Default Ventilating roofs over cathedral ceilings

CASMA
Canadian Asphalt Shingle Manufacturers' Association

TECHNICAL BULLETIN #2
Cathedral ceilings covered with asphalt shingles require adequate ventilation like any other roof to prevent damage to the shingles. There should be a minimum space of at least 1 inch (25 mm) between the roof sheathing and the insulation to allow for the unobstructed air movement. For most residential roof designs a 1 in. (25 mm) air space is sufficient, but for lower sloped roofs (less than 5:12) or long roof runs (>30 feet from eave to ridge) a minimum of 2 in. (50 mm) is recommended.

When a vapour barrier is used, cathedral ceilings require a minimum total net area for inlet and outlet vents equivalent to 1/300 of the total ceiling area. Cross ventilation should be ensured by locating half the required vent area at the eave and the other half at the ridge.

If a vapour barrier is not used, then the vent area should be doubled to 1/150 of the total ceiling area.



Robert Young's ​Montreal Home Inspection Services Inc.
Home Inspections & Building Inspection Services.
Covering on and off islands in greater Montreal and Laval. (514) 489-1887 or (514) 441-3732.
Our Motto: Putting Information Where You Need It Most, "In Your Hands."
https://montreal-home-inspection-services.com

Reply With Quote
Need a home inspection in Newfoundland and Labrador? Check out InterNACHI's listing of Newfoundland and Labrador certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/13/18, 2:21 PM
Leonard Inkster, CMI's Avatar
Leonard Inkster, CMI Leonard Inkster, CMI is offline
Certified Master Inspector ®
 
Join Date: Aug 2011
Location: Niagara Falls, ON
Posts: 3,858
Send a message via Skype™ to linkster
Default Re: Ventilating roofs over cathedral ceilings

Great info Robert. The problem is identifying if there's a continuous baffle when it's hidden.

You can check for ridge venting, but that doesn't guarantee anything. After all, it's a visible inspection. Agree?




Future Proof Property Inspections Inc.

Leonard Inkster, CMI, CITP, CCHI, CPI, IAC2

Any information posted by me on this site should be considered a personal opinion.

Web: http://fppi.ca
Mail: leni@fppi.ca

"Every man always has handy a dozen glib little reasons why he is right not to sacrifice himself..." - Aleksandr Solzhenitsyn
Reply With Quote
  #3  
Old 6/13/18, 2:35 PM
ROBERT YOUNG's Avatar
ROBERT YOUNG ROBERT YOUNG is online now
Certified Professional Inspector (CPI)
 
Join Date: Mar 2010
Location: Montreal, Quebec
Posts: 14,253
Default Re: Ventilating roofs over cathedral ceilings

Quote:
Originally Posted by linkster View Post
Great info Robert. The problem is identifying if there's a continuous baffle when it's hidden.

You can check for ridge venting, but that doesn't guarantee anything. After all, it's a visible inspection. Agree?
100%.

You are quite welcome Len. Thanks for saying so!

Typical/usually, depending upon the depth of the vault, there will be a form of soffit or roof edge venting and a ridge vent, but not always. The vaulted space may run the width/length of the roof.
No pics at the moment. I am not in the office.

At times, Infrared can detect cooler temperature if this space above and below the assembly. Chuck, or one of the other astute InterNACHI colleagues may port some insight.



Robert Young's ​Montreal Home Inspection Services Inc.
Home Inspections & Building Inspection Services.
Covering on and off islands in greater Montreal and Laval. (514) 489-1887 or (514) 441-3732.
Our Motto: Putting Information Where You Need It Most, "In Your Hands."
https://montreal-home-inspection-services.com

Reply With Quote
  #4  
Old 6/14/18, 1:15 PM
Leonard Inkster, CMI's Avatar
Leonard Inkster, CMI Leonard Inkster, CMI is offline
Certified Master Inspector ®
 
Join Date: Aug 2011
Location: Niagara Falls, ON
Posts: 3,858
Send a message via Skype™ to linkster
Default Re: Ventilating roofs over cathedral ceilings

Absolutely Robert, roof edge and ridge venting together are key indicators. However, many times I see Cathedrals with soffits and Roof Rake venting, which of course, if it's properly venting the rake, leaves the last couple of feet without anything.

Never seen (in Canada) horizontal venting, mainly because it would be hidden. It was usual in the U.K. where we used lats to hold the tiles and perforated fascia at the gables.

Most tile and slate roofing I see here in Canada puts the tiles and slates directly (although profiled tiles would need some form of battening I guess) onto the roof deck which means the ventilation needs to go below the deck and therefore vertical.




Future Proof Property Inspections Inc.

Leonard Inkster, CMI, CITP, CCHI, CPI, IAC2

Any information posted by me on this site should be considered a personal opinion.

Web: http://fppi.ca
Mail: leni@fppi.ca

"Every man always has handy a dozen glib little reasons why he is right not to sacrifice himself..." - Aleksandr Solzhenitsyn

Last edited by linkster; 6/14/18 at 1:18 PM..