  #1  
Old 3/22/11, 12:36 AM
Stephen P. Shockley's Avatar
Stephen P. Shockley Stephen P. Shockley is offline
InterNACHI Member
 
Join Date: May 2009
Location: Salisbury, Maryland
Posts: 259
Default Steel plate shims

Hi,

I had this house that I inspected last weekend that had these steel plate shims on top of every pier, except for one. It looks as though whoever did the block work had every Pier set about 3/8" to 1/2" to low. Is this standard practice in construction, because I've never seen it before until now where it was on every Pier. There was one Pier with nothing on it and had a gap above to the girder. Any thoughts appreciated.

Regards,

Steve
Attached Thumbnails
Steel plate shims-capparellf-031911-165-jpg   Steel plate shims-capparellf-031911-178-jpg  



Shore-Footed Property Services, LLC
Stephen P. Shockley

MD Licensed Home Inspector
410-726-3471
Salisbury, Md
Reply With Quote
Need a home inspection in Kansas? Check out InterNACHI's listing of Kansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/22/11, 1:29 AM
Kenton Shepard, CMI's Avatar
Kenton Shepard, CMI Kenton Shepard, CMI is online now
Certified Master Inspector
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 6,545
Send a message via ICQ to kshepard
Default Re: Steel plate shims

Not a problem. If as a contractor you set piers too high, you have a problem... humps in the floor. Getting them all close to perfect is possible but time consuming (expensive). If you set them slightly low, common practice is to shim girders with steel shims (that won't compress over time) to make everything flat and level. Very common practice and perfectly acceptable. If you see piers with no shims... the floor is probably not flat and level, or the contractor didn't make any money, or the original homeowner paid too much.



Kenton Shepard, CMI Inspector/Instructor


Designer/Builder: House of Horrors 1&2
Author: InterNACHI Narrative Library


Last edited by kshepard; 3/22/11 at 1:32 AM..
Reply With Quote
  #3  
Old 3/22/11, 7:06 AM
Wayne B. Wilson, TN 439's Avatar
Wayne B. Wilson, TN 439 Wayne B. Wilson, TN 439 is online now
Certified Professional Inspector (CPI)
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 19,453
Default Re: Steel plate shims

I agree, The problem we have here they use OSB or Plywood for shims sometimes.



Wayne Wilson CMI
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490
https://www.myhomeinspection.net/


Reply With Quote
  #4  
Old 3/22/11, 9:38 PM
Stephen P. Shockley's Avatar
Stephen P. Shockley Stephen P. Shockley is offline
InterNACHI Member
 
Join Date: May 2009
Location: Salisbury, Maryland
Posts: 259
Default Re: Steel plate shims

Kenton, for the one pier where they didn't use a shim and there is an apparent gap of about 3/8", would you recommend that the gap be filled in with some metal plate?



Shore-Footed Property Services, LLC
Stephen P. Shockley

MD Licensed Home Inspector
410-726-3471
Salisbury, Md
Reply With Quote
  #5  
Old 3/23/11, 1:10 AM
Nick Gromicko, CMI's Avatar
Nick Gromicko, CMI Nick Gromicko, CMI is online now
Active Poster
 
Join Date: Aug 2002
Location: Nederland, Colorado
Posts: 63,570
Default Re: Steel plate shims

I once had a local code official make me jack up the steel "I" beam of a house I built and replace my steel shim with one manufactured as a shim. What was my steel shim? I used a worn out circular saw blade. I tried to explain to him that a circular saw blade is made of better steel than the shim he wanted, but he wouldn't listen to reason. I sent him the old blade in the mail for Christmas.
Reply With Quote
  #6  
Old 3/23/11, 11:19 AM
Stephen P. Shockley's Avatar
Stephen P. Shockley Stephen P. Shockley is offline
InterNACHI Member
 
Join Date: May 2009
Location: Salisbury, Maryland
Posts: 259
Default Re: Steel plate shims

Thanks to everyone else for their comments and advice. Regards, Steve



Shore-Footed Property Services, LLC
Stephen P. Shockley

MD Licensed Home Inspector
410-726-3471
Salisbury, Md
Reply With Quote
  #7  
Old 3/24/11, 12:36 AM
Kenton Shepard, CMI's Avatar
Kenton Shepard, CMI Kenton Shepard, CMI is online now
Certified Master Inspector
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 6,545
Send a message via ICQ to kshepard
Default Re: Steel plate shims

Quote:
Originally Posted by sshockley View Post
Kenton, for the one pier where they didn't use a shim and there is an apparent gap of about 3/8", would you recommend that the gap be filled in with some metal plate?
Yep... pretty easy to do. Then you have solid bearing.



Kenton Shepard, CMI Inspector/Instructor


Designer/Builder: House of Horrors 1&2
Author: InterNACHI Narrative Library

Reply With Quote
  #8  
Old 8/31/18, 2:18 PM
David E. Dykeman David E. Dykeman is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2017
Location: Plainfield, IL
Posts: 42
Default Re: Steel plate shims

If there are a stack of shims as shown in pic... do they need to be welded together?
Attached Thumbnails
Steel plate shims-20180830_133527-jpg  
Reply With Quote
  #9  
Old 10/11/18, 10:29 PM
Kenton Shepard, CMI's Avatar
Kenton Shepard, CMI Kenton Shepard, CMI is online now
Certified Master Inspector
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 6,545
Send a message via ICQ to kshepard
Default Re: Steel plate shims

Quote:
Originally Posted by ddykeman View Post
If there are a stack of shims as shown in pic... do they need to be welded together?
No. The weight of the structure will hold them in place.



Kenton Shepard, CMI Inspector/Instructor


Designer/Builder: House of Horrors 1&2
Author: InterNACHI Narrative Library

Reply With Quote
  #10  
Old 10/11/18, 11:04 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
Certified Master Inspector
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 10,785
Send a message via Yahoo to jfunderburk
Default Re: Steel plate shims

Here' a document I wrote when I was a practicing Building Official about the use of shims. This was my policy.

https://cloversc.org/docview.aspx?docid=25330



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Award Winner 2017, 2016, 2015, 2014, 2013, 2012, 2011, 2010.
Ph: 704-351-1776
www.aohomeinspection.com

Reply With Quote
  #11  
Old 10/12/18, 11:07 AM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 30,655
Default Re: Steel plate shims

What's wrong with one plate set the right height on non-shrink grout before you start framing.?



CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers and any rules updates.
Reply With Quote
  #12  
Old 10/12/18, 7:11 PM
David E. Dykeman David E. Dykeman is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2017
Location: Plainfield, IL
Posts: 42
Default Re: Steel plate shims

Quote:
Originally Posted by jfunderburk View Post
Here' a document I wrote when I was a practicing Building Official about the use of shims. This was my policy.

https://cloversc.org/docview.aspx?docid=25330
Thanks for the info. It Helps...
Reply With Quote
  #13  
Old 10/12/18, 8:13 PM
Kenton Shepard, CMI's Avatar
Kenton Shepard, CMI Kenton Shepard, CMI is online now
Certified Master Inspector
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 6,545
Send a message via ICQ to kshepard
Default Re: Steel plate shims

Quote:
Originally Posted by mcyr View Post
What's wrong with one plate set the right height on non-shrink grout before you start framing.?
........................nothing.

I've seen OSB shims fairly often and never seen one crushed. I know it's not supposed to be right but typically I don't even mention it. Realistically, I don't see it as a problem, and if an inspector called it on a home I was selling, I wouldn't pay a contractor to come out and change out all the OSB shims for steel, and I wouldn't drop the price.

Possible exception: if it were in a location where it might suffer decay. Of course, steel shims corrode.


The only crushing I've ever seen was a double 2x6 post supporting a triple 2x12 built-up girder supporting floor joists in a 10,000 sq. ft log home. The bottom of the girder had crushed a good inch.



Kenton Shepard, CMI Inspector/Instructor


Designer/Builder: House of Horrors 1&2
Author: InterNACHI Narrative Library


Last edited by kshepard; 10/12/18 at 8:42 PM..
Reply With Quote
Need a home inspection in Kansas? Check out InterNACHI's listing of Kansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 10/12/18, 8:26 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
Certified Master Inspector ®
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 30,655
Default Re: Steel plate shims

That's what I thought.



CMI 2004-2017 Retired

Awards Committee Member
U.S. Member of the Year Winner 2009
45 Years Residential/Commercial Builder
Submit your AWARDS NOMINATIONS here
The InterNACHI Awards Committee is the final authority of issuance of any award the committee offers and any rules updates.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bonded to building Steel Structure Frame mcyr Electrical Inspections 11 4/29/09 11:50 AM
"A Bridge Too Far" mcyr Exterior Inspections 7 12/18/08 5:38 PM
A steel House rcooke Canadian Home Inspectors 4 3/20/08 11:42 AM
Securing Top Plate To Steel Support Beam jevans Structural Inspections 5 2/17/08 5:49 PM
disimilar metals cbono Canadian Home Inspectors 12 1/15/08 7:43 AM