 1/11/06 9:53 PM

All times are GMT -4. The time now is 2:53 PM.
no new posts