Default Insulation requirements question

There is 2x10 for rafter material being used. In the northern states r-38 is required in ceilings, how would you insulate the rafters if it was a vaulted ceiling (meaning they want to attach drywall directly to the rafters for a sloped ceiling) 2x10 measures 9 1/2" in depth, what materials would you use to acheive the r-38 requirments and yet have the 1" air gap against the roof deck sheating???

Ridge insulation then batts of some sort?????????????????
Reply With Quote
  #2  
Old 3/27/07, 10:24 AM
Paul Hinsperger, CMI's Avatar
Paul Hinsperger, CMI Paul Hinsperger, CMI is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,793
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation requirements question

Yes. That's one way. Working from the underside of the roof deck;- staple up your vents,- then put up the batts in between the rafters- then put up rigid foam insulation sheets covering both the batts and the rafters- then drywall.It will perform better because of the thermal bridge break. If you are diligent in sealing up the seams of the foam sheets it will also provide as a very good vapor barrier.
Reply With Quote
  #3  
Old 3/27/07, 3:33 PM
brepanshek brepanshek is offline
Active Poster
 
Join Date: May 2006
Location: York, PA
Posts: 234
Please Note: brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation requirements question

How would this give you the required R-38??
Batt insulation (R value ??) + ridge insulation board (R value ??) = R-38
describe the types of insulation materials you would use.
Reply With Quote
  #4  
Old 3/27/07, 5:59 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,199
Default Re: Insulation requirements question

Quote:
Originally Posted by phinsperger
Yes. That's one way. Working from the underside of the roof deck;- staple up your vents,- then put up the batts in between the rafters- then put up rigid foam insulation sheets covering both the batts and the rafters- then drywall.It will perform better because of the thermal bridge break. If you are diligent in sealing up the seams of the foam sheets it will also provide as a very good vapor barrier.
Careful ... because typical batts already has a vapor barrier on the back side of the paper. You don't want a double vapor barrier that may trap moisture.

JMO



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #5  
Old 3/27/07, 6:04 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 31,282
Default Re: Insulation requirements question

Quote:
Originally Posted by brepanshek
How would this give you the required R-38??
Batt insulation (R value ??) + ridge insulation board (R value ??) = R-38
describe the types of insulation materials you would use.
Hi. Brian;

Paul directed you well, he just did not quote you any values.
Maybe I can help you with that.

Once you have installed your baffle vents for continuous venting from soffit to ridge vent, the only comfortable space left for insulation (batt) is 8".

Batt insulation has an R-Value of 3.14 per inch so this would equal 25.12. or a high density would be r- 30.
Required R-Values for roofs in the NorthEast is R-38 38.
Deficit -12.88


Paul recommended Polystyrene, I believe and that is 5.00 p.i. 2" = 10

Polyisocyanurate has an R-Value of 7.20 P. I. 1 &1/2" = 10.8 2"= 14.4

Either one, you would have to strap the ceiling in order to sheetrock, unless one wants to use extra long screws.

Alternatives:

Icceynene Spray foam open cell 3.6 R-Value per inch

Polyurethane Spray foam closed cell 6-7 R-Value per inch

One has more insulating values as well as price.

Hope this helps.

Marcel



CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers and any rules updates.

Last edited by mcyr; 3/27/07 at 7:43 PM..
Reply With Quote
  #6  
Old 3/27/07, 7:13 PM
Larry Kage, CMI's Avatar
Larry Kage, CMI Larry Kage, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: NW, MI
Posts: 18,650
Default Re: Insulation requirements question

Quote:
Originally Posted by mcyr


Once you have installed your baffle vents for continuous venting from soffit to ridge vent, the only comfortable space left for insulation (batt) is 9".


Pssst!...Marcel. 2x10's are 9 1/4", minus 1" for the venting equals 8 1/4"...but you are giving some valuable information.




Awards Committee Officer
SUBMIT YOUR AWARD NOMINATIONS HERE:
http://co.nachi.org/inachiawards/

The InterNACHI Awards Committee is the final authority of the issuance of any award the committee offers and any rules interpretation updates.
____________________________________________

Larry Kage, CMI Lifetime Member
State Licensed Builder since 1973
InterNACHI Lifetime Member
~retired~

The above post represents my personal opinion.
Reply With Quote
  #7  
Old 3/27/07, 7:46 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 31,282
Default Re: Insulation requirements question

Sorry Larry;

Thanks for the warning, just too many numbers in my head I guess.
Corrected my post, hope I got it right this time. ha. ha.


Marcel



CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers and any rules updates.
Reply With Quote
  #8  
Old 3/27/07, 8:05 PM
Larry Kage, CMI's Avatar
Larry Kage, CMI Larry Kage, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: NW, MI
Posts: 18,650
Default Re: Insulation requirements question

Ahhh...no "warning" meant, Marcel...just funnin' ya...

You are a wealth of good info, thanks.




Awards Committee Officer
SUBMIT YOUR AWARD NOMINATIONS HERE:
http://co.nachi.org/inachiawards/

The InterNACHI Awards Committee is the final authority of the issuance of any award the committee offers and any rules interpretation updates.
____________________________________________

Larry Kage, CMI Lifetime Member
State Licensed Builder since 1973
InterNACHI Lifetime Member
~retired~

The above post represents my personal opinion.
Reply With Quote
  #9  
Old 3/27/07, 8:48 PM
Paul Hinsperger, CMI's Avatar
Paul Hinsperger, CMI Paul Hinsperger, CMI is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,793
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation requirements question

You can also use a foil faced ridged foam like Energy Sheild for example. Because the foil reflects radiant heat it adds an effective ~R2.2 to the value of the foam for any given thickness. Mineral wool batts also have a slightly higher R value than fiberglass.

Last edited by phinsperger; 3/27/07 at 8:49 PM.. Reason: typo
Reply With Quote
  #10  
Old 3/28/07, 12:51 AM
Randy L. Thomas Randy L. Thomas is offline
New User
 
Join Date: Mar 2007
Location: Oregon
Posts: 11
Please Note: Randy L. Thomas is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation requirements question

Be aware that the code allows for R-30 (normally batts) for vaulted ceilings and R-38 (normally blown-in) for flat ceilings. The vaulted ceiling allowance is good for up to 50% of the ceiling surface area. Anything over that requires R-38. As mentioned in thread above, if there is inadequate space for conventional insulation, then higher R-value material must be used.
Reply With Quote
  #11  
Old 3/29/07, 7:32 PM
Larry Ewens, C.M.R.I.C.'s Avatar
Larry Ewens, C.M.R.I.C. Larry Ewens, C.M.R.I.C. is offline
Active Poster
 
Join Date: Feb 2005
Location: Brantford, On
Posts: 774
Send a message via AIM to lewens
Please Note: lewens is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation requirements question

Two by strapping would take care of the problem. It will give you the required 1" air space and enough left to insulate to required value. The only problem I see is the strapping may interfere with the window height.
Larry
Reply With Quote
  #12  
Old 3/29/07, 7:35 PM
Larry Ewens, C.M.R.I.C.'s Avatar
Larry Ewens, C.M.R.I.C. Larry Ewens, C.M.R.I.C. is offline
Active Poster
 
Join Date: Feb 2005
Location: Brantford, On
Posts: 774
Send a message via AIM to lewens
Please Note: lewens is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation requirements question

Quote:
Originally Posted by roconnor
Careful ... because typical batts already has a vapor barrier on the back side of the paper. You don't want a double vapor barrier that may trap moisture.

JMO
This is strange as I have not seen paper backed batts since the sixties.
Larry
Reply With Quote
  #13  
Old 3/29/07, 7:43 PM
Keith R. Braun's Avatar
Keith R. Braun Keith R. Braun is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Oct 2006
Location: Buffalo, NY
Posts: 129
Default Re: Insulation requirements question

Purchased at the local Home Depot when I insulated my own 2x10 cathedral ceiling: styrofoam baffles & r-30 owens corning fiberglass(kraft faced)
Code in Buffalo called for r-30.
Reply With Quote
  #14  
Old 3/31/07, 9:40 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,199
Default Re: Insulation requirements question

Quote:
Originally Posted by lewens
This is strange as I have not seen paper backed batts since the sixties.
Larry
Not sure what type of insulation is used in you area, but in my neck of the woods almost all the faced insulation blankets are made with kraft paper facing that has a tar like coating on the back side which serves as a vapor retarder which is just called paper faced batts ... e.g.

http://www.jmhomeinsulation.com/howt...&install=Batts

JMO



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #15  
Old 3/31/07, 2:18 PM
homebild homebild is offline
Active Poster
 
Join Date: Nov 2006
Location: Pennsylvania
Posts: 195
Please Note: homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation requirements question

Quote:
Originally Posted by brepanshek
There is 2x10 for rafter material being used. In the northern states r-38 is required in ceilings, how would you insulate the rafters if it was a vaulted ceiling (meaning they want to attach drywall directly to the rafters for a sloped ceiling) 2x10 measures 9 1/2" in depth, what materials would you use to acheive the r-38 requirments and yet have the 1" air gap against the roof deck sheating???

Ridge insulation then batts of some sort?????????????????
Careful.

Pennsylvania allows a wide variety of compliance paths for energy conservation and Code complinace, and R-38 is not always required for ceiling insulation in Pennsylvania.

One can use Chapter 11 of the IRC 2006, the 2006 Pennsylvania Alternative Energy Code, the Department of Energy RESCheck software, and many various alternative complinace methods and approaches under the 2006 IECC.

R-38 for ceiling insulation is not written in stone in Pennsylvania and most designs do not include R-38 anymore.

The IECC allows, for example, that in a cathedral ceiling, you can use R-30 and still comply with the Code provided that the area of the cathedral ceiling with less than R-38 insulation is less than 500 square feet. (404.2.2 2006 IECC)

REScheck and other performance based compliance methods allows one to reduce ceiling insulation R-values provided wall insulation, window U-factors, or heating and cooling system efficiciencies are increased to make up the difference.

If you suspect a less-than-expected level of insulation on Pennsylvania, have your client refer to the local Residential Energy Codes Inspector for the municipality to verify the structure is compliant.

You can see the Pennsylvania Alternative Energy Code online here:

http://www.dli.state.pa.us/landi/lib/landi/ucc/pa_alternative_2006.pdf

You can see the Department of Energy RESCheck and other types of performance based software here:

http://www.energycodes.gov/

Last edited by homebild; 3/31/07 at 2:21 PM.. Reason: q
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
IAC2 In new residential construction mcyr IAC2 Indoor Air Forum 0 10/9/07 6:45 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM
sub flooring insulation Question? cpetty General Inspection Discussion 10 3/6/06 9:23 PM

All times are GMT -4. The time now is 6:35 AM.
no new posts