  #1  
Old 2/9/15, 1:40 PM
Kenton Shepard, CMI's Avatar
Kenton Shepard, CMI Kenton Shepard, CMI is online now
Certified Master Inspector
 
Join Date: Aug 2004
Location: Lyons, CO
Posts: 6,158
Send a message via ICQ to kshepard
Default Energy Star Thermal Bypass Checklist

Anyone using this during inspections? I was thinking about writing narratives for it.
If so, what software do you use?

98 views and not a single comment. Guess those narratives aren't getting written any time soon.



Kenton Shepard, CMI Inspector/Instructor

InterNACHI Director of International Development
Director of Green Building
Author: InterNACHI Narrative Library


Last edited by kshepard; 2/12/15 at 12:27 AM..
Reply With Quote
Need a home inspection in North Carolina? Check out InterNACHI's listing of North Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/12/15, 10:23 AM
Kenneth A. Ramm Kenneth A. Ramm is offline
Certified Professional Inspector (CPI)
 
Join Date: Oct 2012
Location: New Glarus, WI
Posts: 3,783
Default Re: Energy Star Thermal Bypass Checklist

Good reading Kenton, though unless someone is doing new construction or infrared than most likely will not pertain to a normal home inspection. But you knew that.



Kenneth (Kenny) Ramm
608-438-3986
RammHomeInspections@gmail.com
Wisconsin License 2516-106
InterNACHI #12101905
Level II Infraspection Institute Certified Infrared Thermographer #10786

"If you want to live a happy life, tie it to a goal, not to people or objects." Albert Einstein
Reply With Quote
  #3  
Old 2/12/15, 10:55 AM
Kenton Shepard, CMI's Avatar
Kenton Shepard, CMI Kenton Shepard, CMI is online now
Certified Master Inspector
 
Join Date: Aug 2004
Location: Lyons, CO
Posts: 6,158
Send a message via ICQ to kshepard
Default Re: Energy Star Thermal Bypass Checklist

Quote:
Originally Posted by kramm View Post
Good reading Kenton, though unless someone is doing new construction or infrared than most likely will not pertain to a normal home inspection. But you knew that.
Hi Kenneth,
Yeah, that's sort of true with a lot of green-related stuff. But I thought it might be helpful for someone trying to expand into a niche market.



Kenton Shepard, CMI Inspector/Instructor

InterNACHI Director of International Development
Director of Green Building
Author: InterNACHI Narrative Library

Reply With Quote
  #4  
Old 2/12/15, 4:59 PM
Kenneth A. Ramm Kenneth A. Ramm is offline
Certified Professional Inspector (CPI)
 
Join Date: Oct 2012
Location: New Glarus, WI
Posts: 3,783
Default Re: Energy Star Thermal Bypass Checklist

Quote:
Originally Posted by kshepard View Post
Hi Kenneth,
Yeah, that's sort of true with a lot of green-related stuff. But I thought it might be helpful for someone trying to expand into a niche market.
That's what I thought. Keep up the good work and thanks for all you do.



Kenneth (Kenny) Ramm
608-438-3986
RammHomeInspections@gmail.com
Wisconsin License 2516-106
InterNACHI #12101905
Level II Infraspection Institute Certified Infrared Thermographer #10786

"If you want to live a happy life, tie it to a goal, not to people or objects." Albert Einstein
Reply With Quote
  #5  
Old 3/1/15, 5:08 PM
Will Jones, TN 822 Will Jones, TN 822 is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2004
Location: Nashville, TN
Posts: 187
Default Re: Energy Star Thermal Bypass Checklist

I use it all the time but mainly because I'm a rater. The EPA requires the actual paperwork to be submitted so I'm just using a fillable PDF system that allows me to collect all my data and insert my photos to the forms so I only have to keep up with 2 files per house; pre-dryall and final. I do it on my phone in the field with PDF Expert app. I'd love to have the ability to use inspector pro and have sent them a few emails about it. If there was a way to add the fillable pdf to the app I would be pumped. I've even tried to submit an actual template I built that says the exact thing the EPA paperwork says but it was rejected by the EPA because it wasn't the exact paperwork. They just love to be a pain in the ***. I'd be able to produce much better reports and faster. Most of the time the builders don't understand what I'm talking about unless I can diagram it out.
I do have some templates I use for air sealing reports for the builders. I'm still tweaking it but it allows me to draw on the framing members to point out issues and the guys building the homes always grasp it better when they can see a detailed repair option.

There really isn't any good software systems out that help raters produce reports. We mostly build our own software systems. I've talked to a software developer about creating one but I just don't have the time right now to show him what I need it to do. There really needs to be a good program that calculates all the formulas we use and produce a good report with photos.

If anyone knows of any on the market point me in the right direction because I haven't found it yet.



tnproinspections.com
TN license #822
RESNET Rater #1882688
Reply With Quote
  #6  
Old 3/1/15, 7:02 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2004
Location: this side of Texas dirt, another successful day
Posts: 4,502
Default Re: Energy Star Thermal Bypass Checklist

down here they give the stickers freely like halloween candy
over 20 clearly visible incidences of better than 16"x48" displaced or absent insulation in ceilings & walls were just as bad with ir...ymmv

if you print poorly it's better, right?
Attached Thumbnails
energy-star-thermal-bypass-checklist-es2.jpg   energy-star-thermal-bypass-checklist-es.jpg   energy-star-thermal-bypass-checklist-es1.jpg  



badair

ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

National Association of Commercial Building Inspectors & Thermographers™ Member ID 12011-14TX

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #7  
Old 3/1/15, 9:49 PM
Will Jones, TN 822 Will Jones, TN 822 is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2004
Location: Nashville, TN
Posts: 187
Default Re: Energy Star Thermal Bypass Checklist

Does that say 4310 cfm for infiltration?!! That better be one massive house to pass even the infiltration.
Barry unfortunately RESNET has done a piss poor job of monitoring everyone. They are supposed to check the Providers who in turn are supposed to check the Raters but they don't so the Providers just do what they want. I have taken over accounts in the past that the builders didn't even know what I was doing when I was installing the blower door, they had never even seen one. I would advise clients buying an energy star home to get their own rater to check the house. It's a huge issue and a very frustrating one if you make people do it right, because if they get sick of failing they just hire whoever tells them they will pass them. I'm seeing the same thing with code compliance; I had a builder that was in disbelief that I would be at the house for 5 hours testing. He exclaimed that the builder on the lot next to him had a guy come in for 20 minutes and look around and then produce the paperwork. Of course he wouldn't tell me who it was and then guess what he drops me to go with the "imaginary" tester, why because he won't fail! It frustrates me to no end.



tnproinspections.com
TN license #822
RESNET Rater #1882688
Reply With Quote
  #8  
Old 3/2/15, 5:22 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Aug 2004
Location: this side of Texas dirt, another successful day
Posts: 4,502
Default Re: Energy Star Thermal Bypass Checklist

Quote:
Originally Posted by wjones View Post
Does that say 4310 cfm for infiltration?!! That better be one massive house to pass even the infiltration.
Barry unfortunately RESNET has done a piss poor job of monitoring everyone. They are supposed to check the Providers who in turn are supposed to check the Raters but they don't so the Providers just do what they want. I have taken over accounts in the past that the builders didn't even know what I was doing when I was installing the blower door, they had never even seen one. I would advise clients buying an energy star home to get their own rater to check the house. It's a huge issue and a very frustrating one if you make people do it right, because if they get sick of failing they just hire whoever tells them they will pass them. I'm seeing the same thing with code compliance; I had a builder that was in disbelief that I would be at the house for 5 hours testing. He exclaimed that the builder on the lot next to him had a guy come in for 20 minutes and look around and then produce the paperwork. Of course he wouldn't tell me who it was and then guess what he drops me to go with the "imaginary" tester, why because he won't fail! It frustrates me to no end.
Will great advice & you may be an exception to what i often see
that's what i read for 4,228sqft conditioned space
imo, same shaq, absence of 30x20sqft of ceiling insulation should get a notice?
these raters/ratings aren't worth the price of the stickers & i have no equipment/credentials to refute
only common sense, visual & ir images

btw...we've hijacked the purpose of Kent's post ;~))



badair

ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

National Association of Commercial Building Inspectors & Thermographers™ Member ID 12011-14TX

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #9  
Old 3/2/15, 7:39 AM
Kenton Shepard, CMI's Avatar
Kenton Shepard, CMI Kenton Shepard, CMI is online now
Certified Master Inspector
 
Join Date: Aug 2004
Location: Lyons, CO
Posts: 6,158
Send a message via ICQ to kshepard
Default Re: Energy Star Thermal Bypass Checklist

That's OK. At least the thread is going somewhere now.



Kenton Shepard, CMI Inspector/Instructor

InterNACHI Director of International Development
Director of Green Building
Author: InterNACHI Narrative Library

Reply With Quote
  #10  
Old 3/2/15, 11:45 AM
Will Jones, TN 822 Will Jones, TN 822 is offline
Certified Professional Inspector (CPI) ®
 
Join Date: Feb 2004
Location: Nashville, TN
Posts: 187
Default Re: Energy Star Thermal Bypass Checklist

Sorry Kenton! lol

Barry he would have to have 12' ceilings to be where he needs to be. Not to mention the insulation.



tnproinspections.com
TN license #822
RESNET Rater #1882688
Reply With Quote
  #11  
Old 5/23/17, 8:48 PM
Jeff Belrose, CMI Jeff Belrose, CMI is offline
Certified Master Inspector
 
Join Date: Sep 2012
Location: St.Albans, VT
Posts: 3,564
Default Re: Energy Star Thermal Bypass Checklist

Quote:
Originally Posted by kshepard View Post
Anyone using this during inspections? I was thinking about writing narratives for it.
If so, what software do you use?

98 views and not a single comment. Guess those narratives aren't getting written any time soon.
I would like to do more with this. Would be interested in what you are looking to do here.

Am using Home Inspector Pro
Reply With Quote
  #12  
Old 6/16/17, 8:39 AM
Leonard Inkster, CMI's Avatar
Leonard Inkster, CMI Leonard Inkster, CMI is online now
Certified Master Inspector ®
 
Join Date: Aug 2011
Location: Niagara Falls, ON
Posts: 3,707
Send a message via Skype™ to linkster
Default Re: Energy Star Thermal Bypass Checklist

Here's a very good 1/2 guide to the Energy Star Thermal Bypass checklist.

https://youtu.be/kNZZZQDIiOE




Future Proof Property Inspections Inc.

Leonard Inkster, CMI, CITP, CCHI, CPI, IAC2

Any information posted by me on this site should be considered a personal opinion.

Web: http://fppi.ca
Mail: leni@fppi.ca

"Every man always has handy a dozen glib little reasons why he is right not to sacrifice himself..." - Aleksandr Solzhenitsyn
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Mold Inspectors in Coeur d’Alene, ID 83815 rspriggs Ancillary Inspection Services 17 8/11/15 3:43 PM
Top 10 Most Popular Energy Savers Web pages of 2011 swaskewicz Thermal Imaging, Infrared Cameras & Energy Audits 3 12/29/11 11:57 AM
Energy program goes retro rcooke Canadian Home Inspectors 2 6/18/11 8:06 AM
Energy Audit Article ebadofsky General Inspection Discussion 1 2/2/07 7:04 AM