Default CAZ: gas fireplace depressurization limit

Combustion Appliance Zone Test: Does anyone know how to approach a wood or gas fireplace depressurization limit when doing a CAZ test?

For a wood fireplace using combustion air from the home interior, I set a blower door at 300CFM to simulate the fireplace.

However, if the fireplace has outside air source, there has to be some sort of depressurization limit. It doesn't make sense that setting the BD at 300CFM is the proper procedure.

I tested a tight home with a wood fireplace with outside air source and gasket sealed door (less than totally sealed). CAZ worst case: kitchen fan, bathroom fans, and dryer on, I measured -45pa! Power vented water heaters have -15pa limit. Closed combustion have -50pa limit. What's the limit on this fireplace? I'm sure I exceeded it, and reported it as such. But wondering what is the limit.

I can't find this information anywhere in my searching. I'm BPI Building Analyst certified.
Reply With Quote
Need a home inspection in Hawaii? Check out InterNACHI's listing of Hawaii certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/14/18, 6:52 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 27,529
Default Re: CAZ: gas fireplace depressurization limit

Quote:
Originally Posted by msenty View Post
Combustion Appliance Zone Test: Does anyone know how to approach a wood or gas fireplace depressurization limit when doing a CAZ test?

For a wood fireplace using combustion air from the home interior, I set a blower door at 300CFM to simulate the fireplace.

However, if the fireplace has outside air source, there has to be some sort of depressurization limit. It doesn't make sense that setting the BD at 300CFM is the proper procedure.

I tested a tight home with a wood fireplace with outside air source and gasket sealed door (less than totally sealed). CAZ worst case: kitchen fan, bathroom fans, and dryer on, I measured -45pa! Power vented water heaters have -15pa limit. Closed combustion have -50pa limit. What's the limit on this fireplace? I'm sure I exceeded it, and reported it as such. But wondering what is the limit.

I can't find this information anywhere in my searching. I'm BPI Building Analyst certified.

Their is a huge amount of information on the web looks' like you did not try.. GOOGLE


I did and found some .


gas fireplace depressurization limit - Google Search


All the best... Roy
Reply With Quote
  #3  
Old 9/15/18, 9:03 AM
Michael A. Senty Michael A. Senty is offline
Student Inspector
 
Join Date: Jun 2017
Posts: 21
Default Re: CAZ: gas fireplace depressurization limit

Quote:
Originally Posted by rcooke View Post
Their is a huge amount of information on the web looks' like you did not try.. GOOGLE

I did and found some .
Thanks for your comments and search. In fact I did spend time doing a search. Obviously your search came up with the information I needed. Thanks again!

Answering my own question now, from "BPI Interpretations, Clarifications, and Comments: b) If the gas fireplace is a sealed combustion insert, a spillage test is not required. It is recommended to use smoke directly in front of the unit while operating (any signs of spillage may indicate an issue). Carbon monoxide must be measured at the exterior termination point. If this point is not accessible, measuring ambient carbon monoxide directly in front of and above the unit is recommended. Draft testing may be impossible to perform since there may not be an appropriate location in which to properly place a test probe. Any corrective action required is stated in Building Analyst Standard, page 13. CAZ Depressurization Limits for a sealed combustion appliance would apply."

Meaning the depressurization limit for a gas fireplace with sealed combustion and an outside combustion air source is the same as a sealed combustion gas furnace, namely -50pa

The comment in the BPI standard about testing the seal of any opening is an important comment. There are wood fueled fireplaces with outside combustion air source and access doors that have compromised gaskets. In that case, the seal of the door is critical once again. Not sure if these fireplaces are defined as sealed combustion units. They may be more like a power vented furnace with combustion air supplied to the furnace enclosure through a pipe from the outside, or even like a natural vented appliance. In that case, the CAZ limit is -15pa, or even as low as -5pa. I'll have to do more research on this item, using google.

I just performed an energy code compliance test including a CAZ of -42pa and a sealed gas fireplace. A few months past, I had a -45pa CAZ reading on a home with a wood fired fireplace with gasketed doors and outside combustion air source. I found -10pa as a standard with some States for wood heat stoves and likely for sealed door fireplaces. None of these are BPI or ANSI standards.

As homes are built tight, this depressurization can become a fatal condition in terms of carbon monoxide, something to not miss during an energy audit. Thus my initial question and concern.

Last edited by msenty; 9/15/18 at 5:22 PM..
Reply With Quote
  #4  
Old 3/17/19, 11:14 AM
Glen Gallo Glen Gallo is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2019
Location: San Diego
Posts: 55
Default Re: CAZ: gas fireplace depressurization limit

Late to the party here but if I were to get to -45pa on a CAZ test I would be extremely concerned.

What is the pressure in normal conditions?

I often do not get to 50 with my blower door



CSLB 956053
CalCerts Rater 2006053
CHEERS Rater RCN13587
PHIUS Rater
Snell Group Level I Thermography
Reply With Quote
  #5  
Old 3/18/19, 8:56 AM
Michael A. Senty Michael A. Senty is offline
Student Inspector
 
Join Date: Jun 2017
Posts: 21
Default Re: CAZ: gas fireplace depressurization limit

Quote:
Originally Posted by ggallo2 View Post
Late to the party here but if I were to get to -45pa on a CAZ test I would be extremely concerned.

What is the pressure in normal conditions?

I often do not get to 50 with my blower door
Agreed, and so my post. I don't recall exactly any more, but the pressure under natural conditions was normal, around -2pa.

I live in far northern Minnesota, and I see a lot of well built, tight homes. We have an energy code here that has a -3pa limit on leakage at -50pa. I've followed the BPI procedures that Roy pointed me to. Yes, those buildings with CAZ results in the -35 area +/- area are concerning to my thinking, even though they are within limits for closed combustion appliances. What happens as those appliances age, or an unnoticed crack develops in the combustion or heat exchanger, or in the flue? What if a new exhaust fan is added, unknowingly reducing the depressurization beyond -50? What if an appliance with a -15pa limit is installed in the home at a later date? Observing a CO monitor properly placed in the home is another important item I make sure to check and document.

My energy code testing has expanded beyond simply doing a blower door test, as required by our energy code. I include a CAZ appliance test plus confirm that a CO monitor is properly placed. We have a CO death here every few years, so home safety is an important issue beyond code testing.

BTW, I've only had one time I couldn't reach -50pa on my blower door, and that was a very large commercial dining area with numerous leaks.
Reply With Quote
  #6  
Old 3/18/19, 11:20 AM
Glen Gallo Glen Gallo is online now
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2019
Location: San Diego
Posts: 55
Default Re: CAZ: gas fireplace depressurization limit

when you consider that 50pa is like putting a 20mph force on the entire surface I just don't see a bathroom fan or kitchen fan achieving that no matter how tight the home. Perhaps complete supply leakage into unconditioned space on a large air handler would be a jump.

I have a bit of experience with pressure testing.

1) any time a house under natural conditions is at a negative pressure I am concerned your house should not suck

2) I always take elements one at a time during caz beginning with smallest bath fans then hood fans then air handler note each change open close doors to achieve greatest pressure delta

Anomalies and I can only think that a 50pa Caz test is an anomaly I would doubt my findings and double check.

I would think on the tightest of buildings the normal fans of a home cannot achieve -50pa I would expext them to choke out and not have the power to achieve -45. CFM in = CFM out

Home Energy pros would be a good place to go with this there are poster there that have more expertise than I. I am not an engineer or a phd but a fairly competent technician own a BD since 2007 and have done my fair share of testing. You are in a different region

I do suspect something went wrong with your testing



CSLB 956053
CalCerts Rater 2006053
CHEERS Rater RCN13587
PHIUS Rater
Snell Group Level I Thermography

Last edited by ggallo2; 3/18/19 at 11:24 AM..