Default Water Heater gas issue

Each time I would crank up the temperature for the water heater to come on I could smell gas. I placed my meter near the heater exhaust and it confirmed the presence of either carbon monoxide or natural gas. Within a minute it was fine. I also placed a smoke stick near the heater exhaust and it would blow away from the vent at the start up, but again within a minute would start venting properly.
I'm not sure what is causing this??

16 yr old natural gas water heater
No flame rollout on startup
furnace venting is attached below the water heater venting
furnace/water heater exhaust vent is above 2ft of roof surface, with no cause for backdraft

What am I missing?

water-heater-gas-issue-100_7066.jpg
Reply With Quote
Need a home inspection in New York? Check out InterNACHI's listing of New York certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/5/12, 11:21 AM
David A. Andersen, TN HI# 40's Avatar
David A. Andersen, TN HI# 40 David A. Andersen, TN HI# 40 is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Jun 2005
Location: Nashville, TN
Posts: 10,238
Default Re: Water Heater gas issue

That is acceptable.

Guess you should look that one up so you can test these things correctly.



"working together to get-IR-done" Chris Walsh
Bracebridge, Ontario:


David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #3  
Old 12/5/12, 11:37 AM
Juan C. Jimenez Juan C. Jimenez is offline
Certified Professional Inspector (CPI)
 
Join Date: Jan 2012
Location: central va
Posts: 7,682
Default Re: Water Heater gas issue

I'll take a stab at it.

It may be caused by the cold air at the top of the flue. Hot air rises and cold air sinks. When the exhaust first starts venting, it meets with the cold air coming down which would cause the initial backdraft. As soon as it warms up, it drafts properly. I would not be concerned.



Juan Jimenez
A House on a Rock Home Inspections LLC
God. Family. Home.
804-269-4321
Richmond Home Inspector
Richmond Chimney Sweep
Richmond Radon Testing



Last edited by jjimenez; 12/5/12 at 11:41 AM..
Reply With Quote
  #4  
Old 12/5/12, 1:37 PM
Greg W. Mathias, CCHI, CMI's Avatar
Greg W. Mathias, CCHI, CMI Greg W. Mathias, CCHI, CMI is offline
Certified Master Inspector ®
 
Join Date: May 2010
Location: Lloydminster,Ab
Posts: 3,267
Default Re: Water Heater gas issue

There will always be a little smell when they start up. a small delay from when the gas is pushed into the burner to when the pilot ignites it. Sometimes the pilot need to be moved over or the flame increased if there is significant delay. As for the off gases rolling out, it takes a minute for the flue to get hot and a positive draft to start pulling it up the chimney. Very normal operation. You should take a couple of HVAC courses on NACHI to learn more about it as David said. The more you learn the better inspector you become. I have taken some of the courses a second time because there is no way to get it all the first time round.



Greg Mathias, CCHI
Journeyman Carpenter
Level I Thermographer
Certified Master Inspector
Global Property Inspections
(780)205-9912
Reply With Quote
  #5  
Old 12/5/12, 3:37 PM
Jim Horton's Avatar
Jim Horton Jim Horton is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2004
Location: Kokomo, IN
Posts: 535
Default Re: Water Heater gas issue

Thanks guys but maybe I should have stated "I/we could smell an excessive amount of gas", as in not a normal start up. The customer and I were approximately 4' away. It first made me think the water heater vent was semi-clogged. Thus taking longer for the cool air to heat up to perform as normal.
I've not timed the start up process in the past, but this one seems to take 3 times longer plus the excessive smell. This is a SHORT straight run with one elbow.!?

The house is 16 years old and so is the water heater. The water heater is in the garage in what appears to be a newer utility closet along with the furnace. The water heater is sitting on two cinder blocks. This was the first clue that this may have been recently remolded. The dwelling has only been vacant for about a month. There are two other vents currently not being used....
????
water-heater-gas-issue-100_7065.jpg
Reply With Quote
  #6  
Old 12/5/12, 3:49 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
Certified Professional Inspector (CPI)
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 25,989
Default Re: Water Heater gas issue

Quote:
Originally Posted by jhorton1 View Post
Thanks guys but maybe I should have stated "I/we could smell an excessive amount of gas", as in not a normal start up. The customer and I were approximately 4' away. It first made me think the water heater vent was semi-clogged. Thus taking longer for the cool air to heat up to perform as normal.
I've not timed the start up process in the past, but this one seems to take 3 times longer plus the excessive smell. This is a SHORT straight run with one elbow.!?

The house is 16 years old and so is the water heater. The water heater is in the garage in what appears to be a newer utility closet along with the furnace. The water heater is sitting on two cinder blocks. This was the first clue that this may have been recently remolded. The dwelling has only been vacant for about a month. There are two other vents currently not being used....
????
Attachment 60806
Water heater is past its normal life I would budget for Immediate replacement .
Reply With Quote
  #7  
Old 12/5/12, 4:43 PM
Greg W. Mathias, CCHI, CMI's Avatar
Greg W. Mathias, CCHI, CMI Greg W. Mathias, CCHI, CMI is offline
Certified Master Inspector ®
 
Join Date: May 2010
Location: Lloydminster,Ab
Posts: 3,267
Default Re: Water Heater gas issue

I guess the best advice I can give without being there would be to write it up as you just wrote and call for the gas fitter/plumber.



Greg Mathias, CCHI
Journeyman Carpenter
Level I Thermographer
Certified Master Inspector
Global Property Inspections
(780)205-9912
Reply With Quote
  #8  
Old 12/5/12, 4:59 PM
Jim Horton's Avatar
Jim Horton Jim Horton is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2004
Location: Kokomo, IN
Posts: 535
Default Re: Water Heater gas issue

Quote:
Originally Posted by gmathias1 View Post
I guess the best advice I can give without being there would be to write it up as you just wrote and call for the gas fitter/plumber.

Thanks Greg, I'm sure your familiar with something that just bugs ya and ya just can't come up the the right answer or explanation. That's what this is to me....I know what's suppose to happen but????

So far I wrote it up for the block it sits on, which is not a perminate stable foundation for this appliance.
Reply With Quote
  #9  
Old 12/5/12, 5:09 PM
Greg W. Mathias, CCHI, CMI's Avatar
Greg W. Mathias, CCHI, CMI Greg W. Mathias, CCHI, CMI is offline
Certified Master Inspector ®
 
Join Date: May 2010
Location: Lloydminster,Ab
Posts: 3,267
Default Re: Water Heater gas issue

How did the burner look? Was there a bunch of debris on it? Delayed Ignition can be from a few different things. Bottom line is it is getting a bunch of gas in thier before it ignites. Should have been some roll out if the smell is that strong. As for the delayed draft I cannot figure that one out except what I said in my previous post. You may be on the right track. I did some training a year ago on a cracked heat exchanger and that was one of the issues. A delay of 15-20 seconds before the draft would start.



Greg Mathias, CCHI
Journeyman Carpenter
Level I Thermographer
Certified Master Inspector
Global Property Inspections
(780)205-9912
Reply With Quote
  #10  
Old 12/5/12, 5:19 PM
Jim Horton's Avatar
Jim Horton Jim Horton is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2004
Location: Kokomo, IN
Posts: 535
Default Re: Water Heater gas issue

Quote:
Originally Posted by gmathias1 View Post
How did the burner look? Was there a bunch of debris on it? Delayed Ignition can be from a few different things. Bottom line is it is getting a bunch of gas in thier before it ignites. Should have been some roll out if the smell is that strong. As for the delayed draft I cannot figure that one out except what I said in my previous post. You may be on the right track. I did some training a year ago on a cracked heat exchanger and that was one of the issues. A delay of 15-20 seconds before the draft would start.

I was not able to get a good close look due to the water filtration system in front of the water heater(see pic above). I did the best I could with my mirror, but you might as well say I didn't see anything because of my poor eye site.
Reply With Quote
  #11  
Old 12/5/12, 5:37 PM
Greg W. Mathias, CCHI, CMI's Avatar
Greg W. Mathias, CCHI, CMI Greg W. Mathias, CCHI, CMI is offline
Certified Master Inspector ®
 
Join Date: May 2010
Location: Lloydminster,Ab
Posts: 3,267
Default Re: Water Heater gas issue

Without being able to see the burner it can make it tough to diagnos. I think we need Charley on this one.



Greg Mathias, CCHI
Journeyman Carpenter
Level I Thermographer
Certified Master Inspector
Global Property Inspections
(780)205-9912
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dual Water Heaters - parallel or series gmelien Plumbing Inspections 25 9/27/17 10:51 AM
Analyze this Home Inspection california buyer General Inspection Discussion 20 10/18/12 9:25 AM
hydronic radiant floor heat on hot water tanks mnicholet Plumbing Inspections 7 4/14/10 5:48 PM
Weird water heater problem kweiss Plumbing Inspections 3 4/5/09 6:34 PM

All times are GMT -4. The time now is 2:00 AM.
no new posts